FYI, I used Edmonton weather for my run...
On 10/15/2010 12:35 PM, Richard Raustad wrote:
On 10/15/2010 12:33 PM, Langdon Alger wrote:
Would you be able to attach the results file from your simulation?
--- On Fri, 10/15/10, alaa kandil <alaak1974@xxxxxxxxx> wrote:
From: alaa kandil <alaak1974@xxxxxxxxx>
Subject: Re: [EnergyPlus_Support] Large Reheat Consumption During Summer
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Received: Friday, October 15, 2010, 11:53 AM
I tried simulating the file and it is working just fine, and heating energy use looks normal as well.I used Calgary weather data. I am not sure which one you used .. I think it was edmonton .. very close though.Cheers
Alaa Kandil
Energy Analysis Specialist
MA, LEED® AP
MechWave Engineering Ltd.
Suite 200, 1518 7th Street SW
Calgary, Alberta T2R 1A7
Phone: 403-802-1090 Facsimile: 403-244-4440
From: Langdon Alger <wigglish_pup@xxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Fri, October 15, 2010 8:58:03 AM
Subject: RE: [EnergyPlus_Support] Large Reheat Consumption During Summer
Hi James, Thank you for the reply.I have transitioned the file to v5. However I still find that I am getting the same problem as before.I have attached to updated idf file.
--- On Fri, 10/15/10, James V Dirkes II, PE <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
From: James V Dirkes II, PE <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>
Subject: RE: [EnergyPlus_Support] Large Reheat Consumption During Summer
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Received: Friday, October 15, 2010, 9:34 AM
Dear Langdon.
The text â??AHU HEATING COIL CONTROLLERâ?? does not appear in your IDF, so I canâ??t figure out what is referred to by the error. In addition, the IDF is difficult to read because of the many interspersed comments.
I recommend that you begin using the newest version, so it can be opened by the IDF Editor. Transition of your IDF to the current version is almost a one click affair!
The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Langdon Alger
Sent: Friday, October 15, 2010 8:58 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Large Reheat Consumption During Summer
Hello,
I am running multiple simulations using various building configurations and I have run into the problem in my results which I can't determine the cause for.
I get low natural gas consumption in the winter months and high consumption during the summer due to the reheat system. I am using an old version of EnergyPlus which I hope is not a problem.
I do get a Severe error in my simulations which occurs multiple times:
Severe ** Controller error for controller = AHU HEATING COIL CONTROLLER
** ~~~ ** Occurrence info=EDMONTON STONY PLAIN AB CAN WYEC2-B-25145 WMO#=711230, 08/06 04:02 - 04:03
** ~~~ ** Controller function is inconsistent with user specified controller action = "" action
** ~~~ ** Actuator will be set to minimum action
** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled
** ~~~ ** water temperature should be below the setpoint
** ~~~ ** Note: Hot water coils should be normal action and the entering hot
** ~~~ ** water temperature should be above the setpoint
I have attached the simulation file I am working with and the weather file.
Thank you for your help.
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years