|
You haven’t done anything wrong. EMS is just not setup to work like that. The value of the sensor has not yet been re-updated. The sensors very often have some lag because they are derived from output variables. Once you set the actuator, the schedule value will altered when something else in the model goes to use that schedule. But the sensor update occurs when the output variable is updated and that happens elsewhere inside EnergyPlus and not as a result of the setting the actuator. You don’t really need to poll the sensor for the new value because you already have it. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Brouchery Herve Hi, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |