Hi
I have changed all the coordinates surfaces. The coordinate 2 by the coord. 4 and it does not work.
Now i get the follows errors:
Program Version,EnergyPlus 6.0.0.023, 24/02/2011 05:03 p.m.,IDD_Version 6.0.0.023
** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=FLOOR DOWN, in Zone=ZONE_2
** Warning ** Floor Tilt=90.0, much less than expected tilt of 180, for Surface=VOID SPACE SOUTH, in Zone=ZONE_2
** Severe ** GetSurfaces: Outward facing angle [280.0] of subsurface="WINDOWS SOUTH" significantly different than
** ~~~ ** ..facing angle [100.0] of base surface=WALL SOUTH Tilt=90.0
** ~~~ ** ..surface class of base surface=Wall
** Severe ** Suspected non-planar surface:"WALL EAST", Max "out of line"=1.02916E-002 at Vertex # 3
** Severe ** Suspected 4-sided but non-rectangular Window, Door or GlassDoor:
** ~~~ ** Surface=WINDOWS SOUTH,
Diagonal1=39.187, Diagonal2=39.245
************* Note that the following warning(s) may/will occur if you have not enclosed your zone completely.
** Warning ** Entered Volume entered for Zone="ZONE_2" significantly different from calculated Volume
** ~~~ ** Entered Zone Volume value=794.27, Calculated Zone Volume value=1630.63, entered volume will be used in calculations.
The next ones are the surfaces that i am using:
IDF,BuildingSurface:Detailed,FLOOR DOWN,FLOOR,SLAB,Zone_2,Ground,,NoSun,NoWind,1.00000,4,
37.70000,7.00000,0.00000,
4.2, 7,0.00000,
0.00000,0.00000,0.00000,
42.5, 0,0.00000,;
BuildingSurface:Detailed,WALL EAST,Wall,WALL,Zone_2,Outdoors,,SunExposed,WindExposed,0.50000,4,
42.55000,0.00000,3.00000,
37.7, 7, 3,
37.70000,7.00000,0.00000,
42.5, 0, 0
BuildingSurface:Detailed,WALL NORTH,Wall,WALL,Zone_2,Outdoors,,SunExposed,WindExposed,0.50000,4,
37.70000,7.00000,3.00000,
4.2,7.00000, 3,
4.20000,7.00000,0.00000,
37.7,7.00000, 0
BuildingSurface:Detailed,WALL WEST,Wall,WALL,Zone_2,Outdoors,,SunExposed,WindExposed,0.50000,4,
4.20000,7.00000,3.00000,
0, 0, 3,
0.00000,0.00000,0.00000,
4.2, 7, 0
BuildingSurface:Detailed,WALL SOUTH,Wall,WALL,Zone_2,Outdoors,,SunExposed,WindExposed,0.50000,4,
0.00000,0.00000,3.00000,
42.55,0.00000, 3,
42.55000,0.00000,0.00000,
0,0.00000, 0
BuildingSurface:Detailed,FLOOR UP,Floor,SLAB,Zone_2,Outdoors,,SunExposed,WindExposed,0.2,4,
4.20000,7.00000,3.00000,
37.7, 7,3.00000,
42.55000,0.00000,3.00000,
0, 0,3.00000
BuildingSurface:Detailed,VOID SPACE SOUTH,Floor,VOID,Zone_2,Outdoors,,SunExposed,WindExposed,0.50000,4,
1.57,-0.00000,1.29,
40.77,-0.00000, 1.29,
40.77,-0.00000,1,
1.57,-0.00000, 1;
What can i do?
Jaime Zuluaga M
From: Richard Raustad <RRaustad@xxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thu, 24 February, 2011 16:45:52
Subject: Re: [EnergyPlus_Support] Simulation errors
You have probably specified a counter-clockwise vertex order (as viewed from outside - below the slab for a floor). So switch the order of your floor coordinates to flip it upside down. Make sure you move the semi-colon (;) to the last line and all other lines end with a comma (,).
BuildingSurface:Detailed,FLOORUP, Floor, SLAB, Zone_2,Outdoors, ,SunExposed,WindExposed, 0.2, 4,
4.20000, 7.00000, 3.00000,
37.70000,7.00000,3.0000,
42.55000, 0.00000,3.00000,
0.00000, 0.00000, 3.00000;
On 2/24/2011 4:37 PM, Jaime Zuluaga Machado wrote:
Hi everyone.
I got the following errors:
** Warning ** Floor Tilt=0.0, much less than expected tilt of 180, for Surface=FLOOR UP, in Zone=ZONE_2
** Warning ** Floor Tilt=90.0, much less than expected tilt of 180, for Surface=VOID SPACE SOUTH, in Zone=ZONE_2
** Severe ** Suspected 4-sided but non-rectangular Window, Door or GlassDoor:
** ~~~ ** Surface=WINDOWS SOUTH, Diagonal1=39.187, Diagonal2=39.245
This is the surface description:
BuildingSurface:Detailed,FLOORUP, Floor, SLAB, Zone_2,Outdoors, ,SunExposed,WindExposed, 0.2, 4,
4.20000, 7.00000, 3.00000,
0.00000, 0.00000, 3.00000,
42.55000, 0.00000,3.00000,
37.70000,7.00000,3.00000
BuildingSurface:Detailed, VOID SPACE SOUTH, Floor, VOID,Zone_2, Outdoors, , SunExposed, WindExposed, 0.50000, 4,
1.57,-0.00000,1.29,
1.57,-0.00000,1,
40.77,-0.00000,1,
40.77,-0.00000,1.29
I do not have any idea what is going wrong, does anyone can help me please?
Thanks a lot
Jaime Zuluaga M
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years