Another possibility of getting the error message is that you have placed the South facing window on the North Wall. After rotation, the widow is facing West and the wall is facing East. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jaimezuluagam@xxxxxxxxx Date: Fri, 18 Mar 2011 14:55:48 +0000 Subject: [EnergyPlus_Support] Problem with windows Hi!
I got a building, there I created one window in a south surface then i change the orientation of this and i had the next errors
** Severe ** GetSurfaces: Outward facing angle [270.0] of subsurface="WINDOWS NORTH" significantly different than
** ~~~ ** ..facing angle [0.0] of base surface=WALL NORTH Tilt=90.0 ** ~~~ ** ..surface class of base surface=Wall Does anyone know what would be the problem?, i guess is windows orientation but i have checked this but i did not see any problem.
Thanks
Jaime Zuluaga M __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.