Dear Shane, There are MANY possible reasons! Are the unmet loads for cooling? Heating? Occupied or unoccupied hours? (I don’t worry as much about unoccupied hours) You NEED to report a lot of variables and review them carefully in order to understand where things are going wrong. Once you know where the problem is, a solution often becomes apparent. If you are autosizing, review the design discharge temperature setpoints. For example, in a VAV / reheat system, the zone reheat coil discharge temp must be greater than the air handler discharge temp or you’ll never do any heating. I always create an RVI file so that output variables are organized in a manner that is organized and makes sense to me. Then I dump the data into a spreadsheet which has appropriate display settings for the variable type. It makes the review much easier! Example shown below�. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Shane Watson Thankyou James, I am sizing the HVAC system as per the ASHRAE 90.1 specifications, but still the unmet hours are high. Could you throw some light as how to reduce these setpoint not met hours. From: "James V Dirkes II, PE" <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> Dear Shane, EnergyPlus normally responds favorably to assigning a Sizing:Parameter Sizing Factor greater than 1.0. ASHRAE 90.1 requires a factor of 1.15 for Cooling systems and 1.25 for heating systems. There are many other reasons why you may be experiencing the high number of unmet load hours, but that’s a start! The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Shane Watson When on simulating the idf model on design days, i am getting a large number of timeset point not met hours. What would be the correct way to reduce the setpoint not met hours and upto what limit. Thanks in advance. From: Drury B Crawley <dbcrawley@xxxxxxxxx> It is better to use design conditions from Chapter 14 of 2009 ASHRAE Fundamentals. If there are design data for that location, the .zip file will contain a .ddy file with that design data (design days). Otherwise you will have to create design day objects with the data from ASHRAE. You can read about design days in the ASHRAE document.
On Thu, Feb 10, 2011 at 8:17 AM, Shane Watson <mechenergy@xxxxxxxxx> wrote: Hi everyone, I am simulating a VAV system in an office building, Sizing of the system is done with weather file by using the objectSizing period:Weather file days. Is it a correct way to size the system on the weather file and let the software decide the design condtions. What impact it will have on the HVAC energy consumption. Thanks in advance. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |