Hi everyone,
I'm modelling a two-storey house with an underfloor heating system using the LowTemperatureRadiant:VariableFlow function. This unit should run with water provided by a Boiler:HotWater. However, the output shows that there is no water flow present in the plant and I cann't figure out why. I tried to change the design temperatures as well as entering a specific value instead of autosize the rated flow rates, but the result stays the same.
Does anyone know what is wrong?
Yours sincerely, Jan
PS: I don't know how to attach files, so I've just inserted the txt here
----------------------------------------------------------
!-Generator IDFEditor 1.38a
!-Option SortedOrder
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
!- Use '!' comments if they need to be retained when using the IDFEditor.
!- =========== ALL OBJECTS IN CLASS: VERSION
===========
Version,
6.0; !- Version Identifier
!- =========== ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
SimulationControl,
No, !- Do Zone Sizing Calculation
No, !- Do System Sizing Calculation
Yes, !- Do Plant Sizing Calculation
No, !- Run Simulation for Sizing Periods
Yes; !- Run Simulation for Weather File Run Periods
!- =========== ALL OBJECTS IN CLASS: BUILDING ===========
Building,
NormalScale, !- Name
315, !- North Axis {deg}
Suburbs, !- Terrain
0.04, !- Loads Convergence Tolerance Value
0.4, !- Temperature Convergence Tolerance Value {deltaC}
FullExterior, !- Solar Distribution
25; !- Maximum Number of Warmup Days
!- =========== ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:INSIDE ===========
SurfaceConvectionAlgorithm:Inside,
TARP; !- Algorithm
!- =========== ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:OUTSIDE
===========
SurfaceConvectionAlgorithm:Outside,
DOE-2; !- Algorithm
!- =========== ALL OBJECTS IN CLASS: HEATBALANCEALGORITHM ===========
HeatBalanceAlgorithm,
ConductionFiniteDifference, !- Algorithm
200; !- Surface Temperature Upper Limit
!- =========== ALL OBJECTS IN CLASS: ZONEAIRHEATBALANCEALGORITHM ===========
ZoneAirHeatBalanceAlgorithm,
ThirdOrderBackwardDifference; !- Algorithm
!- =========== ALL OBJECTS IN CLASS: TIMESTEP ===========
Timestep,
6; !- Number of Timesteps per Hour
!- =========== ALL OBJECTS IN CLASS: SITE:LOCATION ===========
Site:Location,
Susten, !- Name
7.8, !- Latitude {deg}
46.3, !- Longitude {deg}
1, !- Time Zone {hr}
639; !- Elevation {m}
!- =========== ALL OBJECTS IN CLASS: SIZINGPERIOD:WEATHERFILEDAYS ===========
SizingPeriod:WeatherFileDays,
SizingWeatherFileDays, !- Name
1, !- Begin Month
1, !- Begin Day
of Month
3, !- End Month
31, !- End Day of Month
Monday, !- Day of Week for Start Day
Yes, !- Use Weather File Daylight Saving Period
Yes; !- Use Weather File Rain and Snow Indicators
!- =========== ALL OBJECTS IN CLASS: RUNPERIOD ===========
RunPeriod,
, !- Name
1, !- Begin Month
1, !- Begin Day of Month
3, !- End Month
31, !- End Day of Month
UseWeatherFile, !- Day of Week for Start Day
Yes, !- Use Weather File Holidays and Special Days
Yes, !- Use Weather File Daylight Saving Period
No, !- Apply Weekend Holiday Rule
Yes, !- Use Weather File Rain Indicators
Yes, !- Use Weather File Snow Indicators
1; !- Number of Times Runperiod to be Repeated
!- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========
Site:GroundTemperature:BuildingSurface,
5, !- January Ground Temperature {C}
5.67, !- February Ground Temperature {C}
7.5, !- March
Ground Temperature {C}
10, !- April Ground Temperature {C}
12.5, !- May Ground Temperature {C}
14.33, !- June Ground Temperature {C}
15, !- July Ground Temperature {C}
14.33, !- August Ground Temperature {C}
12.5, !- September Ground Temperature {C}
10, !- October Ground Temperature {C}
7.5, !- November Ground Temperature {C}
5.67; !- December Ground Temperature {C}
!- =========== ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
ScheduleTypeLimits,
Any Number; !- Name
ScheduleTypeLimits,
Fraction, !- Name
0.0, !- Lower Limit Value
1.0, !- Upper Limit Value
CONTINUOUS; !- Numeric Type
ScheduleTypeLimits,
Temperature, !- Name
-60, !- Lower Limit Value
200, !- Upper Limit Value
CONTINUOUS; !- Numeric Type
ScheduleTypeLimits,
On/Off, !- Name
0, !- Lower Limit Value
1, !- Upper Limit Value
DISCRETE; !- Numeric Type
ScheduleTypeLimits,
Control
Type, !- Name
0, !- Lower Limit Value
4, !- Upper Limit Value
DISCRETE; !- Numeric Type
ScheduleTypeLimits,
Humidity, !- Name
10, !- Lower Limit Value
90, !- Upper Limit Value
CONTINUOUS; !- Numeric Type
ScheduleTypeLimits,
Number; !- Name
!- =========== ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========
Schedule:Compact,
Heating Setpoint Schedule, !- Name
Temperature, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 05:00, !- Field 3
21, !- Field 4
Until: 19:00, !- Field 5
21.0, !- Field 6
Until: 24:00, !- Field 7
21; !- Field 8
Schedule:Compact,
Baseboard Operation Schedule, !- Name
On/Off, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
1; !- Field 4
Schedule:Compact,
Zone One Control Type Schedule, !- Name
Control Type, !- Schedule Type
Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
1; !- Field 4
!- =========== ALL OBJECTS IN CLASS: MATERIAL ===========
Material,
Aw innenputz, !- Name
Smooth, !- Roughness
0.015, !- Thickness {m}
0.7, !- Conductivity {W/m-K}
1400, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
Aw Modulbackstein, !- Name
MediumRough, !- Roughness
0.18, !- Thickness {m}
0.44, !- Conductivity {W/m-K}
1100, !- Density {kg/m3}
940, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
Aw Lamitherm , !- Name
MediumRough, !- Roughness
0.14, !- Thickness {m}
0.038, !- Conductivity {W/m-K}
20, !- Density {kg/m3}
1450, !- Specific Heat {J/kg-K}
0.9, !- Thermal
Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
Aw Aussenputz, !- Name
Rough, !- Roughness
0.012, !- Thickness {m}
0.87, !- Conductivity {W/m-K}
1800, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
Material,
Iw Verputz innen, !- Name
Smooth, !- Roughness
0.015, !- Thickness {m}
0..87, !- Conductivity {W/m-K}
1400, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
Iw Modulbackstein, !- Name
MediumRough, !- Roughness
0.12, !- Thickness {m}
0.44, !- Conductivity {W/m-K}
1100, !- Density {kg/m3}
940, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
Iw Verputz aussen, !-
Name
Smooth, !- Roughness
0.015, !- Thickness {m}
0.87, !- Conductivity {W/m-K}
1400, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
BgE Zementunterlag, !- Name
MediumRough, !- Roughness
0.03, !- Thickness {m}
1.5, !- Conductivity {W/m-K}
1800, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
BgE Swisspor EPS20, !- Name
MediumSmooth, !- Roughness
0.022, !- Thickness {m}
0.037, !- Conductivity {W/m-K}
20, !- Density {kg/m3}
1450, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
BgE Flumroc, !- Name
MediumSmooth, !- Roughness
0.08, !- Thickness {m}
0.036, !- Conductivity {W/m-K}
32, !- Density
{kg/m3}
1030, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
BgE Betonplatten, !- Name
MediumSmooth, !- Roughness
0.25, !- Thickness {m}
1.7, !- Conductivity {W/m-K}
2400, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
BgE Misapor, !- Name
MediumSmooth, !- Roughness
0.35, !- Thickness {m}
0.08, !- Conductivity {W/m-K}
55, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
BguR Zementmörtel, !- Name
MediumSmooth, !- Roughness
0.07, !- Thickness {m}
1.5, !- Conductivity {W/m-K}
2100, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0..9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible
Absorptance
Material,
BguG Trittschaldpl, !- Name
Smooth, !- Roughness
0.04, !- Thickness {m}
0.038, !- Conductivity {W/m-K}
9, !- Density {kg/m3}
1450, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
BguR Stahlbeton, !- Name
MediumRough, !- Roughness
0.2, !- Thickness {m}
1.8, !- Conductivity {W/m-K}
2400, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
BguR Schichtex, !- Name
Smooth, !- Roughness
0.12, !- Thickness {m}
0.125, !- Conductivity {W/m-K}
600, !- Density {kg/m3}
2100, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
Dach Lamitherm , !- Name
MediumRough, !- Roughness
0.24, !- Thickness {m}
0.038, !-
Conductivity {W/m-K}
20, !- Density {kg/m3}
1450, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
Dach Holz, !- Name
Rough, !- Roughness
0.05, !- Thickness {m}
0.13, !- Conductivity {W/m-K}
700, !- Density {kg/m3}
1600, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0, !- Solar Absorptance
0; !- Visible Absorptance
Material,
Dach Ziegel, !- Name
Rough, !- Roughness
0.02, !- Thickness {m}
1, !- Conductivity {W/m-K}
2000, !- Density {kg/m3}
1000, !- Specific Heat {J/kg-K}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
!- =========== ALL OBJECTS IN CLASS: MATERIAL:NOMASS ===========
Material:NoMass,
Aw Wu innen, !- Name
Smooth, !- Roughness
0.125, !- Thermal Resistance {m2-K/W}
0.9000000, !- Thermal Absorptance
0.7, !- Solar
Absorptance
0.7; !- Visible Absorptance
Material:NoMass,
Aw Wu aussen, !- Name
Rough, !- Roughness
0.5, !- Thermal Resistance {m2-K/W}
0.9000000, !- Thermal Absorptance
0.7, !- Solar Absorptance
0..7; !- Visible Absorptance
Material:NoMass,
Iw Wu innen, !- Name
Smooth, !- Roughness
0.125, !- Thermal Resistance {m2-K/W}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
Material:NoMass,
Iw Wu aussen, !- Name
MediumSmooth, !- Roughness
0.04, !- Thermal Resistance {m2-K/W}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
Material:NoMass,
BgE Wu innen, !- Name
MediumSmooth, !- Roughness
0.72, !- Thermal Resistance {m2-K/W}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
Material:NoMass,
BguR Wu innen, !- Name
Smooth, !- Roughness
0.167, !-
Thermal Resistance {m2-K/W}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
Material:NoMass,
BguR Wu aussen, !- Name
MediumSmooth, !- Roughness
0.167, !- Thermal Resistance {m2-K/W}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
Material:NoMass,
Dach Wu innen, !- Name
MediumSmooth, !- Roughness
0.125, !- Thermal Resistance {m2-K/W}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
Material:NoMass,
Dach Wu aussen, !- Name
Rough, !- Roughness
0.05, !- Thermal Resistance {m2-K/W}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
Material:NoMass,
BgE Wu aussen, !- Name
MediumRough, !- Roughness
0.001, !- Thermal Resistance {m2-K/W}
0.9, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible
Absorptance
Material:NoMass,
Ceiling perfect, !- Name
VerySmooth, !- Roughness
0.001, !- Thermal Resistance {m2-K/W}
0.001, !- Thermal Absorptance
0.7, !- Solar Absorptance
0.7; !- Visible Absorptance
!- =========== ALL OBJECTS IN CLASS: WINDOWMATERIAL:SIMPLEGLAZINGSYSTEM ===========
WindowMaterial:SimpleGlazingSystem,
window, !- Name
1.6, !- U-Factor {W/m2-K}
0.6; !- Solar Heat Gain Coefficient
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
Construction,
Aussenwand, !- Name
Aw Wu aussen, !- Outside Layer
Aw Aussenputz, !- Layer 2
Aw Lamitherm , !- Layer 3
Aw Modulbackstein, !- Layer 4
Aw innenputz, !- Layer 5
Aw Wu innen; !- Layer 6
Construction,
Innenwand Treppe, !- Name
Iw Wu aussen, !- Outside Layer
Iw Verputz aussen, !- Layer 2
Iw Modulbackstein, !- Layer 3
Iw Verputz innen, !- Layer 4
Iw Wu innen; !- Layer
5
Construction,
Bodenflaeche g. Erdreich,!- Name
BgE Misapor, !- Outside Layer
BgE Betonplatten, !- Layer 2
BgE Flumroc, !- Layer 3
BgE Wu innen; !- Layer 4
Construction,
Bodenflaeche g. unb. Raeume, !- Name
BguR Wu aussen, !- Outside Layer
BguR Schichtex, !- Layer 2
BguR Stahlbeton, !- Layer 3
BguG Trittschaldpl, !- Layer 4
BguR Zementmörtel, !- Layer 5
BguR Wu innen; !- Layer 6
Construction,
Dach, !- Name
Dach Wu aussen, !- Outside Layer
Dach Ziegel, !- Layer 2
Dach Holz, !- Layer 3
Dach Lamitherm , !- Layer 4
Dach Wu innen; !- Layer 5
Construction,
Ceiling, !- Name
Ceiling perfect; !- Outside Layer
Construction,
Window, !- Name
window; !- Outside Layer
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION:INTERNALSOURCE ===========
Construction:InternalSource,
BodenEG with IS, !- Name
3, !- Source Present After Layer Number
3, !-
Temperature Calculation Requested After Layer Number
2, !- Dimensions for the CTF Calculation
0.3, !- Tube Spacing {m}
BgE Misapor, !- Outside Layer
BgE Betonplatten, !- Layer 2
BgE Flumroc, !- Layer 3
BgE Wu innen; !- Layer 4
Construction:InternalSource,
BodenOG with IS, !- Name
5, !- Source Present After Layer Number
5, !- Temperature Calculation Requested After Layer Number
2, !- Dimensions for the CTF Calculation
0.3, !- Tube Spacing {m}
BguR Wu aussen, !- Outside Layer
BguR Schichtex, !- Layer 2
BguR Stahlbeton, !- Layer 3
BguG Trittschaldpl, !- Layer 4
BguR Zementmörtel, !- Layer 5
BguR Wu innen; !- Layer 6
!- =========== ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
GlobalGeometryRules,
UpperLeftCorner, !- Starting Vertex Position
CounterClockWise, !- Vertex Entry Direction
Relative; !- Coordinate System
!- =========== ALL OBJECTS IN CLASS: ZONE
===========
Zone,
EG Zone, !- Name
0, !- Direction of Relative North {deg}
0, !- X Origin {m}
0, !- Y Origin {m}
0, !- Z Origin {m}
1, !- Type
1, !- Multiplier
autocalculate, !- Ceiling Height {m}
autocalculate; !- Volume {m3}
Zone,
UG Zone, !- Name
0, !- Direction of Relative North {deg}
0, !- X Origin {m}
0, !- Y Origin {m}
0, !- Z Origin {m}
1, !- Type
1, !- Multiplier
autocalculate, !- Ceiling Height {m}
autocalculate, !- Volume {m3}
, !- Zone Inside Convection Algorithm
, !- Zone Outside Convection Algorithm
Yes; !- Part of Total Floor Area
Zone,
OG Zone, !- Name
0, !- Direction of Relative North {deg}
0, !- X Origin {m}
0, !- Y Origin {m}
0, !- Z Origin {m}
1, !- Type
1, !- Multiplier
autocalculate, !- Ceiling Height {m}
autocalculate, !- Volume {m3}
, !- Zone Inside Convection Algorithm
, !- Zone Outside Convection
Algorithm
Yes; !- Part of Total Floor Area
!- =========== ALL OBJECTS IN CLASS: ZONELIST ===========
ZoneList,
house_susten, !- Zone List Name
EG Zone, !- Zone 1 Name
UG Zone, !- Zone 2 Name
OG Zone; !- Zone 3 Name
ZoneList,
EG and OG, !- Zone List Name
EG Zone, !- Zone 1 Name
OG Zone; !- Zone 2 Name
!- =========== ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
BuildingSurface:Detailed,
EG:Wall001, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of Vertices
0, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
0, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate
{m}
0, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
12.65, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Wall002, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of Vertices
12.65, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
12.65, !-
Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Wall003, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of Vertices
12.65, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Wall004, !-
Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of Vertices
9.82, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
9.82, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
11.77, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Wall005, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside
Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of Vertices
9.82, !- Vertex 1 X-coordinate {m}
11.77, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
9.82, !- Vertex 2 X-coordinate {m}
11.77, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
4.6, !- Vertex 3 X-coordinate {m}
11.77, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
4.6, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Wall006, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of
Vertices
4.6, !- Vertex 1 X-coordinate {m}
11.77, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
4.6, !- Vertex 2 X-coordinate {m}
11.77, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
4.6, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
4.6, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Wall007, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of Vertices
4.6, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
4.6, !- Vertex 2 X-coordinate
{m}
9.25, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
2.65, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Wall008, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
2.65, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
0,
!- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
5.6, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Wall009, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0.5000000, !- View Factor to Ground
4, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
0, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
0, !- Vertex 4 X-coordinate {m}
5.6, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate
{m}
BuildingSurface:Detailed,
EG:Wall010, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
0..5000000, !- View Factor to Ground
4, !- Number of Vertices
0, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
0, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
0, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
0, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Floor_unb, !- Name
Floor, !- Surface Type
BodenOG with IS, !- Construction Name
EG Zone, !- Zone Name
Surface, !- Outside
Boundary Condition
UG:Ceiling_keller, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
8, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
4.6, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
4.6, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
0, !- Vertex 4 Z-coordinate {m}
9.82, !- Vertex 5 X-coordinate {m}
11.77, !- Vertex 5 Y-coordinate {m}
0, !- Vertex 5 Z-coordinate {m}
9.82, !- Vertex 6 X-coordinate {m}
9.25, !- Vertex 6 Y-coordinate {m}
0, !- Vertex 6 Z-coordinate {m}
12.65, !- Vertex 7 X-coordinate {m}
9.25, !- Vertex 7 Y-coordinate {m}
0, !- Vertex 7
Z-coordinate {m}
12.65, !- Vertex 8 X-coordinate {m}
5.6, !- Vertex 8 Y-coordinate {m}
0; !- Vertex 8 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Floor_erd, !- Name
Floor, !- Surface Type
BodenEG with IS, !- Construction Name
EG Zone, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
4, !- Number of Vertices
0, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
0, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
12.65, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Wall001,
!- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
0, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
6.47, !- Vertex 1 Z-coordinate {m}
0, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
12.65, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
6.47; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Wall002, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside
Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
12.65, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
6.47, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
12.65, !- Vertex 4 X-coordinate {m}
5.6, !- Vertex 4 Y-coordinate {m}
5.86; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Wall003, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to
Ground
autocalculate, !- Number of Vertices
12.65, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
5.24, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
2.65, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
5.24; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Wall004, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
5.24, !-
Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
2.65, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
5.6, !- Vertex 4 Y-coordinate {m}
5.86; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Wall005, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
5.86, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate
{m}
0, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
0, !- Vertex 4 X-coordinate {m}
5.6, !- Vertex 4 Y-coordinate {m}
5.86; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Wall006, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
0, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
5..86, !- Vertex 1 Z-coordinate {m}
0, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
0, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
0, !- Vertex 4 X-coordinate {m}
0,
!- Vertex 4 Y-coordinate {m}
6.47; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Floor, !- Name
Floor, !- Surface Type
BodenOG with IS, !- Construction Name
OG Zone, !- Zone Name
Surface, !- Outside Boundary Condition
EG:Ceiling, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
6, !- Number of Vertices
0, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
0, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
2.65, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
2.94, !- Vertex 4 Z-coordinate {m}
12.65, !- Vertex 5 X-coordinate {m}
9.25, !- Vertex 5 Y-coordinate {m}
2.94, !-
Vertex 5 Z-coordinate {m}
12.65, !- Vertex 6 X-coordinate {m}
0, !- Vertex 6 Y-coordinate {m}
2.94; !- Vertex 6 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Roof_hoch, !- Name
Roof, !- Surface Type
Dach, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
0, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
6.47, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
6.47, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
5.86, !- Vertex 3 Z-coordinate {m}
0, !- Vertex 4 X-coordinate {m}
5.6, !- Vertex 4 Y-coordinate {m}
5.86; !- Vertex 4 Z-coordinate
{m}
BuildingSurface:Detailed,
UG:Wall001, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
-2.75, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
-2.75, !- Vertex 3 Z-coordinate {m}
12.65, !- Vertex 4 X-coordinate {m}
5.6, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall002, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone
Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
12.65, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
-2.75, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
-2.75, !- Vertex 3 Z-coordinate {m}
12.65, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall003, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind
Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
12.65, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
-2.75, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
-2.75, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall004, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
9.82, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1
Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
9.82, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
-2.75, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
11.77, !- Vertex 3 Y-coordinate {m}
-2.75, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall005, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
9.82, !- Vertex 1 X-coordinate {m}
11.77, !- Vertex 1 Y-coordinate {m}
1.32, !- Vertex 1 Z-coordinate {m}
9.82, !- Vertex 2 X-coordinate {m}
11.77, !- Vertex 2 Y-coordinate
{m}
-1.45, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
18.09, !- Vertex 3 Y-coordinate {m}
-1.45, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
18.09, !- Vertex 4 Y-coordinate {m}
1.32; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall006, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
9.82, !- Vertex 1 X-coordinate {m}
18.09, !- Vertex 1 Y-coordinate {m}
1.32, !- Vertex 1 Z-coordinate {m}
9.82, !- Vertex 2 X-coordinate {m}
18.09, !- Vertex 2 Y-coordinate {m}
-1.45, !- Vertex 2 Z-coordinate {m}
2.65, !- Vertex 3 X-coordinate {m}
18.09, !- Vertex 3 Y-coordinate {m}
-1.45,
!- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
18.09, !- Vertex 4 Y-coordinate {m}
1.32; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall007, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
18.09, !- Vertex 1 Y-coordinate {m}
1..32, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
18.09, !- Vertex 2 Y-coordinate {m}
-1.45, !- Vertex 2 Z-coordinate {m}
2.65, !- Vertex 3 X-coordinate {m}
11.77, !- Vertex 3 Y-coordinate {m}
-1.45, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
1.32; !- Vertex 4
Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall008, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
11.77, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
11.77, !- Vertex 2 Y-coordinate {m}
-2.75, !- Vertex 2 Z-coordinate {m}
2.65, !- Vertex 3 X-coordinate {m}
5.6, !- Vertex 3 Y-coordinate {m}
-2.75, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
5.6, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall009, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone
Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
11.77, !- Vertex 1 Y-coordinate {m}
-1.45, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
11.77, !- Vertex 2 Y-coordinate {m}
-2.75, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
11.77, !- Vertex 3 Y-coordinate {m}
-2.75, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
-1.45; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Wall010, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Zone, !- Outside Boundary Condition
EG Zone, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind
Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
11.77, !- Vertex 1 Y-coordinate {m}
1.32, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
11.77, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
11.77, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
1.32; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Floor_keller, !- Name
Floor, !- Surface Type
Bodenflaeche g. Erdreich,!- Construction Name
UG Zone, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
6, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
5.6, !-
Vertex 1 Y-coordinate {m}
-2.75, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
11.77, !- Vertex 2 Y-coordinate {m}
-2.75, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
11..77, !- Vertex 3 Y-coordinate {m}
-2.75, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
-2.75, !- Vertex 4 Z-coordinate {m}
12.65, !- Vertex 5 X-coordinate {m}
9.25, !- Vertex 5 Y-coordinate {m}
-2.75, !- Vertex 5 Z-coordinate {m}
12.65, !- Vertex 6 X-coordinate {m}
5.6, !- Vertex 6 Y-coordinate {m}
-2.75; !- Vertex 6 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Floor_garage, !- Name
Floor, !- Surface Type
Bodenflaeche g. Erdreich,!- Construction Name
UG Zone, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View
Factor to Ground
4, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
11.77, !- Vertex 1 Y-coordinate {m}
-1.45, !- Vertex 1 Z-coordinate {m}
2.65, !- Vertex 2 X-coordinate {m}
18.09, !- Vertex 2 Y-coordinate {m}
-1.45, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
18.09, !- Vertex 3 Y-coordinate {m}
-1.45, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
-1.45; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Roof_garage, !- Name
Roof, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
11.77, !- Vertex 1 Y-coordinate
{m}
1.32, !- Vertex 1 Z-coordinate {m}
9.82, !- Vertex 2 X-coordinate {m}
11.77, !- Vertex 2 Y-coordinate {m}
1.32, !- Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
18.09, !- Vertex 3 Y-coordinate {m}
1.32, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
18.09, !- Vertex 4 Y-coordinate {m}
1.32; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Roof_eingang, !- Name
Roof, !- Surface Type
Aussenwand, !- Construction Name
EG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
4.6, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
9.82, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
2.94, !-
Vertex 2 Z-coordinate {m}
9.82, !- Vertex 3 X-coordinate {m}
11.77, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
4.6, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Roof_bei_eingang, !- Name
Roof, !- Surface Type
Aussenwand, !- Construction Name
UG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
9.25, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
4.6, !- Vertex 2 X-coordinate {m}
9.25, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
4.6, !- Vertex 3 X-coordinate {m}
11.77, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate
{m}
2.65, !- Vertex 4 X-coordinate {m}
11.77, !- Vertex 4 Y-coordinate {m}
0; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
EG:Ceiling, !- Name
Ceiling, !- Surface Type
BodenOG with IS, !- Construction Name
EG Zone, !- Zone Name
Surface, !- Outside Boundary Condition
OG:Floor, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
6, !- Number of Vertices
0, !- Vertex 1 X-coordinate {m}
0, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
0, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
2.94, !- Vertex 4 Z-coordinate {m}
2.65, !- Vertex 5 X-coordinate
{m}
5.6, !- Vertex 5 Y-coordinate {m}
2.94, !- Vertex 5 Z-coordinate {m}
0, !- Vertex 6 X-coordinate {m}
5.6, !- Vertex 6 Y-coordinate {m}
2.94; !- Vertex 6 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Roof_tief, !- Name
Roof, !- Surface Type
Dach, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
5.86, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
5.86, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
5.24, !- Vertex 3 Z-coordinate {m}
2.65, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4
Y-coordinate {m}
5.24; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
OG:Wall007, !- Name
Wall, !- Surface Type
Aussenwand, !- Construction Name
OG Zone, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
autocalculate, !- Number of Vertices
12.65, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
5.86, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
12.65, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
5.24; !- Vertex 4 Z-coordinate {m}
BuildingSurface:Detailed,
UG:Ceiling_Keller, !- Name
Ceiling, !-
Surface Type
BodenOG with IS, !- Construction Name
UG Zone, !- Zone Name
Surface, !- Outside Boundary Condition
EG:Floor_erd, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
8, !- Number of Vertices
2.65, !- Vertex 1 X-coordinate {m}
5.6, !- Vertex 1 Y-coordinate {m}
0, !- Vertex 1 Z-coordinate {m}
12.65, !- Vertex 2 X-coordinate {m}
5.6, !- Vertex 2 Y-coordinate {m}
0, !- Vertex 2 Z-coordinate {m}
12.65, !- Vertex 3 X-coordinate {m}
9.25, !- Vertex 3 Y-coordinate {m}
0, !- Vertex 3 Z-coordinate {m}
9.82, !- Vertex 4 X-coordinate {m}
9.25, !- Vertex 4 Y-coordinate {m}
0, !- Vertex 4 Z-coordinate {m}
9.82, !- Vertex 5 X-coordinate {m}
11.77, !- Vertex 5 Y-coordinate {m}
0, !- Vertex 5 Z-coordinate {m}
4.6, !- Vertex 6 X-coordinate {m}
11.77, !- Vertex 6 Y-coordinate {m}
0, !- Vertex 6 Z-coordinate
{m}
4.6, !- Vertex 7 X-coordinate {m}
9.25, !- Vertex 7 Y-coordinate {m}
0, !- Vertex 7 Z-coordinate {m}
2.65, !- Vertex 8 X-coordinate {m}
9.25, !- Vertex 8 Y-coordinate {m}
0; !- Vertex 8 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: WINDOW ===========
Window,
ost_og_wall2_links, !- Name
Window, !- Construction Name
OG:Wall002, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
2.5, !- Starting X Coordinate {m}
0.85, !- Starting Z Coordinate {m}
0.8, !- Length {m}
1.3; !- Height {m}
Window,
ost_og_wall2_rechts, !- Name
Window, !- Construction Name
OG:Wall007, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
0.9, !- Starting X Coordinate {m}
0.85, !- Starting Z Coordinate {m}
2.1, !- Length {m}
1.3; !- Height {m}
Window,
ost_eg_wall2_links, !-
Name
Window, !- Construction Name
EG:Wall002, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
3, !- Starting X Coordinate {m}
0.1, !- Starting Z Coordinate {m}
0.8, !- Length {m}
2.2; !- Height {m}
Window,
ost_eg_wall2_rechts, !- Name
Window, !- Construction Name
EG:Wall002, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
6.5, !- Starting X Coordinate {m}
1.45, !- Starting Z Coordinate {m}
2, !- Length {m}
0.7; !- Height {m}
Window,
ost_eg_wall4, !- Name
Window, !- Construction Name
EG:Wall004, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
0.7, !- Starting X Coordinate {m}
0.1, !- Starting Z Coordinate {m}
0.8, !- Length {m}
2.2; !- Height {m}
Window,
ost_ug_garage, !- Name
Window, !- Construction
Name
UG:Wall005, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
2, !- Starting X Coordinate {m}
1.5, !- Starting Z Coordinate {m}
1.8, !- Length {m}
0.6; !- Height {m}
Window,
nord_og_wall3, !- Name
Window, !- Construction Name
OG:Wall003, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
6, !- Starting X Coordinate {m}
0.8, !- Starting Z Coordinate {m}
0.8, !- Length {m}
1.2; !- Height {m}
Window,
nord_eg_wall3, !- Name
Window, !- Construction Name
EG:Wall003, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
1, !- Starting X Coordinate {m}
0.5, !- Starting Z Coordinate {m}
1.2, !- Length {m}
2; !- Height {m}
Window,
nord_eg_wall5, !- Name
Window, !- Construction Name
EG:Wall005, !- Building Surface
Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
3, !- Starting X Coordinate {m}
1.5, !- Starting Z Coordinate {m}
1.8, !- Length {m}
0.6; !- Height {m}
Window,
west_og_wall4_links, !- Name
Window, !- Construction Name
OG:Wall004, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
0.3, !- Starting X Coordinate {m}
0.1, !- Starting Z Coordinate {m}
1.44, !- Length {m}
0.8; !- Height {m}
Window,
west_og_wall4_rechts, !- Name
Window, !- Construction Name
OG:Wall004, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
1.8, !- Starting X Coordinate {m}
0.1, !- Starting Z Coordinate {m}
0.8, !- Length {m}
2.4; !- Height {m}
Window,
west_og_wall6, !- Name
Window, !- Construction Name
OG:Wall006, !- Building Surface Name
, !- Shading
Control Name
, !- Frame and Divider Name
1, !- Multiplier
2, !- Starting X Coordinate {m}
0.8, !- Starting Z Coordinate {m}
0.96, !- Length {m}
1.3; !- Height {m}
Window,
west_eg_wall10, !- Name
Window, !- Construction Name
EG:Wall010, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
2, !- Starting X Coordinate {m}
0.1, !- Starting Z Coordinate {m}
3.26, !- Length {m}
2.2; !- Height {m}
Window,
nord_og_wall1_links, !- Name
Window, !- Construction Name
OG:Wall001, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
1.5, !- Starting X Coordinate {m}
0.2, !- Starting Z Coordinate {m}
1, !- Length {m}
1.94; !- Height {m}
Window,
nord_og_wall1_mitte, !- Name
Window, !- Construction Name
OG:Wall001, !- Building Surface Name
, !- Shading Control Name
, !-
Frame and Divider Name
1, !- Multiplier
4, !- Starting X Coordinate {m}
0.2, !- Starting Z Coordinate {m}
2.5, !- Length {m}
1.94; !- Height {m}
Window,
nord_og_wall1_rechtsklein, !- Name
Window, !- Construction Name
OG:Wall001, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
7.8, !- Starting X Coordinate {m}
0.8, !- Starting Z Coordinate {m}
0.6, !- Length {m}
1.3; !- Height {m}
Window,
nord_og_wall1_rechts, !- Name
Window, !- Construction Name
OG:Wall001, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
8.8, !- Starting X Coordinate {m}
0.2, !- Starting Z Coordinate {m}
2.5, !- Length {m}
1.94; !- Height {m}
Window,
nord_eg_wall1_links, !- Name
Window, !- Construction Name
EG:Wall001, !- Building Surface Name
, !- Shading Control Name
, !- Frame and
Divider Name
1, !- Multiplier
0.3, !- Starting X Coordinate {m}
0..1, !- Starting Z Coordinate {m}
3.4, !- Length {m}
2.2; !- Height {m}
Window,
nord_eg_wall1_mitte, !- Name
Window, !- Construction Name
EG:Wall001, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
4.8, !- Starting X Coordinate {m}
0.1, !- Starting Z Coordinate {m}
3.5, !- Length {m}
2.2; !- Height {m}
Window,
nord_eg_wall1_rechts, !- Name
Window, !- Construction Name
EG:Wall001, !- Building Surface Name
, !- Shading Control Name
, !- Frame and Divider Name
1, !- Multiplier
9.5, !- Starting X Coordinate {m}
0.1, !- Starting Z Coordinate {m}
1.96, !- Length {m}
2.2; !- Height {m}
!- =========== ALL OBJECTS IN CLASS: INTERNALMASS ===========
InternalMass,
internal_mass_UG, !- Name
Innenwand Treppe, !- Construction Name
UG Zone, !- Zone
Name
0.7; !- Surface Area {m2}
InternalMass,
internal_mass_EG, !- Name
Innenwand Treppe, !- Construction Name
EG Zone, !- Zone Name
0.525; !- Surface Area {m2}
InternalMass,
internal_mass_OG, !- Name
Innenwand Treppe, !- Construction Name
OG Zone, !- Zone Name
1.5; !- Surface Area {m2}
!- =========== ALL OBJECTS IN CLASS: SHADING:SITE:DETAILED ===========
Shading:Site:Detailed,
vordach_schatten, !- Name
, !- Transmittance Schedule Name
4, !- Number of Vertices
3.8, !- Vertex 1 X-coordinate {m}
-3.66, !- Vertex 1 Y-coordinate {m}
2.94, !- Vertex 1 Z-coordinate {m}
12, !- Vertex 2 X-coordinate {m}
-3.66, !- Vertex 2 Y-coordinate {m}
2.94, !- Vertex 2 Z-coordinate {m}
12, !- Vertex 3 X-coordinate {m}
0, !- Vertex 3 Y-coordinate {m}
2.94, !- Vertex 3 Z-coordinate {m}
3.8, !- Vertex 4 X-coordinate {m}
0, !- Vertex 4 Y-coordinate {m}
2.94; !- Vertex 4
Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: ZONEINFILTRATION:DESIGNFLOWRATE ===========
ZoneInfiltration:DesignFlowRate,
Zone Durchfluss EG, !- Name
EG Zone, !- Zone or ZoneList Name
Baseboard Operation Schedule, !- Schedule Name
Flow/Zone, !- Design Flow Rate Calculation Method
0.026903, !- Design Flow Rate {m3/s}
, !- Flow per Zone Floor Area {m3/s-m2}
, !- Flow per Exterior Surface Area {m3/s-m2}
, !- Air Changes per Hour
0, !- Constant Term Coefficient
0, !- Temperature Term Coefficient
0.2237, !- Velocity Term Coefficient
0; !- Velocity Squared Term Coefficient
ZoneInfiltration:DesignFlowRate,
Zone Durchfluss OG, !- Name
OG Zone, !- Zone or ZoneList Name
Baseboard Operation Schedule, !- Schedule Name
Flow/Zone, !- Design Flow Rate Calculation Method
0.028159, !- Design Flow Rate {m3/s}
, !- Flow per Zone Floor Area {m3/s-m2}
, !- Flow per Exterior Surface Area
{m3/s-m2}
, !- Air Changes per Hour
0, !- Constant Term Coefficient
0, !- Temperature Term Coefficient
0.2237, !- Velocity Term Coefficient
0; !- Velocity Squared Term Coefficient
!- =========== ALL OBJECTS IN CLASS: SIZING:ZONE ===========
Sizing:Zone,
EG Zone, !- Zone Name
14, !- Zone Cooling Design Supply Air Temperature {C}
30, !- Zone Heating Design Supply Air Temperature {C}
0.009, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
0.009, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
Flow/Person, !- Outdoor Air Method
0.00944, !- Outdoor Air Flow per Person {m3/s}
, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
, !- Outdoor Air Flow per Zone {m3/s}
, !- Zone Heating Sizing Factor
, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
, !- Cooling Design Air Flow Rate {m3/s}
0.000762, !- Cooling Minimum Air Flow per Zone
Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
, !- Cooling Minimum Air Flow Fraction
DesignDay, !- Heating Design Air Flow Method
, !- Heating Design Air Flow Rate {m3/s}
0.002032, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
0.1415762, !- Heating Maximum Air Flow {m3/s}
0.3; !- Heating Maximum Air Flow Fraction
Sizing:Zone,
OG Zone, !- Zone Name
14, !- Zone Cooling Design Supply Air Temperature {C}
30, !- Zone Heating Design Supply Air Temperature {C}
0.009, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
0.009, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
Flow/Person, !- Outdoor Air Method
0.00944, !- Outdoor Air Flow per Person {m3/s}
, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
, !- Outdoor Air Flow per Zone {m3/s}
, !- Zone Heating Sizing Factor
, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow
Method
, !- Cooling Design Air Flow Rate {m3/s}
0.000762, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
, !- Cooling Minimum Air Flow Fraction
DesignDay, !- Heating Design Air Flow Method
, !- Heating Design Air Flow Rate {m3/s}
0.002032, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
0.1415762, !- Heating Maximum Air Flow {m3/s}
0.3; !- Heating Maximum Air Flow Fraction
!- =========== ALL OBJECTS IN CLASS: SIZING:PLANT ===========
Sizing:Plant,
plant_bodenheizung, !- Plant or Condenser Loop Name
Heating, !- Loop Type
90, !- Design Loop Exit Temperature {C}
20; !- Loop Design Temperature Difference {deltaC}
!- =========== ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========
ZoneControl:Thermostat,
Zone One Control, !- Name
EG and OG, !- Zone or ZoneList Name
Zone One Control Type Schedule, !- Control Type Schedule
Name
ThermostatSetpoint:SingleHeating, !- Control 1 Object Type
Single Heating; !- Control 1 Name
!- =========== ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:SINGLEHEATING ===========
ThermostatSetpoint:SingleHeating,
Single Heating, !- Name
Heating Setpoint Schedule; !- Setpoint Temperature Schedule Name
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW ===========
ZoneHVAC:LowTemperatureRadiant:VariableFlow,
bodenheizung, !- Name
Baseboard Operation Schedule, !- Availability Schedule Name
EG Zone, !- Zone Name
EG:Floor_erd, !- Surface Name or Radiant Surface Group Name
0..013, !- Hydronic Tubing Inside Diameter {m}
60, !- Hydronic Tubing Length {m}
OperativeTemperature, !- Temperature Control Type
0.2, !- Maximum Hot Water Flow {m3/s}
boden_in, !- Heating Water Inlet Node Name
boden_out, !- Heating Water Outlet Node Name
0.5, !- Heating Control
Throttling Range {deltaC}
Baseboard Operation Schedule, !- Heating Control Temperature Schedule Name
, !- Maximum Cold Water Flow {m3/s}
, !- Cooling Water Inlet Node Name
, !- Cooling Water Outlet Node Name
, !- Cooling Control Throttling Range {deltaC}
, !- Cooling Control Temperature Schedule Name
SimpleOff, !- Condensation Control Type
1; !- Condensation Control Dewpoint Offset {C}
ZoneHVAC:LowTemperatureRadiant:VariableFlow,
bodenheizung2, !- Name
Baseboard Operation Schedule, !- Availability Schedule Name
OG Zone, !- Zone Name
OG:Floor, !- Surface Name or Radiant Surface Group Name
0.013, !- Hydronic Tubing Inside Diameter {m}
100, !- Hydronic Tubing Length {m}
OperativeTemperature, !- Temperature Control Type
0.2, !- Maximum Hot Water Flow {m3/s}
boden_in2, !- Heating Water Inlet Node Name
boden_out2, !- Heating Water Outlet Node Name
0.5, !- Heating Control Throttling Range
{deltaC}
Baseboard Operation Schedule, !- Heating Control Temperature Schedule Name
, !- Maximum Cold Water Flow {m3/s}
, !- Cooling Water Inlet Node Name
, !- Cooling Water Outlet Node Name
, !- Cooling Control Throttling Range {deltaC}
, !- Cooling Control Temperature Schedule Name
SimpleOff, !- Condensation Control Type
1; !- Condensation Control Dewpoint Offset {C}
ZoneHVAC:LowTemperatureRadiant:VariableFlow,
bodenheizung3, !- Name
Baseboard Operation Schedule, !- Availability Schedule Name
EG Zone, !- Zone Name
EG:Floor_unb, !- Surface Name or Radiant Surface Group Name
0.013, !- Hydronic Tubing Inside Diameter {m}
40, !- Hydronic Tubing Length {m}
OperativeTemperature, !- Temperature Control Type
0.2, !- Maximum Hot Water Flow {m3/s}
boden_in3, !- Heating Water Inlet Node Name
boden_out3, !- Heating Water Outlet Node Name
0.5, !- Heating Control Throttling Range {deltaC}
Baseboard
Operation Schedule, !- Heating Control Temperature Schedule Name
, !- Maximum Cold Water Flow {m3/s}
, !- Cooling Water Inlet Node Name
, !- Cooling Water Outlet Node Name
, !- Cooling Control Throttling Range {deltaC}
, !- Cooling Control Temperature Schedule Name
SimpleOff, !- Condensation Control Type
1; !- Condensation Control Dewpoint Offset {C}
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========
ZoneHVAC:EquipmentList,
Equiptment EG Bodenheizung, !- Name
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Zone Equipment 1 Object Type
bodenheizung, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Sequence
1, !- Zone Equipment 1 Heating or No-Load Sequence
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Zone Equipment 2 Object Type
bodenheizung3, !- Zone Equipment 2 Name
2, !- Zone Equipment 2 Cooling Sequence
2; !- Zone Equipment 2 Heating or No-Load
Sequence
ZoneHVAC:EquipmentList,
Equipment OG Bodenheizung, !- Name
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Zone Equipment 1 Object Type
bodenheizung2, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Sequence
1; !- Zone Equipment 1 Heating or No-Load Sequence
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========
ZoneHVAC:EquipmentConnections,
EG Zone, !- Zone Name
Equiptment EG Bodenheizung, !- Zone Conditioning Equipment List Name
, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
EG Zone Air Node, !- Zone Air Node Name
EG Zone return outlet; !- Zone Return Air Node Name
ZoneHVAC:EquipmentConnections,
OG Zone, !- Zone Name
Equipment OG Bodenheizung, !- Zone Conditioning Equipment List Name
, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
OG Zone Air Node, !- Zone Air
Node Name
OG Zone return outlet; !- Zone Return Air Node Name
!- =========== ALL OBJECTS IN CLASS: BRANCH ===========
Branch,
branch_boiler, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Boiler:HotWater, !- Component 1 Object Type
bodenheizung_boiler, !- Component 1 Name
boiler_in, !- Component 1 Inlet Node Name
boiler_out, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
branch_boden, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Component 1 Object Type
bodenheizung, !- Component 1 Name
boden_in, !- Component 1 Inlet Node Name
boden_out, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
branch_boden2, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve
Name
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Component 1 Object Type
bodenheizung2, !- Component 1 Name
boden_in2, !- Component 1 Inlet Node Name
boden_out2, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
branch_pipe_in, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pump:VariableSpeed, !- Component 1 Object Type
pumpe2, !- Component 1 Name
pumpe_in2, !- Component 1 Inlet Node Name
pipe_inletin2, !- Component 1 Outlet Node Name
Active, !- Component 1 Branch Control Type
Pipe:Adiabatic, !- Component 2 Object Type
pipe_inlet2, !- Component 2 Name
pipe_inletin2, !- Component 2 Inlet Node Name
pipe_inletout2, !- Component 2 Outlet Node Name
Passive; !- Component 2 Branch Control Type
Branch,
branch_pipe_out, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !-
Component 1 Object Type
pipe_outlet, !- Component 1 Name
pipe_outletin, !- Component 1 Inlet Node Name
pipe_outletout, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
branch_boden3, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Component 1 Object Type
bodenheizung3, !- Component 1 Name
boden_in3, !- Component 1 Inlet Node Name
boden_out3, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
HS Bypass Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Heating Supply Bypass, !- Component 1 Name
bypass_in, !- Component 1 Inlet Node Name
bypass_out, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
HS Outlet Branch, !-
Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
Heating Supply Outlet, !- Component 1 Name
outletpipe_in, !- Component 1 Inlet Node Name
outletpipe_out, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
pump_inlet, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pump:VariableSpeed, !- Component 1 Object Type
bodenheizung_pumpe, !- Component 1 Name
pumpe_in, !- Component 1 Inlet Node Name
pumpe_out, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
!- =========== ALL OBJECTS IN CLASS: BRANCHLIST ===========
BranchList,
branch_supply, !- Name
pump_inlet, !- Branch 1 Name
branch_boiler, !- Branch 2 Name
HS Bypass Branch, !- Branch 3 Name
HS Outlet Branch; !- Branch 4 Name
BranchList,
branch_demand, !-
Name
branch_pipe_in, !- Branch 1 Name
branch_boden, !- Branch 2 Name
branch_boden2, !- Branch 3 Name
branch_boden3, !- Branch 4 Name
branch_pipe_out; !- Branch 5 Name
!- =========== ALL OBJECTS IN CLASS: CONNECTOR:SPLITTER ===========
Connector:Splitter,
splitter1, !- Name
branch_pipe_in, !- Inlet Branch Name
branch_boden, !- Outlet Branch 1 Name
branch_boden2, !- Outlet Branch 2 Name
branch_boden3; !- Outlet Branch 3 Name
Connector:Splitter,
connector_bypass_split, !- Name
pump_inlet, !- Inlet Branch Name
branch_boiler, !- Outlet Branch 1 Name
HS Bypass Branch; !- Outlet Branch 2 Name
!- =========== ALL OBJECTS IN CLASS: CONNECTOR:MIXER ===========
Connector:Mixer,
connector_mixer, !- Name
branch_pipe_out, !- Outlet Branch Name
branch_boden, !- Inlet Branch 1 Name
branch_boden2, !- Inlet Branch 2 Name
branch_boden3; !- Inlet Branch 3
Name
Connector:Mixer,
connector_bypass_mix, !- Name
HS Outlet Branch, !- Outlet Branch Name
branch_boiler, !- Inlet Branch 1 Name
HS Bypass Branch; !- Inlet Branch 2 Name
!- =========== ALL OBJECTS IN CLASS: CONNECTORLIST ===========
ConnectorList,
connectorlist_split1, !- Name
Connector:Splitter, !- Connector 1 Object Type
splitter1, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
connector_mixer; !- Connector 2 Name
ConnectorList,
connectorlist_bypass, !- Name
Connector:Splitter, !- Connector 1 Object Type
connector_bypass_split, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
connector_bypass_mix; !- Connector 2 Name
!- =========== ALL OBJECTS IN CLASS: PIPE:ADIABATIC ===========
Pipe:Adiabatic,
pipe_outlet, !- Name
pipe_outletin, !- Inlet Node Name
pipe_outletout; !- Outlet Node Name
Pipe:Adiabatic,
pipe_inlet2, !-
Name
pipe_inletin2, !- Inlet Node Name
pipe_inletout2; !- Outlet Node Name
Pipe:Adiabatic,
Heating Supply Bypass, !- Name
bypass_in, !- Inlet Node Name
bypass_out; !- Outlet Node Name
Pipe:Adiabatic,
Heating Supply Outlet, !- Name
outletpipe_in, !- Inlet Node Name
outletpipe_out; !- Outlet Node Name
!- =========== ALL OBJECTS IN CLASS: PUMP:VARIABLESPEED ===========
Pump:VariableSpeed,
bodenheizung_pumpe, !- Name
pumpe_in, !- Inlet Node Name
pumpe_out, !- Outlet Node Name
autosize, !- Rated Flow Rate {m3/s}
179352, !- Rated Pump Head {Pa}
autosize, !- Rated Power Consumption {W}
0.8, !- Motor Efficiency
0, !- Fraction of Motor Inefficiencies to Fluid Stream
0, !- Coefficient 1 of the Part Load Performance Curve
0, !- Coefficient 2 of the Part Load Performance Curve
0, !- Coefficient 3 of the Part Load Performance Curve
0, !- Coefficient 4 of the Part Load Performance
Curve
0, !- Minimum Flow Rate {m3/s}
Intermittent; !- Pump Control Type
Pump:VariableSpeed,
pumpe2, !- Name
pumpe_in2, !- Inlet Node Name
pipe_inletin2, !- Outlet Node Name
autosize, !- Rated Flow Rate {m3/s}
179352, !- Rated Pump Head {Pa}
autosize, !- Rated Power Consumption {W}
0.8, !- Motor Efficiency
0, !- Fraction of Motor Inefficiencies to Fluid Stream
0, !- Coefficient 1 of the Part Load Performance Curve
0, !- Coefficient 2 of the Part Load Performance Curve
0, !- Coefficient 3 of the Part Load Performance Curve
0, !- Coefficient 4 of the Part Load Performance Curve
0, !- Minimum Flow Rate {m3/s}
Intermittent; !- Pump Control Type
!- =========== ALL OBJECTS IN CLASS: BOILER:HOTWATER ===========
Boiler:HotWater,
bodenheizung_boiler, !- Name
Electricity, !- Fuel Type
8000, !- Nominal Capacity {W}
1, !- Nominal Thermal Efficiency
, !- Normalized Boiler Efficiency
Curve Name
30, !- Design Water Outlet Temperature {C}
autosize, !- Design Water Flow Rate {m3/s}
0, !- Minimum Part Load Ratio
1.2, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
boiler_in, !- Boiler Water Inlet Node Name
boiler_out, !- Boiler Water Outlet Node Name
99.9, !- Water Outlet Upper Temperature Limit {C}
VariableFlow, !- Boiler Flow Mode
, !- Parasitic Electric Load {W}
1; !- Sizing Factor
!- =========== ALL OBJECTS IN CLASS: PLANTLOOP ===========
PlantLoop,
plant_bodenheizung, !- Name
Water, !- Fluid Type
Hot Loop Operation, !- Plant Equipment Operation Scheme Name
outletpipe_out, !- Loop Temperature Setpoint Node Name
100, !- Maximum Loop Temperature {C}
10, !- Minimum Loop Temperature {C}
autosize, !- Maximum Loop Flow Rate {m3/s}
0.0, !- Minimum Loop Flow Rate {m3/s}
autocalculate, !- Plant Loop Volume {m3}
pumpe_in, !- Plant Side Inlet Node
Name
outletpipe_out, !- Plant Side Outlet Node Name
branch_supply, !- Plant Side Branch List Name
connectorlist_bypass, !- Plant Side Connector List Name
pumpe_in2, !- Demand Side Inlet Node Name
pipe_outletout, !- Demand Side Outlet Node Name
branch_demand, !- Demand Side Branch List Name
connectorlist_split1, !- Demand Side Connector List Name
Sequential, !- Load Distribution Scheme
, !- Availability Manager List Name
SingleSetpoint, !- Plant Loop Demand Calculation Scheme
CommonPipe, !- Common Pipe Simulation
None; !- Pressure Simulation Type
!- =========== ALL OBJECTS IN CLASS: PLANTEQUIPMENTLIST ===========
PlantEquipmentList,
plant_bodenheizung, !- Name
Boiler:HotWater, !- Equipment 1 Object Type
bodenheizung_boiler; !- Equipment 1 Name
!- =========== ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATION:HEATINGLOAD
===========
PlantEquipmentOperation:HeatingLoad,
bodenheizung_heating_control, !- Name
0, !- Load Range 1 Lower Limit {W}
1000000, !- Load Range 1 Upper Limit {W}
plant_bodenheizung; !- Range 1 Equipment List Name
!- =========== ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATIONSCHEMES ===========
PlantEquipmentOperationSchemes,
Hot Loop Operation, !- Name
PlantEquipmentOperation:HeatingLoad, !- Control Scheme 1 Object Type
bodenheizung_heating_control, !- Control Scheme 1 Name
Baseboard Operation Schedule; !- Control Scheme 1 Schedule Name
!- =========== ALL OBJECTS IN CLASS: SETPOINTMANAGER:SCHEDULED ===========
SetpointManager:Scheduled,
Plant Manager, !- Name
Temperature, !- Control Variable
Baseboard Operation Schedule, !- Schedule Name
outletpipe_out; !- Setpoint Node or NodeList Name
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY
===========
Output:VariableDictionary,
regular; !- Key Field
!- =========== ALL OBJECTS IN CLASS: OUTPUT:SURFACES:DRAWING ===========
Output:Surfaces:Drawing,
DXF; !- Report Type
!- =========== ALL OBJECTS IN CLASS: OUTPUT:CONSTRUCTIONS ===========
Output:Constructions,
Constructions; !- Details Type 1
!- =========== ALL OBJECTS IN CLASS: OUTPUT:TABLE:SUMMARYREPORTS ===========
Output:Table:SummaryReports,
AllSummary; !- Report 1 Name
!- =========== ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE ===========
OutputControl:Table:Style,
TabAndHTML; !- Column Separator
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
Output:Variable,
*, !- Key Value
Zone Mean Air Temperature, !- Variable Name
hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Outdoor Dry Bulb , !- Variable Name
Hourly; !- Reporting
Frequency
Output:Variable,
*, !- Key Value
Wind Speed , !- Variable Name
Hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Diffuse Solar , !- Variable Name
Hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Pump Outlet Temp , !- Variable Name
Hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Boiler Water Mass Flow Rate , !- Variable Name
Hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Boiler Water Outlet Temp , !- Variable Name
Hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Plant Loop InletNode Flowrate , !- Variable Name
Hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Hydronic Low Temp Radiant Chilled Water Consumption , !- Variable Name
Hourly; !- Reporting Frequency
Output:Variable,
*, !- Key Value
Pump Mass Flow Rate , !- Variable
Name
Hourly; !- Reporting Frequency
!- =========== ALL OBJECTS IN CLASS: OUTPUT:SQLITE ===========
Output:SQLite,
Simple; !- Option Type