Hi REZA
I am using the Version 5.0.0.031 and I think that you use the Versin 6.
Subject: Re: [EnergyPlus_Support] severe
Hi,
I corrected your file
it had many problems.
1-concerto ( material ) details are copied to schedule !!!
2- schedule compact because of 1 was wrong.
3-airflow network simulation control is changed.
4-airflow multizone : : : zone didn't define ! ! !
5-airflow multizone surface at the name was wrong (janelasul)
i think most of these problems are because of the first software that you made dxf in it.
The attachments file is correct and work, but you must change the airflow multizone : : : zone
look at the help (energy plus input/output reference)
REZAOn Sat, Nov 13, 2010 at 2:32 PM, clélia moraes <arqclelia@xxxxxxxxxxx> wrote:
Dear
I didn`t understand how I define the Zona01
In annex is the file. Are you help me.
Best regards,
Clelia
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: reza.energy@xxxxxxxxx
Date: Sat, 13 Nov 2010 09:16:35 +0100
Subject: Re: [EnergyPlus_Support] severe
hi,
please attach your file.
it said you didnt define inside zona01
have good day
byeOn Fri, Nov 12, 2010 at 11:28 PM, clélia moraes <arqclelia@xxxxxxxxxxx> wrote:
Dear
I don`t find what I have change with this warning.
Program Version,EnergyPlus 5.0.0.031, 11/10/2010 10:04 PM,IDD_Version 5.0.0.031
** Warning ** GetAirflowNetworkInput: AirflowNetwork:SimulationControl object, Specified AirflowNetwork Control = "MultizoneWithoutDistribution" and ZoneInfiltration objects are present.
** ~~~ ** ..ZoneInfiltration objects will not be simulated.
** Severe ** GetAirflowNetworkInput: For an AirflowNetwork Simulation, at least one AirflowNetwork:MultiZone:Zone object is required but none were found.
** Severe ** GetAirflowNetworkInput: AirflowNetwork:MultiZone:Surface object, Surface Name = JANELASUL
** ~~~ ** ..Zone for inside surface must be defined in a AirflowNetwork:MultiZone:Zone object. Could not find Zone = ZONA01
** Severe ** GetAirflowNetworkInput: AirflowNetwork:MultiZone:Surface object, Surface Name = PORTA LESTE
** ~~~ ** ..Zone for inside surface must be defined in a AirflowNetwork:MultiZone:Zone object. Could not find Zone = ZONA01
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___