Re: [EnergyPlus_Support] Problem with windows





A guess would be that you put in the window in clockwise vertex order and the wall in counter clockwise or vice versa.

Your wall faces north (0) and your window is facing west (270)

At 08:55 AM 3/18/2011, Jaime Zuluaga Machado wrote:
I got a building, there I created one window in a south surface then i change the orientation of this and i had the next errors
 
** Severe  ** GetSurfaces: Outward facing angle [270.0] of subsurface="WINDOWS NORTH" significantly different than
   **   ~~~   ** ..facing angle [0.0] of base surface=WALL NORTH Tilt=90.0
   **   ~~~   ** ..surface class of base surface=Wall
 
Does anyone know what would be the problem?, i guess is windows orientation but i have checked this but i did not see any problem.
 
 