Dear Andrea,

The HX object is convinced that flows should never fall outside the 50-130% range. (I?m hoping that E+ improves this limitation in a future release, since it has caused me problems, too!) This calculation is based on the Air Loop flow at the HX.  If you are using a constant volume system, this should be easy to fix; one or more of your flows do not agree / coincide.



If you have a VAV system or are using an economizer with variable outdoor air flow across the HX, you?re not going to avoid these errors.  I don?t think the errors cause serious inaccuracies in the model, however, but I have not checked it in detail.



You may be able to add a zone HX which accomplishes the equivalent thermodynamic process, depending on the actual system you are attempting to model.



The Building Performance Team
James V. Dirkes II, P.E., LEED AP, BEMP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653



From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of andreacostaenergyplus
Sent: Friday, April 22, 2011 4:09 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: AHU with plate heat exchanger and no mixing box, possible?




__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=19957/stime=1303472942>

Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmcWZ1NHNjBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMDM0NzI5NDI->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkbmJtcmxlBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzAzNDcyOTQy>Visit Your Group  | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use  | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe

__,_._,___


=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17360)
<http://www.pctools.com/?cclick=EmailFooterClean_51>http://www.pctools.com
=======