Dear Francisco, I do not think that you can properly simulate VRF with individual zone DX systems. A VRF system essentially responds to the total system load. If, for example, 5 zones are in heating mode, and 6 are in cooling mode, you might have a cooling load that is a small percentage of the total capacity. This can be true even if the 6 cooling mode zones are operating at 100% of their capacity. In this situation, the true part load of the system may be only 9% (as an example). I hope that is clear (I don’t have time now for more details)! For that reason, I think a better approach is: · WSHP in each zone with COP = 1000 (yes, one thousand so that there is essentially no compressor heat added at the zone level) · WSHPs served by a chiller (COP= 1000) and boiler (efficiency = 1.0) · Create a custom meter for the chiller and boiler energy · Via post-processing (e.g., Excel spreadsheet), calculate the net heating / cooling load and apply a part load factor appropriate for the VRF manufacturer · Calculate a new total for electric usage based on the new calculated VRF electricity use. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of fm1n0 Hi. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |