Dear Martin, “Purchased” can be a couple of different, similar ideas: 1. Some cities sell steam, hot water or chilled water to customers in their locale. It is produced in a central plant and then distributed to the buildings nearby. These customers thus purchase heating, cooling or both. 2. Some large commercial, industrial or institutional campuses use a central power plant to provide heating and cooling for the buildings on the campus. Although the individual buildings do not “purchase” the service, it is not generated within the building. In addition the part load efficiencies are not the same as the individual buildings (since they correspond to the entire campus part loads) and so you do not want to assign a specific boiler or chiller to the E+ Plant. Hope that helps! The Building Performance Team From: Ene
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.