This probably means that you did not list the heat pump in the AirloopHVAC branch list. Follow the "Branch List Name" in the AirloopHVAC object to find what is defined for that air loop. AirLoopHVAC, Air Loop Branches, !- Branch List Name BranchList, Air Loop Branches, !- Name Air Loop Main Branch; !- Branch 1 Name Branch, Air Loop Main Branch, !- Name 1.7, !- Maximum Flow Rate {m3/s} , !- Pressure Drop Curve Name AirLoopHVAC:OutdoorAirSystem, !- Component 1 Object Type OA Sys 1, !- Component 1 Name Outdoor Air Mixer Inlet Node, !- Component 1 Inlet Node Name Mixed Air Node, !- Component 1 Outlet Node Name PASSIVE, !- Component 1 Branch Control Type AirLoopHVAC:UnitaryHeatPump:AirToAir, !- Component 2 Object Type DXAC Heat Pump 1, !- Component 2 Name Mixed Air Node, !- Component 2 Inlet Node Name Air Loop Outlet Node, !- Component 2 Outlet Node Name ACTIVE; !- Component 2 Branch Control Type On 2/4/2011 5:41 AM, Takashi_Toi wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |