FYI, I used Edmonton weather for my run...
On 10/15/2010 12:35 PM, Richard Raustad wrote:
On 10/15/2010 12:33 PM, Langdon Alger wrote:
Would you
be able to attach the results file from your
simulation?
--- On Fri, 10/15/10, alaa kandil <alaak1974@xxxxxxxxx>
wrote:
From: alaa kandil <alaak1974@xxxxxxxxx>
Subject: Re: [EnergyPlus_Support] Large Reheat
Consumption During Summer
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Received: Friday, October 15, 2010, 11:53 AM
I tried simulating the file and it
is working just fine, and heating
energy use looks normal as well.
I used Calgary weather data. I am
not sure which one you used .. I think
it was edmonton .. very close though.
Cheers
Alaa Kandil
Energy Analysis
Specialist
MA, LEED® AP
MechWave
Engineering Ltd.
Suite 200, 1518 7th
Street SW
Calgary, Alberta T2R 1A7
Phone: 403-802-1090 Facsimile:
403-244-4440
From:
Langdon Alger <wigglish_pup@xxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Fri,
October 15, 2010 8:58:03 AM
Subject: RE:
[EnergyPlus_Support] Large Reheat
Consumption During Summer
| Hi James,
Thank you for the
reply.
I have transitioned
the file to v5.
However I still find
that I am getting the
same problem as
before.
I have attached to
updated idf file.
--- On Fri,
10/15/10, James V
Dirkes II, PE <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>
wrote:
From: James V Dirkes
II, PE <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>
Subject: RE:
[EnergyPlus_Support]
Large Reheat
Consumption During
Summer
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Received: Friday,
October 15, 2010,
9:34 AM
Dear
Langdon.
The
text “AHU
HEATING COIL
CONTROLLER” does
not appear in
your IDF, so I
can’t figure
out what is
referred to by
the error. In
addition, the
IDF is
difficult to
read because
of the many
interspersed
comments.
I
recommend that
you begin
using the
newest
version, so it
can be opened
by the IDF
Editor.
Transition of
your IDF to
the current
version is
almost a one
click affair!
The
Building
Performance
Team
James
V. Dirkes II,
P.E., LEED AP
1631
Acacia
Drive NW
Grand Rapids,
MI 49504
616 450 8653
|
Hello,
I
am running
multiple
simulations
using various
building
configurations
and I have run
into the
problem in my
results which
I can't
determine the
cause for.
I
get low
natural gas
consumption in
the winter
months and
high
consumption
during the
summer due to
the reheat
system. I am
using an old
version of
EnergyPlus
which I hope
is not a
problem.
I
do get a
Severe error
in my
simulations
which occurs
multiple
times:
Severe
** Controller
error for
controller =
AHU HEATING
COIL
CONTROLLER
**
~~~ **
Occurrence
info=EDMONTON
STONY PLAIN AB
CAN
WYEC2-B-25145
WMO#=711230,
08/06 04:02 -
04:03
**
~~~ **
Controller
function is
inconsistent
with user
specified
controller
action =
"" action
**
~~~ **
Actuator will
be set to
minimum action
**
~~~ ** Note:
Chilled water
coils should
be reverse
action and the
entering
chilled
**
~~~ ** water
temperature
should be
below the
setpoint
**
~~~ ** Note:
Hot water
coils should
be normal
action and the
entering hot
**
~~~ ** water
temperature
should be
above the
setpoint
I
have attached
the simulation
file I am
working with
and the
weather file.
Thank
you for your
help.
|
|
|
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|