Camille,
It has been my experience that there is not necessarily a linear relationship between number of surfaces (or number of zones) and run time. Often this run time is more dependent on the number of air loops you are simulating, and also the complexity of the systems. Systems employing radiant cooling or heating strategies often take much longer. Also, improperly set up files can take extraordinarily long because the temperatures are having convergence problems.
There is some documentation regarding run time optimization in the "Tips_andTricks_Using_EnergyPlus.pdf" document included with the installation.
One way to reduce run time is to include the following:
Output:Diagnostics, CreateMinimalSurfaceVariables;
Also, it is generally a good idea to do smaller sample runs of a week in summer and a week in winter to perform troubleshooting measures / make sure things are operating properly.
This can be accomplished through modifying the SimulationControl and RunPeriod objects.
SimulationControl,
Yes, !- Do Zone Sizing Calculation
Yes, !- Do System Sizing Calculation
Yes, !- Do Plant Sizing Calculation
No, !- Run Simulation for Sizing Periods
Yes; !- Run Simulation for Weather File Run Periods
RunPeriod,
Summer Week, !- Name
7, !- Begin Month
15, !- Begin Day of Month
7, !- End Month
22, !- End Day of Month
UseWeatherFile, !- Day of Week for Start Day
No, !- Use Weather File Holidays and Special Days
No, !- Use Weather File Daylight Saving Period
Yes, !- Apply Weekend Holiday Rule
Yes, !- Use Weather File Rain Indicators
Yes, !- Use Weather File Snow Indicators
1; !- Number of Times Runperiod to be Repeated
RunPeriod,
Winter Week, !- Name
1, !- Begin Month
15, !- Begin Day of Month
1, !- End Month
22, !- End Day of Month
UseWeatherFile, !- Day of Week for Start Day
No, !- Use Weather File Holidays and Special Days
No, !- Use Weather File Daylight Saving Period
Yes, !- Apply Weekend Holiday Rule
Yes, !- Use Weather File Rain Indicators
Yes, !- Use Weather File Snow Indicators
1; !- Number of Times Runperiod to be Repeated
Also, I have found that version 6 (the newest release of EnergyPlus) has greatly improved run time over previous versions, so if you are using a previous version, I would suggest updating to the newest release.
Hope this helps.
JasonOn Wed, Jan 12, 2011 at 5:02 AM, le_carambar <le_carambar@xxxxxxxx> wrote:
Dear E+ user,
Do you know if there is an approximative relation between the simulation time and the building surface or the number of zone.
For instance, a 2000m² building will be 2 times longer to be simulated than a 1000m² or 4 times longer ?
Thanks,
Camille
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___