Try adjusting the temperatures and humidity ratios in the Sizing:System object. Watch how the warning message changes to make sure you are modifying the correct sizing object.
On 3/4/2011 1:12 PM, x z wrote:Hi Group,I am a new user of EnergyPlus, and I am trying to use FCU template by learning from the example: HVACTemplate-5ZoneFanCoil.I copied the HVACTemplate:Zone:FanCoil objects together with Boiler, Chiller template objects to my model. I set the cooling temperature 12.2C and I got warning msg during plant sizing period as below:** Warning ** In calculating the design coil UA for Coil:Cooling:Water 1F:ZONE5 COOLING COIL
** ~~~ ** no apparatus dew-point can be found for the initial entering and leaving conditions;
** ~~~ ** the coil outlet design conditions will be changed to correct the problem.
** ~~~ ** The initial design conditions are: Tair,in = 28.0957
** ~~~ ** Wair,in = 1.690250E-002
** ~~~ ** Twater,in = 7.2200
** ~~~ ** Tair,out = 12.2000
** ~~~ ** Wair,out = 8.000000E-003
** ~~~ ** The revised design conditions are: Tair,out = 12.2455
** ~~~ ** Wair,out = 7.981631E-003I realize this msg is related to my summer design day conditions, and set design day dry bulb temperature will decrese the number of warnings. And It seems that the msg is related to dew-point of my cooling coil, but I can't find place to specify my FCU design dew-point.May I ask, does this relates to my SummerDesignDay conditions setup? How to eliminate this warning msg?ThanksXiaoSong ZHANG-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___