[EnergyPlus_Support] Re: Energy Plus Support help
looking forward to other replies. I think the pipe object can act as a flow restrictor so technically you should be able to set up a section of pipe just before your coil in the water loop to your equipment with an actuator to constrict the pipe till there is no flow. You may have to write a short EMS program to get this to actuate as per the sensor or schedule that you want to employ.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "thomawong8" <thomawong8@...> wrote:
>
> Richard,
>
> I am sorry that I misunderstand what you say. I want to have multi zones control.I want to switch off the cooling coil while keeping the fan on. I do not want to switch off the whole plant. Can cooling coil follows the AvailabilityManager:LowTemperatureTurnOff.?
> Thank you.
>
> Regards,
> Thomas
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@> wrote:
> >
> > It sounds to me like you want the AHU fan and CW coil to turn on based
> > on the output of the AvailabilityManager:HIghTemperatureTunOn object. In
> > your file, this will turn on the AHU fan and CW coil when outside air
> > temperature is above a certain value.
> >
> > Now you also want to turn only the fan on at all other times (or other
> > times that you specify) without turning on the coils?
> >
> > If I am understanding this correctly, you want the fan to run all the
> > time and the AHU coil and plant to turn on based on the high temperature
> > turn on manager.
> >
> > You could probably use a scheduled system availability manager to turn
> > on the air loop all the time, and then use the high temperature turn on
> > manager to cycle on the plant when you need it. If the plant is off, the
> > air loop coils are off.
> >
> > If you are using a high temperature turn on manager in both the air loop
> > and the plant, then if you add a scheduled availability manager to the
> > system availability manager LIST for the air loop, this might give you
> > what you want. the high temperature turn on manager will turn on both
> > the AHU and the plant when you want. Then the scheduled manager will
> > turn on the fan any other time.
> >
> > There are a number of ways you can do this, you just have to try several
> > combinations.
> >
> > On 11/23/2010 11:03 PM, thomawong8 wrote:
> > >
> > > Richard,
> > >
> > > I am sorry. I just mean that the chiller will be switched off while
> > > the fan inside AHU can still operate. Or when AHU is switched off, the
> > > mechanical fan starts.
> > >
> > > Regards,
> > > Thomas
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > <RRaustad@> wrote:
> > > >
> > > > Are you talking about 2 different fans? How can your AHU fan be off
> > > when
> > > > the AHU is on?
> > > >
> > > > On 11/23/2010 4:26 AM, thomawong8 wrote:
> > > > >
> > > > > Jason,
> > > > >
> > > > > Thank you very much for your reply. I am so sorry that i didn't
> > > > > clarify my condition. The outside air temperature determines whether
> > > > > my AHU is on or off. I have used
> > > > > AvailabilityManager:HighTemperatureTurn On to do that. Therefore I
> > > > > cannot use simple schedule to turn on or turn off the fan. AHU
> > > > > schedule is not regulate in my case. Can
> > > > > AvailabilityManager:NightCycle still useful in my case? Thank yuo
> > > very
> > > > > much.
> > > > >
> > > > > Regarsd,
> > > > > Thomas
> > > > >
> > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Jason Kirkpatrick
> > > > > <jason.alan.kirkpatrick@> wrote:
> > > > > >
> > > > > > Thomas,
> > > > > >
> > > > > > Try using AvailabilityManager:NightCycle
> > > > > >
> > > > > > This will allow you to have the AHU fan cycle on when the AHU is
> > > > > scheduled
> > > > > > to be off.
> > > > > >
> > > > > > If you mean that you have a zone with a fan in addition to an air
> > > > > handler,
> > > > > > then you can just schedule these to be on or off by defining an
> > > > > operating
> > > > > > schedule.
> > > > > >
> > > > > > Regards,
> > > > > >
> > > > > > Jason
> > > > > >
> > > > > >
> > > > > > On Fri, Nov 19, 2010 at 11:04 PM, Wong Thomas <thomawong8@>wrote:
> > > > > >
> > > > > > >
> > > > > > >
> > > > > > > Dear all,
> > > > > > >
> > > > > > > I am an undergraduate student who is using energyplus to
> > > simulate the
> > > > > > > energy consumption of a company. When the AHU is off, I would
> > > like
> > > > > to turn
> > > > > > > on the mechanical fan and vice versa. I want to know if there is
> > > > > any command
> > > > > > > or skills which i can use. Thank you very much.
> > > > > > >
> > > > > > > Thomas
> > > > > > >
> > > > > > >
> > > > > > >
> > > > > > >
> > > > > >
> > > > >
> > > > >
> > > >
> > > > --
> > > > Richard A. Raustad
> > > > Senior Research Engineer
> > > > Florida Solar Energy Center
> > > > University of Central Florida
> > > > 1679 Clearlake Road
> > > > Cocoa, FL 32922-5703
> > > > Phone: (321) 638-1454
> > > > Fax: (321) 638-1439 or 1010
> > > > Visit our web site at: http://www.fsec.ucf.edu
> > > >
> > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > >
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/