You can not have two AirloopHVAC objects serving the same zone since only 1 return node is allowed per zone. And placing the heat pumps in series in a single AirloopHVAC object will probably not satisfy your needs, although you could try it. You can also have 2 systems in the same zone by using the ZoneHVAC object. See the WindowAC or WSHP_DOAS example files. On 2/4/2011 8:06 AM, Richard Raustad wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.