And just to close it out, here is the response from the support folks:

	>I do see that the air flow rate for the DX cooling coil 
	>is sizing larger than the Window AC unit. 
	>The problem is that the air flow rate required to 
	>meet the heating load is higher than the air flow 
	>rate required to meet the cooling load.
	>In Energyplus, the Window AC is sized using the 
	>zone design cooling flow rate.
	>However, the DX cooling coil is sized using 
	>the larger of the design cooling and design heating 
	>flow rates. You might ask yourself why do that, 
	>it is because a cooling coil can be 
	>used in the same air stream as a heating 
	>coil and both of these coils would need to use the same 
	>design flow rate. In your case, the Window AC does not 
	>have a heating coil and the software does not 
	>specifically account for that.
	>I see you are using a Window AC for cooling 
	>and convective water baseboard for heating in each zone.
	>If the simulation is using baseboard to heat, 
	>then in Sizing:Zone, entering a high heating supply 
	>temperature should fix the problem.  That should result 
	>in a small heating design flow rate, but nothing in 
	>the user's model should care about that.

I went and changed the supply temp from 40 to 60 and the problem went away.

-Will





------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/