[EnergyPlus_Support] Re: Design heating load is zero
The temperature in certain zones, zone=1F19 OFFICE in your case, are above the heating set point. The temperature of a zone depends on heat transfers through the building envelope (walls, ceilings, floors) and the internal loads from people, equipment and lights. ooi
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Dora Chi 纪æ??å?? <dochido@...> wrote:
>
> I receive this warning for some of my zones:
>
> ** Warning ** Calculated design heating load for zone=1F19 OFFICE is zero.
> ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
>
> I do not get the same warning for all the zones, and I cannot find the logic
> why certain zones get this message. Please help, thanks!
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/
=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17300)
http://www.pctools.com/
=======