|
Linda is right, there are duplicate interior partitions because of “somethinh wrong.” The interior partitions use the “Zone” outside boundary condition. This creates the other side surface automatically, but when you also enter in the other side surface, you get two that are collocated in the same place. This messes up the volume calculations. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Linda Lawrie I have seen this before when users put in the interzone surfaces so as to let EnergyPlus create them and then, for some reason, also put them in as surfaces in the zone.
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |