RE: [EnergyPlus_Support] Some Tutorials And websites for energy plus







Ok, I use the same process to remove the 2 warnings. 
 
The file vein with - all ~ views result - turned off as I do to work the err (I tried with the key F8 put was not possible).

Thanks

Clelia



To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: RRaustad@xxxxxxxxxxxx
Date: Mon, 15 Nov 2010 13:12:37 -0500
Subject: Re: [EnergyPlus_Support] Some Tutorials And websites for energy plus

 
You changed the Wind Pressure Coefficient Type to SurfaceAverageCalculation. Why did you add the Wind Pressure Coefficient Array and Value objects and the External Node objects? These objects are not used when Wind Pressure Coefficient Type = SurfaceAverageCalculation.  You have also entered other data that is not necessary. When I fixed these errors, the simulation found that only 2 surfaces exist for the airflow network simulation. I assume you still need to add 2 more walls and a roof to complete the simulation. I will let you do that.

On 11/15/2010 12:02 PM, clélia moraes wrote:
 
ok!

I didn't get to turn this serializes below and when to the the simulation to conclude it seemed 4 warning.

If you have a rectangular building, you could change that input to SurfaceAverageCalculation and you would not need these additional input objects.

AirflowNetwork:SimulationControl,
VentNatural, !- Name
MultizoneWithoutDistribution, !- AirflowNetwork Control
SurfaceAverageCalculation, !- Wind Pressure Coefficient Type

From the IDD file:

A3 , \field Wind Pressure Coefficient Type
\type choice
\key Input
\key SurfaceAverageCalculation
\default SurfaceAverageCalculation

\note Input: User must enter AirflowNetwork:MultiZone:WindPressureCoefficientArray,
\note AirflowNetwork:MultiZone:ExternalNode, and
\note AirflowNetwork:MultiZone:WindPressureCoefficientValues objects.

\note SurfaceAverageCalculation: used only for rectangular buildings.
\note If SurfaceAverageCalculation is selected,
\note AirflowNetwork:MultiZone:WindPressureCoefficientArray, AirflowNetwork:MultiZone:ExternalNode,
\note and AirflowNetwork:MultiZone:WindPressureCoefficientValues objects are not used.



I need your help.


4 Warning

Program Version,EnergyPlus 5.0.0.031, 11/10/2010 10:04 PM,IDD_Version 5.0.0.031
   ** Warning ** GetAirflowNetworkInput: AirflowNetwork:SimulationControl object, Specified AirflowNetwork Control = "MultizoneWithoutDistribution" and ZoneInfiltration objects are present.
   **   ~~~   ** ..ZoneInfiltration objects will not be simulated.
   ** Severe  ** GetAirflowNetworkInput: For an AirflowNetwork Simulation, at least one AirflowNetwork:MultiZone:Zone object is required but none were found.
   ** Severe  ** GetAirflowNetworkInput: AirflowNetwork:MultiZone:Surface object, Surface Name = JANELASUL
   **   ~~~   ** ..Zone for inside surface must be defined in a AirflowNetwork:MultiZone:Zone object.  Could not find Zone = ZONA01
   ** Severe  ** GetAirflowNetworkInput: AirflowNetwork:MultiZone:Surface object, Surface Name = PORTA LESTE
   **   ~~~   ** ..Zone for inside surface must be defined in a AirflowNetwork:MultiZone:Zone object.  Could not find Zone = ZONA01





To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: RRaustad@xxxxxxxxxxxx
Date: Mon, 15 Nov 2010 10:31:41 -0500
Subject: Re: [EnergyPlus_Support] Some Tutorials And websites for energy plus

 
** Severe ** GetAirflowNetworkInput: AirflowNetwork:SimulationControl object, Wind Pressure Coefficient Type = INPUT.
** ~~~ ** ..AirflowNetwork Wind Pressure Coefficient Array Name was not entered.

In your file, you have left blank the field for the wind pressure coefficient array name when you said the wind pressure coefficient type was INPUT.

AirflowNetwork:SimulationControl,
VentNatural, !- Name
MultizoneWithoutDistribution, !- AirflowNetwork Control
Input, !- Wind Pressure Coefficient Type
, !- AirflowNetwork Wind Pressure Coefficient Array Name

Look at the example file AirflowNetwork3zVent.idf. That file has the same input as yours and DID specify the coefficient array name. You will also need one AirflowNetwork:MultiZone:WindPressureCoefficientValues object for each face of the building (I only show 1, see the same example file)

AirflowNetwork:SimulationControl,
NaturalVentilation, !- Name
MultizoneWithoutDistribution, !- AirflowNetwork Control
INPUT, !- Wind Pressure Coefficient Type
Every 30 Degrees, !- AirflowNetwork Wind Pressure Coefficient Array Name

AirflowNetwork:MultiZone:WindPressureCoefficientArray,
Every 30 Degrees, !- Name
0, !- Wind Direction 1 {deg}
30, !- Wind Direction 2 {deg}
60, !- Wind Direction 3 {deg}
90, !- Wind Direction 4 {deg}
120, !- Wind Direction 5 {deg}
150, !- Wind Direction 6 {deg}
180, !- Wind Direction 7 {deg}
210, !- Wind Direction 8 {deg}
240, !- Wind Direction 9 {deg}
270, !- Wind Direction 10 {deg}
300, !- Wind Direction 11 {deg}
330; !- Wind Direction 12 {deg}

AirflowNetwork:MultiZone:WindPressureCoefficientValues,
NFacade_WPCValue, !- Name
Every 30 Degrees, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
0.60, !- Wind Pressure Coefficient Value 1 {dimensionless}
0.48, !- Wind Pressure Coefficient Value 2 {dimensionless}
0.04, !- Wind Pressure Coefficient Value 3 {dimensionless}
-0.56, !- Wind Pressure Coefficient Value 4 {dimensionless}
-0.56, !- Wind Pressure Coefficient Value 5 {dimensionless}
-0.42, !- Wind Pressure Coefficient Value 6 {dimensionless}
-0.37, !- Wind Pressure Coefficient Value 7 {dimensionless}
-0.42, !- Wind Pressure Coefficient Value 8 {dimensionless}
-0.56, !- Wind Pressure Coefficient Value 9 {dimensionless}
-0.56, !- Wind Pressure Coefficient Value 10 {dimensionless}
0.04, !- Wind Pressure Coefficient Value 11 {dimensionless}
0.48; !- Wind Pressure Coefficient Value 12 {dimensionless}

If you have a rectangular building, you could change that input to SurfaceAverageCalculation and you would not need these additional input objects.

AirflowNetwork:SimulationControl,
VentNatural, !- Name
MultizoneWithoutDistribution, !- AirflowNetwork Control
SurfaceAverageCalculation, !- Wind Pressure Coefficient Type

From the IDD file:

A3 , \field Wind Pressure Coefficient Type
\type choice
\key Input
\key SurfaceAverageCalculation
\default SurfaceAverageCalculation

\note Input: User must enter AirflowNetwork:MultiZone:WindPressureCoefficientArray,
\note AirflowNetwork:MultiZone:ExternalNode, and
\note AirflowNetwork:MultiZone:WindPressureCoefficientValues objects.

\note SurfaceAverageCalculation: used only for rectangular buildings.
\note If SurfaceAverageCalculation is selected,
\note AirflowNetwork:MultiZone:WindPressureCoefficientArray, AirflowNetwork:MultiZone:ExternalNode,
\note and AirflowNetwork:MultiZone:WindPressureCoefficientValues objects are not used.



On 11/15/2010 10:05 AM, clélia moraes wrote:
 
Hi REZA

Ok! 
 
 I file now this working in the version 6 showing 1 severe that I don't get to correct. It is in enclosed

Thanks

Clelia



To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: reza.energy@xxxxxxxxx
Date: Mon, 15 Nov 2010 15:12:56 +0100
Subject: Re: [EnergyPlus_Support] Some Tutorials And websites for energy plus

 
Hi,
please send email at the related topic
for learning energy plus these are my suggestions.
1- if you want to have fewer problems, please change your version to 6.
2-for opening version 5 or older versions at the energy plus version 6 you have to use transmission tool that you can download it from http://energyplus.helpserve.com
3-please check sample file of energy plus that they can be related to your work and check your file and example file differences they are in "C:\EnergyPlusV6-0-0\ExampleFiles" ( if you didn't change the installation path)
4-download training files from energy plus website
http://apps1.eere.energy.gov/buildings/energyplus/energyplus_training.cfm
at the "Energy Plus University Course Teaching Material" after registration you can download training files that they are power point files (6.5 MB  zip file)
they are very useful
also if you checked the file that I emailed to you, I corrected your file in version 6.
I hope it is useful.
REZA


On Mon, Nov 15, 2010 at 1:45 PM, clélia moraes <arqclelia@xxxxxxxxxxx> wrote:
 

Hi Reza

I managed to do with that the version 6 is scanned the version 5. They put the severe returned in the old mistake. As it could correct it. I inform that I am still learning how to use the software. 
 
Program Version,EnergyPlus 5.0.0.031, 11/10/2010 10:04 PM,IDD_Version 5.0.0.031 
   * * Warning * * GetAirflowNetworkInput: AirflowNetwork:SimulationControl object, Specified AirflowNetwork Control = "MultizoneWithoutDistribution" and ZoneInfiltration objects plows present. 
   * * ~ ~ ~ * *.. ZoneInfiltration objects will not be simulated. 
   * * Severe * * GetAirflowNetworkInput: It goes an AirflowNetwork Simulation, attn least one AirflowNetwork:MultiZone:Zone object i required but none were found. 
   * * Severe * * GetAirflowNetworkInput: AirflowNetwork:MultiZone:Surface object, Surface Name = JANELASUL 
   * * ~ ~ ~ * *.. Zone goes inside surface must be defined in the AirflowNetwork:MultiZone:Zone object.  Could not find Zone = ZONA01 
   * * Severe * * GetAirflowNetworkInput: AirflowNetwork:MultiZone:Surface object, Surface Name = PORTA LESTE 
   * * ~ ~ ~ * *.. Zone goes inside surface must be defined in the AirflowNetwork:MultiZone:Zone object.  Could not find Zone = ZONA01 





To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: reza.energy@xxxxxxxxx
Date: Mon, 15 Nov 2010 03:12:39 +0100
Subject: [EnergyPlus_Support] Some Tutorials And websites for energy plus


 
Hi ,
Some websites that they have tutorials for energy plus.
There is an online tutorial,  http://www.vibyor.com/tutorials
It's a brief tutorial made by Prof. Vishal Garg, from IIIT Hyderabad,India.
There is also a forum on vibyor where the participants of the course can
discuss their problems.
And another tutorial here:
http://www.labeee.ufsc.br/pos-graduacao/ecv_4202/ecv4202_doc.html
There is also the training material designed for University use on the
regular website (which is down until 11/16/2010 morning).
if some one know some thing else please add to this email
with Regards
REZA




-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___