Dear Jean, A quick review suggests that you look at: 1.
You are using an On/Off fan. The fan uses an “Always
on” schedule, but the nature of this fan is to cycle on and off as needed
for building loads. 2.
You are also using AvailabilityManager:NightCycle set for “StayOff”.
Normally this means that your fan will never operate at night. I’m
not sure what happens with an OnOff fan …, but you might get rid of this
manager since it does not apply to your situation. 3.
Finally, you are autosizing minimum outdoor air in the Controller:Outdoor
Air. I’d be inclined to set the minimum at a non-zero value or create a minimum
fraction or schedule for outdoor air. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef Thank you Dr. Li, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.