Re: [EnergyPlus_Support] Re: Energy Plus Support help





It sounds to me like you want the AHU fan and CW coil to turn on based on the output of the AvailabilityManager:HIghTemperatureTunOn object. In your file, this will turn on the AHU fan and CW coil when outside air temperature is above a certain value.

Now you also want to turn only the fan on at all other times (or other times that you specify) without turning on the coils?

If I am understanding this correctly, you want the fan to run all the time and the AHU coil and plant to turn on based on the high temperature turn on manager.

You could probably use a scheduled system availability manager to turn on the air loop all the time, and then use the high temperature turn on manager to cycle on the plant when you need it. If the plant is off, the air loop coils are off.

If you are using a high temperature turn on manager in both the air loop and the plant, then if you add a scheduled availability manager to the system availability manager LIST for the air loop, this might give you what you want. the high temperature turn on manager will turn on both the AHU and the plant when you want. Then the scheduled manager will turn on the fan any other time.

There are a number of ways you can do this, you just have to try several combinations.

On 11/23/2010 11:03 PM, thomawong8 wrote:
 

Richard,

I am sorry. I just mean that the chiller will be switched off while the fan inside AHU can still operate. Or when AHU is switched off, the mechanical fan starts.

Regards,
Thomas

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Are you talking about 2 different fans? How can your AHU fan be off when
> the AHU is on?
>
> On 11/23/2010 4:26 AM, thomawong8 wrote:
> >
> > Jason,
> >
> > Thank you very much for your reply. I am so sorry that i didn't
> > clarify my condition. The outside air temperature determines whether
> > my AHU is on or off. I have used
> > AvailabilityManager:HighTemperatureTurn On to do that. Therefore I
> > cannot use simple schedule to turn on or turn off the fan. AHU
> > schedule is not regulate in my case. Can
> > AvailabilityManager:NightCycle still useful in my case? Thank yuo very
> > much.
> >
> > Regarsd,
> > Thomas
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Jason Kirkpatrick
> > <jason.alan.kirkpatrick@> wrote:
> > >
> > > Thomas,
> > >
> > > Try using AvailabilityManager:NightCycle
> > >
> > > This will allow you to have the AHU fan cycle on when the AHU is
> > scheduled
> > > to be off.
> > >
> > > If you mean that you have a zone with a fan in addition to an air
> > handler,
> > > then you can just schedule these to be on or off by defining an
> > operating
> > > schedule.
> > >
> > > Regards,
> > >
> > > Jason
> > >
> > >
> > > On Fri, Nov 19, 2010 at 11:04 PM, Wong Thomas <thomawong8@>wrote:
> > >
> > > >
> > > >
> > > > Dear all,
> > > >
> > > > I am an undergraduate student who is using energyplus to simulate the
> > > > energy consumption of a company. When the AHU is off, I would like
> > to turn
> > > > on the mechanical fan and vice versa. I want to know if there is
> > any command
> > > > or skills which i can use. Thank you very much.
> > > >
> > > > Thomas
> > > >
> > > >
> > > >
> > > >
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___