Oi Clelia,
O download neste feriado esta indisponivel, eles me enviaram um email informando. Me avise se precisar com urgência que eu verifico se consigo te enviar o arquivo que baixei recentemente.
Obrigada,
Bjs Rita
Enviado via iPhone
Hi REZA
Thank for you help.
Clelia
To:
EnergyPlus_Support@xxxxxxxxxxxxxxxFrom:
reza.energy@xxxxxxxxxDate: Sat, 13 Nov 2010 18:24:27 +0100
Subject: Re: [EnergyPlus_Support] severe
i suggest you to use version 6
On Sat, Nov 13, 2010 at 6:21 PM, clélia moraes
<arqclelia@xxxxxxxxxxx> wrote:
Hi REZA
I am using the Version 5.0.0.031 and I think that you use the Versin 6.
Date: Sat, 13 Nov 2010 16:58:44 +0100
Subject: Re: [EnergyPlus_Support] severe
Hi,I corrected
your fileit had many problems.
1-concerto ( material ) details are copied to schedule !!!
2- schedule compact because of 1 was wrong.
3-airflow network simulation
control is changed.4-airflow multizone : : : zone didn't define ! ! !
5-airflow multizone surface at the name was wrong (janelasul)
i think most of these problems are because of the first software that you made dxf in it.
The attachments file is correct and work, but you must change the airflow multizone : : : zone
look at the help (energy plus input/output reference)
REZA
On Sat, Nov 13, 2010 at 2:32 PM, clélia moraes
<arqclelia@xxxxxxxxxxx> wrote:
Dear
I didn`t understand how I define the Zona01
In annex is the file. Are you help me.
Best regards,
Clelia
To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
From:
reza.energy@xxxxxxxxxDate: Sat, 13 Nov 2010 09:16:35 +0100
Subject: Re: [EnergyPlus_Support] severe
hi,
please attach your file.
it said you didnt define inside zona01
have good day
bye
On Fri, Nov 12, 2010 at 11:28 PM, clélia moraes
<arqclelia@xxxxxxxxxxx> wrote:
Dear
I don`t find what I have change with this warning.
Program Version,EnergyPlus 5.0.0.031, 11/10/2010 10:04 PM,IDD_Version 5.0.0.031
** Warning ** GetAirflowNetworkInput: AirflowNetwork:SimulationControl object, Specified AirflowNetwork Control = "MultizoneWithoutDistribution" and ZoneInfiltration objects are present.
** ~~~ ** ..ZoneInfiltration objects will not be simulated.
** Severe ** GetAirflowNetworkInput: For an AirflowNetwork Simulation, at least one AirflowNetwork:MultiZone:Zone object is required but none were found.
** Severe ** GetAirflowNetworkInput: AirflowNetwork:MultiZone:Surface object, Surface Name = JANELASUL
** ~~~ ** ..Zone for inside surface must be defined in a AirflowNetwork:MultiZone:Zone object. Could not find Zone = ZONA01
** Severe ** GetAirflowNetworkInput: AirflowNetwork:MultiZone:Surface object, Surface Name = PORTA LESTE
** ~~~ ** ..Zone for inside surface must be defined in a AirflowNetwork:MultiZone:Zone object. Could not find Zone = ZONA01