In which part of E+ I can set Thermal radiation or Internel reflective cavity i searched for these key words but i couldn't find

On Sun, Dec 12, 2010 at 4:27 PM, Griffith, Brent <brent.griffith@xxxxxxxx> wrote:
 

The  model for surface heat transfer in EnergyPlus is not what you seem to imagine.  Trying to assemble an internal reflective cavity using Construction and Material objects does not work.  You would need to develop equivalent properties for that portion of the assembly and collapse them into a single Material layer.

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of reza m
Sent: Sunday, December 12, 2010 8:15 AM

Subject: Re: [EnergyPlus_Support] problem with thermal radiation

 

 


i saw many details that they use 3 or 4  metal layers with foam as insulation layers.

 

On Sun, Dec 12, 2010 at 4:09 PM, Griffith, Brent <brent.griffith@xxxxxxxx> wrote:

 

Your metal layers are inside the construction and will not do anything to affect thermal radiation.  Only the first and last Materials affect the surface radiation properties of the Construction.   

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of reza m
Sent: Saturday, December 11, 2010 4:31 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] problem with thermal radiation

 

 

Hi,
I investigate on thermal radiation and its effects
I have two alternative materials
1- external wall ( with two metal layers)
2- external wall2 (with out metal)
The difference between two simulations  was very poor and thermal radiation energy loos by the wall that has this material wasn't change.

A9C38D:Surface Ext Thermal Radiation Heat Loss to Outdoors [kWh](Monthly)

 

with out Reflector

 with Reflector

January

108.8691475

108.8541296

February

128.5922864

128.6258381

March

251.0705809

250.9363295

April

395.7446768

395.1045226

May

566.9424429

567.0461548

June

587.9205448

587.9979196

July

638.0636581

638.0444506

August

516.8364084

516.6539877

September

348.7579962

348.6593856

October

215.2195033

215.3210677

November

122.2107265

122.2722356

December

90.07916896

90.1409641



do you have any idea?


what should i do to have better result for radiation
i attached my IDF file
thank you in advance for your time
REZA

 




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___