Good point!  I’m not sure why a fan coil requires a constant volume fan, but that’s apparently the case.

 

How about using a ZoneHVAC:UnitHeater?  Heat transfer will be the same and the fan can be “On/Off”.  This only works for heating, not cooling. 

 

Another possibility to get cooling capability is a UnitVentilator.  You’d have to define it with no outdoor air and a variable volume fan. If you make the variable volume fan coefficients proportional to load (100% load = 100% power, 50% load = 50% power, etc., it should end up very close to On/Off operation.

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of grandocu
Sent: Saturday, October 02, 2010 1:11 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: Fan Coil Night time Cycling

 

 

They would need to be connected to an airloop then right? What if they are only set up as zonal equipment? if I use availabilitymanager:nightcycle doesn't it only work if I can assign the availabilitymanager:assignmentlist to something? I don't see where I can include that into the fan coil at the zone level.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "James V Dirkes II, PE" <jim@...> wrote:
>
> Try "AvailabilityManager:NightCycle"
>
>
>
> The Building Performance Team
> James V. Dirkes II, P.E., LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
>
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of grandocu
> Sent: Saturday, October 02, 2010 11:03 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Fan Coil Night time Cycling
>
>
>
>
>
> Hello,
>
> How you get fan coil units to cycle on at night if the zone passes the
> setback temperature? I just want them to turn on to meet the load in the
> room. Thank you.
>



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___