There is another warning that the SEASONAL RESET SUPPLY AIR TEMP SCH is not used, when you turn on the Output Diagnostics for DisplayUnusedSchedules
ooi
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Álvaro Fialho <alvarofialho@...> wrote:
>
> Hello all,
>
> I was playing a bit with the sample Exercises provided in the "Getting
> started with EnergyPlus" document. And Exercise 2C (the most "complete"
> one) outputs a warning message (and some consequent error messages) that
> I don't know what to do. As a "learning exercise", could you please help
> me into solving this? It is important to let you know that I'm a
> computer scientist, with no experience at all (for the moment) with the
> design of HVAC systems :-) Thanks!
>
>
> Here goes the warning message:
>
> ** Warning ** Coil:Cooling:DX:SingleSpeed "NORTH ZONE UNITARY
> COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This
> indicates the possibility of coil frost/freeze. Outlet temperature = 1.29 C.
> ** ~~~ ** ...Occurrence info = Chicago Ohare Intl Ap IL USA
> TMY3 WMO#=725300, 04/25 14:00 - 14:15
> ** ~~~ ** ... Possible reasons for low outlet air dry-bulb
> temperatures are: This DX coil
> ** ~~~ ** 1) may have a low inlet air dry-bulb temperature.
> Inlet air temperature = 21.146 C.
> ** ~~~ ** 2) may have a low air flow rate per watt of cooling
> capacity. Check inputs.
> ** ~~~ ** 3) is used as part of a HX assisted cooling coil
> which uses a high sensible effectiveness. Check inputs.
>
>
>
> And the consequent error message:
>
> ************* ===== Recurring Error Summary =====
> ************* The following recurring error messages occurred.
> *************
> ************* ** Warning ** Coil:Cooling:DX:SingleSpeed "NORTH ZONE
> UNITARY COOLING COIL" - Full load outlet temperature indicates a
> possibility of frost/freeze error continues. Outlet air temperature
> statistics follow:
> ************* ** ~~~ ** This error occurred 46 total times;
> ************* ** ~~~ ** during Warmup 0 times;
> ************* ** ~~~ ** during Sizing 0 times.
> ************* ** ~~~ ** Max=1.986818 Min=0.362192
>
>
> Thanks lot!
> Álvaro.
>
> ps: I'm sending the IDF attached, although you might all have it in the
> Examples/BasicsFiles folder of your E+ installation.
>
> !-Generator IDFEditor 1.29a
> !-Option OriginalOrderTop UseSpecialFormat
> !-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
> !- Use '!' comments if they need to be retained when using the IDFEditor.
>
> Output:Variable,*,Zone/Sys Air Temperature,Monthly,Office Occupancy 2;
>
> Output:Table:Monthly,
> Zone Temperature Report, !- Name
> 2, !- Digits After Decimal
> Zone Mean Air Temperature, !- Variable or Meter 1 Name
> SumOrAverage, !- Aggregation Type for Variable or Meter 1
> Zone Mean Air Temperature, !- Variable or Meter 2 Name
> Maximum, !- Aggregation Type for Variable or Meter 2
> Zone Mean Air Temperature, !- Variable or Meter 3 Name
> Minimum, !- Aggregation Type for Variable or Meter 3
> Zone People Number of Occupants, !- Variable or Meter 4 Name
> HoursPositive, !- Aggregation Type for Variable or Meter 4
> Zone Mean Air Temperature, !- Variable or Meter 5 Name
> SumOrAverageDuringHoursShown, !- Aggregation Type for Variable or Meter 5
> Zone Mean Air Temperature, !- Variable or Meter 6 Name
> MaximumDuringHoursShown, !- Aggregation Type for Variable or Meter 6
> Zone Mean Air Temperature, !- Variable or Meter 7 Name
> MinimumDuringHoursShown; !- Aggregation Type for Variable or Meter 7
>
> HVACTemplate:System:VAV,
> VAV with Reheat, !- Name
> Office HVAC, !- System Availability Schedule Name
> autosize, !- Supply Fan Maximum Flow Rate {m3/s}
> autosize, !- Supply Fan Minimum Flow Rate {m3/s}
> 0.7, !- Supply Fan Total Efficiency
> 1000, !- Supply Fan Delta Pressure {Pa}
> 0.9, !- Supply Fan Motor Efficiency
> 1, !- Supply Fan Motor in Air Stream Fraction
> ChilledWater, !- Cooling Coil Type
> , !- Cooling Coil Availability Schedule Name
> , !- Cooling Coil Setpoint Schedule Name
> 13, !- Cooling Coil Design Setpoint {C}
> None, !- Heating Coil Type
> , !- Heating Coil Availability Schedule Name
> , !- Heating Coil Setpoint Schedule Name
> 10.0, !- Heating Coil Design Setpoint {C}
> 0.8, !- Gas Heating Coil Efficiency
> , !- Gas Heating Coil Parasitic Electric Load {W}
> None, !- Preheat Coil Type
> , !- Preheat Coil Availability Schedule Name
> , !- Preheat Coil Setpoint Schedule Name
> 7.2, !- Preheat Coil Design Setpoint {C}
> 0.8, !- Gas Preheat Coil Efficiency
> , !- Gas Preheat Coil Parasitic Electric Load {W}
> autosize, !- Maximum Outdoor Air Flow Rate {m3/s}
> autosize, !- Minimum Outdoor Air Flow Rate {m3/s}
> ProportionalMinimum, !- Minimum Outdoor Air Control Type
> Office Minimum OA, !- Minimum Outdoor Air Schedule Name
> FixedDryBulb, !- Economizer Type
> NoLockout, !- Economizer Lockout
> , !- Economizer Upper Temperature Limit {C}
> , !- Economizer Lower Temperature Limit {C}
> , !- Economizer Upper Enthalpy Limit {J/kg}
> , !- Supply Plenum Name
> PLENUM, !- Return Plenum Name
> DrawThrough, !- Supply Fan Placement
> InletVaneDampers, !- Supply Fan Part-Load Power Coefficients
> StayOff, !- Night Cycle Control
> , !- Night Cycle Control Zone Name
> None, !- Heat Recovery Type
> 0.7, !- Sensible Heat Recovery Effectiveness
> 0.65, !- Latent Heat Recovery Effectiveness
> None, !- Cooling Coil Setpoint Reset Type
> None, !- Heating Coil Setpoint Reset Type
> , !- Dehumidification Control Type
> , !- Dehumidification Control Zone Name
> , !- Dehumidification Setpoint {percent}
> , !- Humidifier Type
> , !- Humidifier Availability Schedule Name
> , !- Humidifier Rated Capacity {m3/s}
> , !- Humidifier Rated Electric Power {W}
> , !- Humidifier Control Zone Name
> ; !- Humidifier Setpoint {percent}
>
> HVACTemplate:Zone:VAV,
> SOUTH PERIMETER, !- Zone Name
> VAV with Reheat, !- Template VAV System Name
> Office Thermostat, !- Template Thermostat Name
> autosize, !- Supply Air Maximum Flow Rate {m3/s}
> , !- Zone Heating Sizing Factor
> , !- Zone Cooling Sizing Factor
> Constant, !- Zone Minimum Air Flow Input Method
> 0.2, !- Constant Minimum Air Flow Fraction
> , !- Fixed Minimum Air Flow Rate {m3/s}
> , !- Minimum Air Flow Fraction Schedule Name
> Flow/Person, !- Outdoor Air Method
> 0.00944, !- Outdoor Air Flow Rate per Person {m3/s}
> 0.0, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
> 0.0, !- Outdoor Air Flow Rate per Zone {m3/s}
> HotWater, !- Reheat Coil Type
> , !- Reheat Coil Availability Schedule Name
> Reverse, !- Damper Heating Action
> , !- Maximum Flow per Zone Floor Area During Reheat {m3/s-m2}
> , !- Maximum Flow Fraction During Reheat
> , !- Maximum Reheat Air Temperature {C}
> , !- Design Specification Outdoor Air Object Name
> , !- Supply Plenum Name
> , !- Return Plenum Name
> None, !- Baseboard Heating Type
> , !- Baseboard Heating Availability Schedule Name
> autosize; !- Baseboard Heating Capacity {W}
>
> HVACTemplate:Zone:VAV,
> EAST PERIMETER, !- Zone Name
> VAV with Reheat, !- Template VAV System Name
> Office Thermostat, !- Template Thermostat Name
> autosize, !- Supply Air Maximum Flow Rate {m3/s}
> , !- Zone Heating Sizing Factor
> , !- Zone Cooling Sizing Factor
> Constant, !- Zone Minimum Air Flow Input Method
> 0.2, !- Constant Minimum Air Flow Fraction
> , !- Fixed Minimum Air Flow Rate {m3/s}
> , !- Minimum Air Flow Fraction Schedule Name
> Flow/Person, !- Outdoor Air Method
> 0.00944, !- Outdoor Air Flow Rate per Person {m3/s}
> 0.0, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
> 0.0, !- Outdoor Air Flow Rate per Zone {m3/s}
> HotWater, !- Reheat Coil Type
> , !- Reheat Coil Availability Schedule Name
> Reverse, !- Damper Heating Action
> , !- Maximum Flow per Zone Floor Area During Reheat {m3/s-m2}
> , !- Maximum Flow Fraction During Reheat
> , !- Maximum Reheat Air Temperature {C}
> , !- Design Specification Outdoor Air Object Name
> , !- Supply Plenum Name
> , !- Return Plenum Name
> None, !- Baseboard Heating Type
> , !- Baseboard Heating Availability Schedule Name
> autosize; !- Baseboard Heating Capacity {W}
>
> HVACTemplate:Zone:VAV,
> WEST PERIMETER, !- Zone Name
> VAV with Reheat, !- Template VAV System Name
> Office Thermostat, !- Template Thermostat Name
> autosize, !- Supply Air Maximum Flow Rate {m3/s}
> , !- Zone Heating Sizing Factor
> , !- Zone Cooling Sizing Factor
> Constant, !- Zone Minimum Air Flow Input Method
> 0.2, !- Constant Minimum Air Flow Fraction
> , !- Fixed Minimum Air Flow Rate {m3/s}
> , !- Minimum Air Flow Fraction Schedule Name
> Flow/Person, !- Outdoor Air Method
> 0.00944, !- Outdoor Air Flow Rate per Person {m3/s}
> 0.0, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
> 0.0, !- Outdoor Air Flow Rate per Zone {m3/s}
> HotWater, !- Reheat Coil Type
> , !- Reheat Coil Availability Schedule Name
> Reverse, !- Damper Heating Action
> , !- Maximum Flow per Zone Floor Area During Reheat {m3/s-m2}
> , !- Maximum Flow Fraction During Reheat
> , !- Maximum Reheat Air Temperature {C}
> , !- Design Specification Outdoor Air Object Name
> , !- Supply Plenum Name
> , !- Return Plenum Name
> None, !- Baseboard Heating Type
> , !- Baseboard Heating Availability Schedule Name
> autosize; !- Baseboard Heating Capacity {W}
>
> HVACTemplate:Zone:VAV,
> CORE, !- Zone Name
> VAV with Reheat, !- Template VAV System Name
> Office Thermostat, !- Template Thermostat Name
> autosize, !- Supply Air Maximum Flow Rate {m3/s}
> , !- Zone Heating Sizing Factor
> , !- Zone Cooling Sizing Factor
> Constant, !- Zone Minimum Air Flow Input Method
> 0.2, !- Constant Minimum Air Flow Fraction
> , !- Fixed Minimum Air Flow Rate {m3/s}
> , !- Minimum Air Flow Fraction Schedule Name
> Flow/Person, !- Outdoor Air Method
> 0.00944, !- Outdoor Air Flow Rate per Person {m3/s}
> 0.0, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
> 0.0, !- Outdoor Air Flow Rate per Zone {m3/s}
> HotWater, !- Reheat Coil Type
> , !- Reheat Coil Availability Schedule Name
> Reverse, !- Damper Heating Action
> , !- Maximum Flow per Zone Floor Area During Reheat {m3/s-m2}
> , !- Maximum Flow Fraction During Reheat
> , !- Maximum Reheat Air Temperature {C}
> , !- Design Specification Outdoor Air Object Name
> , !- Supply Plenum Name
> , !- Return Plenum Name
> None, !- Baseboard Heating Type
> , !- Baseboard Heating Availability Schedule Name
> autosize; !- Baseboard Heating Capacity {W}
>
> HVACTemplate:Plant:ChilledWaterLoop,
> Chilled Water Plant, !- Name
> , !- Pump Schedule Name
> Intermittent, !- Pump Control Type
> Default, !- Chiller Plant Operation Scheme Type
> , !- Chiller Plant Equipment Operation Schemes Name
> , !- Chilled Water Setpoint Schedule Name
> 7.22, !- Chilled Water Design Setpoint {C}
> ConstantPrimaryNoSecondary, !- Chilled Water Pump Configuration
> 179352, !- Primary Chilled Water Pump Rated Head {Pa}
> 179352, !- Secondary Chilled Water Pump Rated Head {Pa}
> Default, !- Condenser Plant Operation Scheme Type
> , !- Condenser Equipment Operation Schemes Name
> SpecifiedSetpoint, !- Condenser Water Temperature Control Type
> , !- Condenser Water Setpoint Schedule Name
> 29.4, !- Condenser Water Design Setpoint {C}
> 179352, !- Condenser Water Pump Rated Head {Pa}
> None, !- Chilled Water Setpoint Reset Type
> 12.2, !- Chilled Water Setpoint at Outdoor Dry-Bulb Low {C}
> 15.6, !- Chilled Water Reset Outdoor Dry-Bulb Low {C}
> 6.7, !- Chilled Water Setpoint at Outdoor Dry-Bulb High {C}
> 26.7; !- Chilled Water Reset Outdoor Dry-Bulb High {C}
>
> HVACTemplate:Plant:Chiller,
> Chiller 1, !- Name
> ElectricReciprocatingChiller, !- Chiller Type
> autosize, !- Capacity {W}
> 3.6, !- Nominal COP {W/W}
> WaterCooled, !- Condenser Type
> , !- Priority
> 1.0; !- Sizing Factor
>
> HVACTemplate:Plant:Tower,
> Tower 1, !- Name
> TwoSpeed, !- Tower Type
> autosize, !- High Speed Nominal Capacity {W}
> autosize, !- High Speed Fan Power {W}
> autosize, !- Low Speed Nominal Capacity {W}
> autosize, !- Low Speed Fan Power {W}
> autosize, !- Free Convection Capacity {W}
> , !- Priority
> 1.0; !- Sizing Factor
>
> HVACTemplate:Plant:HotWaterLoop,
> Hot Water Plant, !- Name
> , !- Pump Schedule Name
> Intermittent, !- Pump Control Type
> Default, !- Hot Water Plant Operation Scheme Type
> , !- Hot Water Plant Equipment Operation Schemes Name
> , !- Hot Water Setpoint Schedule Name
> 82, !- Hot Water Design Setpoint {C}
> ConstantFlow, !- Hot Water Pump Configuration
> 179352, !- Hot Water Pump Rated Head {Pa}
> None, !- Hot Water Setpoint Reset Type
> 82.2, !- Hot Water Setpoint at Outdoor Dry-Bulb Low {C}
> -6.7, !- Hot Water Reset Outdoor Dry-Bulb Low {C}
> 65.6, !- Hot Water Setpoint at Outdoor Dry-Bulb High {C}
> 10; !- Hot Water Reset Outdoor Dry-Bulb High {C}
>
> HVACTemplate:Plant:Boiler,
> Boiler 1, !- Name
> HotWaterBoiler, !- Boiler Type
> autosize, !- Capacity {W}
> 0.8, !- Efficiency
> NaturalGas, !- Fuel Type
> , !- Priority
> 1.0; !- Sizing Factor
>
> Output:Variable,*,VAV Terminal Damper Position,Monthly;
>
> Output:Variable,*,Chiller Evap Heat Trans Rate,Monthly;
>
> Output:Variable,*,Chiller COP,Monthly;
>
> Output:Variable,*,Boiler Heating Output Rate,Monthly;
>
> Output:Variable,*,Tower Heat Transfer,Monthly;
>
> Output:Variable,*,Furnace Fan Part-Load Ratio,Monthly;
>
> Output:Variable,*,DX Cooling Coil Runtime Fraction,Monthly;
>
> Output:Variable,*,Heating Coil Runtime Fraction,Monthly;
>
> HVACTemplate:System:Unitary,
> North Zone Unitary, !- Name
> Office HVAC, !- System Availability Schedule Name
> NORTH PERIMETER, !- Control Zone or Thermostat Location Name
> autosize, !- Supply Fan Maximum Flow Rate {m3/s}
> Continuous, !- Supply Fan Operating Mode Schedule Name
> 0.7, !- Supply Fan Total Efficiency
> 600, !- Supply Fan Delta Pressure {Pa}
> 0.9, !- Supply Fan Motor Efficiency
> 1, !- Supply Fan Motor in Air Stream Fraction
> SingleSpeedDX, !- Cooling Coil Type
> , !- Cooling Coil Availability Schedule Name
> autosize, !- Cooling Coil Capacity {W}
> autosize, !- Cooling Coil Rated Sensible Heat Ratio
> 3, !- Cooling Coil Rated COP
> Gas, !- Heating Coil Type
> , !- Heating Coil Availability Schedule Name
> autosize, !- Heating Coil Capacity {W}
> 0.8, !- Gas Heating Coil Efficiency
> , !- Gas Heating Coil Parasitic Electric Load {W}
> autosize, !- Maximum Outdoor Air Flow Rate {m3/s}
> autosize, !- Minimum Outdoor Air Flow Rate {m3/s}
> Office Minimum OA, !- Minimum Outdoor Air Schedule Name
> NoEconomizer, !- Economizer Type
> NoLockout, !- Economizer Lockout
> , !- Economizer Upper Temperature Limit {C}
> , !- Economizer Lower Temperature Limit {C}
> , !- Economizer Upper Enthalpy Limit {J/kg}
> , !- Supply Plenum Name
> , !- Return Plenum Name
> BlowThrough, !- Supply Fan Placement
> StayOff, !- Night Cycle Control
> , !- Night Cycle Control Zone Name
> None, !- Heat Recovery Type
> 0.7, !- Sensible Heat Recovery Effectiveness
> 0.65, !- Latent Heat Recovery Effectiveness
> , !- Dehumidification Control Type
> , !- Dehumidification Control Zone Name
> , !- Dehumidification Setpoint {percent}
> , !- Humidifier Type
> , !- Humidifier Availability Schedule Name
> , !- Humidifier Rated Capacity {m3/s}
> , !- Humidifier Rated Electric Power {W}
> , !- Humidifier Control Zone Name
> ; !- Humidifier Setpoint {percent}
>
> Sizing:Parameters,
> 1.2, !- Heating Sizing Factor
> 1.2; !- Cooling Sizing Factor
>
> HVACTemplate:Thermostat,
> Office Thermostat, !- Name
> Office Heating Setpoints,!- Heating Setpoint Schedule Name
> , !- Constant Heating Setpoint {C}
> Office Cooling Setpoints,!- Cooling Setpoint Schedule Name
> ; !- Constant Cooling Setpoint {C}
>
> HVACTemplate:Zone:Unitary,
> NORTH PERIMETER, !- Zone Name
> North Zone Unitary, !- Template Unitary System Name
> Office Thermostat, !- Template Thermostat Name
> autosize, !- Supply Air Maximum Flow Rate {m3/s}
> , !- Zone Heating Sizing Factor
> , !- Zone Cooling Sizing Factor
> Flow/Person, !- Outdoor Air Method
> 0.00944, !- Outdoor Air Flow Rate per Person {m3/s}
> 0.0, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
> 0.0, !- Outdoor Air Flow Rate per Zone {m3/s}
> , !- Supply Plenum Name
> , !- Return Plenum Name
> None, !- Baseboard Heating Type
> , !- Baseboard Heating Availability Schedule Name
> autosize; !- Baseboard Heating Capacity {W}
>
> ! Introduction to EnergyPlus - Exercise 2C
> !
> ! Building: Single floor rectangular building 30.5 m (100 ft) x 15.2 m (50 ft). 5 zones -
> ! 4 exterior, 1 interior, zone height 2.4 m (8 ft). Exterior zone
> ! depth is 3.7 m (12 ft). There is a 0.6 m (2 ft) high return plenum. The
> ! overall building height is 3m (10 ft). There are windows on
> ! all 4 facades; the south and north facades have glass doors.
> ! The south facing glass is shaded by overhangs. The walls
> ! are woodshingle over plywood, R11 insulation, and gypboard.
> ! The roof is a gravel built up roof with mineral board
> ! insulation and plywood sheathing. The floor slab is 0.1 m (4 in)
> ! of heavy concrete. The windows and glass doors are double
> ! pane Low-e clear glass with argon gap. The window to wall ratio is
> ! approximately 0.3.
> !
> ! The building is oriented with the long axis running east-west.
> !
> ! Floor Area: 463.6 m2 (5000 ft2)
> !
> ! Internal: Lighting is 16 W/m2 (1.5 W/ft2), office equip is 10.8 W/m2 (1.0 W/ft2).
> ! 1 occupant per 9.3 m2 (100 ft2) of floor area. The
> ! Infiltration is 0.25 air changes per hour.
> !
> ! HVAC: Single-zone unitary with DX cooling and gas heating serving NORTH PERIMETER zone.
> ! VAV with hot water reheat, return plenum, chiller, boiler, and tower serving
> ! the other four occupied zones.
> !
> ! Environment: Chicago, IL, USA, TMY2
> !
> !
>
> VERSION,6.0;
>
> Building,
> Exercise 2C, !- Name
> 0.0, !- North Axis {deg}
> City, !- Terrain
> 0.04, !- Loads Convergence Tolerance Value
> 0.4, !- Temperature Convergence Tolerance Value {deltaC}
> FullInteriorAndExterior, !- Solar Distribution
> ; !- Maximum Number of Warmup Days
>
> Timestep,4;
>
> SurfaceConvectionAlgorithm:Inside,Simple;
>
> SurfaceConvectionAlgorithm:Outside,SimpleCombined;
>
> HeatBalanceAlgorithm,ConductionTransferFunction;
>
> ZoneCapacitanceMultiplier:ResearchSpecial,
> 1, !- Temperature Capacity Multiplier
> 1, !- Humidity Capacity Multiplier
> 1; !- Carbon Dioxide Capacity Multiplier
>
> SimulationControl,
> Yes, !- Do Zone Sizing Calculation
> Yes, !- Do System Sizing Calculation
> Yes, !- Do Plant Sizing Calculation
> No, !- Run Simulation for Sizing Periods
> Yes; !- Run Simulation for Weather File Run Periods
>
> RunPeriod,
> , !- Name
> 1, !- Begin Month
> 1, !- Begin Day of Month
> 12, !- End Month
> 31, !- End Day of Month
> UseWeatherFile, !- Day of Week for Start Day
> Yes, !- Use Weather File Holidays and Special Days
> Yes, !- Use Weather File Daylight Saving Period
> No, !- Apply Weekend Holiday Rule
> Yes, !- Use Weather File Rain Indicators
> Yes, !- Use Weather File Snow Indicators
> 1; !- Number of Times Runperiod to be Repeated
>
> Site:Location,
> CHICAGO_IL_USA TMY2-94846, !- Name
> 41.78, !- Latitude {deg}
> -87.75, !- Longitude {deg}
> -6.00, !- Time Zone {hr}
> 190.00; !- Elevation {m}
>
> ! CHICAGO_IL_USA Heating 99%, MaxDB= -18.10°C
>
> SizingPeriod:DesignDay,
> CHICAGO_IL_USA Heating 99% Conditions, !- Name
> -18.10, !- Maximum Dry-Bulb Temperature {C}
> 0.00, !- Daily Temperature Range {deltaC}
> -18.10, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 99063., !- Barometric Pressure {Pa}
> 4.60, !- Wind Speed {m/s}
> 270.00, !- Wind Direction {deg}
> 0.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 1, !- Month
> WinterDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> ! CHICAGO_IL_USA Cooling (DB=>MWB) 1%, MaxDB= 31.30°C MWB= 22.80°C
>
> SizingPeriod:DesignDay,
> CHICAGO_IL_USA Cooling 1% Conditions DB=>MWB, !- Name
> 31.30, !- Maximum Dry-Bulb Temperature {C}
> 10.90, !- Daily Temperature Range {deltaC}
> 22.80, !- Humidity Indicating Conditions at Maximum Dry-Bulb
> 99063., !- Barometric Pressure {Pa}
> 5.40, !- Wind Speed {m/s}
> 230.00, !- Wind Direction {deg}
> 1.00, !- Sky Clearness
> 0, !- Rain Indicator
> 0, !- Snow Indicator
> 21, !- Day of Month
> 7, !- Month
> SummerDesignDay, !- Day Type
> 0, !- Daylight Saving Time Indicator
> WetBulb; !- Humidity Indicating Type
>
> Site:GroundTemperature:BuildingSurface,20.4,20.4,20.4,20.4,21.5,22.7,22.9,23.0,23.0,21.9,20.7,20.5;
>
> Material,
> WD10, !- Name
> MediumSmooth, !- Roughness
> 0.667, !- Thickness {m}
> 0.115, !- Conductivity {W/m-K}
> 513, !- Density {kg/m3}
> 1381, !- Specific Heat {J/kg-K}
> 0.9, !- Thermal Absorptance
> 0.78, !- Solar Absorptance
> 0.78; !- Visible Absorptance
>
> Material,
> RG01, !- Name
> Rough, !- Roughness
> 1.2700000E-02, !- Thickness {m}
> 1.442000, !- Conductivity {W/m-K}
> 881.0000, !- Density {kg/m3}
> 1674.000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.6500000, !- Solar Absorptance
> 0.6500000; !- Visible Absorptance
>
> Material,
> BR01, !- Name
> VeryRough, !- Roughness
> 9.4999997E-03, !- Thickness {m}
> 0.1620000, !- Conductivity {W/m-K}
> 1121.000, !- Density {kg/m3}
> 1464.000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.7000000, !- Solar Absorptance
> 0.7000000; !- Visible Absorptance
>
> Material,
> IN46, !- Name
> VeryRough, !- Roughness
> 7.6200001E-02, !- Thickness {m}
> 2.3000000E-02, !- Conductivity {W/m-K}
> 24.00000, !- Density {kg/m3}
> 1590.000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.5000000, !- Solar Absorptance
> 0.5000000; !- Visible Absorptance
>
> Material,
> WD01, !- Name
> MediumSmooth, !- Roughness
> 1.9099999E-02, !- Thickness {m}
> 0.1150000, !- Conductivity {W/m-K}
> 513.0000, !- Density {kg/m3}
> 1381.000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.7800000, !- Solar Absorptance
> 0.7800000; !- Visible Absorptance
>
> Material,
> PW03, !- Name
> MediumSmooth, !- Roughness
> 1.2700000E-02, !- Thickness {m}
> 0.1150000, !- Conductivity {W/m-K}
> 545.0000, !- Density {kg/m3}
> 1213.000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.7800000, !- Solar Absorptance
> 0.7800000; !- Visible Absorptance
>
> Material,
> IN02, !- Name
> Rough, !- Roughness
> 9.0099998E-02, !- Thickness {m}
> 4.3000001E-02, !- Conductivity {W/m-K}
> 10.00000, !- Density {kg/m3}
> 837.0000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.7500000, !- Solar Absorptance
> 0.7500000; !- Visible Absorptance
>
> Material,
> GP01, !- Name
> MediumSmooth, !- Roughness
> 1.2700000E-02, !- Thickness {m}
> 0.1600000, !- Conductivity {W/m-K}
> 801.0000, !- Density {kg/m3}
> 837.0000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.7500000, !- Solar Absorptance
> 0.7500000; !- Visible Absorptance
>
> Material,
> GP02, !- Name
> MediumSmooth, !- Roughness
> 1.5900001E-02, !- Thickness {m}
> 0.1600000, !- Conductivity {W/m-K}
> 801.0000, !- Density {kg/m3}
> 837.0000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.7500000, !- Solar Absorptance
> 0.7500000; !- Visible Absorptance
>
> Material,
> CC03, !- Name
> MediumRough, !- Roughness
> 0.1016000, !- Thickness {m}
> 1.310000, !- Conductivity {W/m-K}
> 2243.000, !- Density {kg/m3}
> 837.0000, !- Specific Heat {J/kg-K}
> 0.9000000, !- Thermal Absorptance
> 0.6500000, !- Solar Absorptance
> 0.6500000; !- Visible Absorptance
>
> Material:NoMass,
> CP01, !- Name
> Rough, !- Roughness
> 0.3670000, !- Thermal Resistance {m2-K/W}
> 0.9000000, !- Thermal Absorptance
> 0.7500000, !- Solar Absorptance
> 0.7500000; !- Visible Absorptance
>
> Material:NoMass,
> MAT-SB-U, !- Name
> Rough, !- Roughness
> 0.117406666, !- Thermal Resistance {m2-K/W}
> 0.65, !- Thermal Absorptance
> 0.65, !- Solar Absorptance
> 0.65; !- Visible Absorptance
>
> Material:NoMass,
> MAT-CLNG-1, !- Name
> Rough, !- Roughness
> 0.652259290, !- Thermal Resistance {m2-K/W}
> 0.65, !- Thermal Absorptance
> 0.65, !- Solar Absorptance
> 0.65; !- Visible Absorptance
>
> Material:NoMass,
> MAT-FLOOR-1, !- Name
> Rough, !- Roughness
> 3.522199631, !- Thermal Resistance {m2-K/W}
> 0.65, !- Thermal Absorptance
> 0.65, !- Solar Absorptance
> 0.65; !- Visible Absorptance
>
> Material:AirGap,
> AL21, !- Name
> 0.1570000; !- Thermal Resistance {m2-K/W}
>
> Material:AirGap,
> AL23, !- Name
> 0.1530000; !- Thermal Resistance {m2-K/W}
>
> WindowMaterial:Glazing,
> CLEAR 3MM, !- Name
> SpectralAverage, !- Optical Data Type
> , !- Window Glass Spectral Data Set Name
> 0.003, !- Thickness {m}
> 0.837, !- Solar Transmittance at Normal Incidence
> 0.075, !- Front Side Solar Reflectance at Normal Incidence
> 0.075, !- Back Side Solar Reflectance at Normal Incidence
> 0.898, !- Visible Transmittance at Normal Incidence
> 0.081, !- Front Side Visible Reflectance at Normal Incidence
> 0.081, !- Back Side Visible Reflectance at Normal Incidence
> 0.0, !- Infrared Transmittance at Normal Incidence
> 0.84, !- Front Side Infrared Hemispherical Emissivity
> 0.84, !- Back Side Infrared Hemispherical Emissivity
> 0.9; !- Conductivity {W/m-K}
>
> WindowMaterial:Glazing,
> GREY 3MM, !- Name
> SpectralAverage, !- Optical Data Type
> , !- Window Glass Spectral Data Set Name
> 0.003, !- Thickness {m}
> 0.626, !- Solar Transmittance at Normal Incidence
> 0.061, !- Front Side Solar Reflectance at Normal Incidence
> 0.061, !- Back Side Solar Reflectance at Normal Incidence
> 0.611, !- Visible Transmittance at Normal Incidence
> 0.061, !- Front Side Visible Reflectance at Normal Incidence
> 0.061, !- Back Side Visible Reflectance at Normal Incidence
> 0.0, !- Infrared Transmittance at Normal Incidence
> 0.84, !- Front Side Infrared Hemispherical Emissivity
> 0.84, !- Back Side Infrared Hemispherical Emissivity
> 0.9; !- Conductivity {W/m-K}
>
> WindowMaterial:Glazing,
> CLEAR 6MM, !- Name
> SpectralAverage, !- Optical Data Type
> , !- Window Glass Spectral Data Set Name
> 0.006, !- Thickness {m}
> 0.775, !- Solar Transmittance at Normal Incidence
> 0.071, !- Front Side Solar Reflectance at Normal Incidence
> 0.071, !- Back Side Solar Reflectance at Normal Incidence
> 0.881, !- Visible Transmittance at Normal Incidence
> 0.080, !- Front Side Visible Reflectance at Normal Incidence
> 0.080, !- Back Side Visible Reflectance at Normal Incidence
> 0.0, !- Infrared Transmittance at Normal Incidence
> 0.84, !- Front Side Infrared Hemispherical Emissivity
> 0.84, !- Back Side Infrared Hemispherical Emissivity
> 0.9; !- Conductivity {W/m-K}
>
> WindowMaterial:Glazing,
> LoE CLEAR 6MM, !- Name
> SpectralAverage, !- Optical Data Type
> , !- Window Glass Spectral Data Set Name
> 0.006, !- Thickness {m}
> 0.600, !- Solar Transmittance at Normal Incidence
> 0.170, !- Front Side Solar Reflectance at Normal Incidence
> 0.220, !- Back Side Solar Reflectance at Normal Incidence
> 0.840, !- Visible Transmittance at Normal Incidence
> 0.055, !- Front Side Visible Reflectance at Normal Incidence
> 0.078, !- Back Side Visible Reflectance at Normal Incidence
> 0.0, !- Infrared Transmittance at Normal Incidence
> 0.84, !- Front Side Infrared Hemispherical Emissivity
> 0.10, !- Back Side Infrared Hemispherical Emissivity
> 0.9; !- Conductivity {W/m-K}
>
> WindowMaterial:Gas,
> AIR 6MM, !- Name
> Air, !- Gas Type
> 0.0063; !- Thickness {m}
>
> WindowMaterial:Gas,
> AIR 13MM, !- Name
> Air, !- Gas Type
> 0.0127; !- Thickness {m}
>
> WindowMaterial:Gas,
> ARGON 13MM, !- Name
> Argon, !- Gas Type
> 0.0127; !- Thickness {m}
>
> Construction,
> ROOF-1, !- Name
> RG01, !- Outside Layer
> BR01, !- Layer 2
> IN46, !- Layer 3
> WD01; !- Layer 4
>
> Construction,
> WALL-1, !- Name
> WD01, !- Outside Layer
> PW03, !- Layer 2
> IN02, !- Layer 3
> GP01; !- Layer 4
>
> Construction,
> CLNG-1, !- Name
> MAT-CLNG-1; !- Outside Layer
>
> Construction,
> SB-U, !- Name
> MAT-SB-U; !- Outside Layer
>
> Construction,
> FLOOR-1, !- Name
> MAT-FLOOR-1; !- Outside Layer
>
> Construction,
> FLOOR-SLAB-1, !- Name
> CC03; !- Outside Layer
>
> Construction,
> INT-WALL-1, !- Name
> GP02, !- Outside Layer
> AL21, !- Layer 2
> GP02; !- Layer 3
>
> Construction,
> Double LoE Clear Argon, !- Name
> LoE CLEAR 6MM, !- Outside Layer
> ARGON 13MM, !- Layer 2
> CLEAR 6MM; !- Layer 3
>
> Zone,
> PLENUM, !- Name
> 0, !- Direction of Relative North {deg}
> 0, !- X Origin {m}
> 0, !- Y Origin {m}
> 0, !- Z Origin {m}
> 1, !- Type
> 1, !- Multiplier
> 0.609600067, !- Ceiling Height {m}
> 283.2, !- Volume {m3}
> , !- Zone Inside Convection Algorithm
> , !- Zone Outside Convection Algorithm
> No; !- Part of Total Floor Area
>
> Zone,
> SOUTH PERIMETER, !- Name
> 0, !- Direction of Relative North {deg}
> 0, !- X Origin {m}
> 0, !- Y Origin {m}
> 0, !- Z Origin {m}
> 1, !- Type
> 1, !- Multiplier
> 2.438400269, !- Ceiling Height {m}
> 239.247360229, !- Volume {m3}
> , !- Zone Inside Convection Algorithm
> , !- Zone Outside Convection Algorithm
> Yes; !- Part of Total Floor Area
>
> Zone,
> EAST PERIMETER, !- Name
> 0, !- Direction of Relative North {deg}
> 0, !- X Origin {m}
> 0, !- Y Origin {m}
> 0, !- Z Origin {m}
> 1, !- Type
> 1, !- Multiplier
> 2.438400269, !- Ceiling Height {m}
> 103.311355591, !- Volume {m3}
> , !- Zone Inside Convection Algorithm
> , !- Zone Outside Convection Algorithm
> Yes; !- Part of Total Floor Area
>
> Zone,
> NORTH PERIMETER, !- Name
> 0, !- Direction of Relative North {deg}
> 0, !- X Origin {m}
> 0, !- Y Origin {m}
> 0, !- Z Origin {m}
> 1, !- Type
> 1, !- Multiplier
> 2.438400269, !- Ceiling Height {m}
> 239.247360229, !- Volume {m3}
> , !- Zone Inside Convection Algorithm
> , !- Zone Outside Convection Algorithm
> Yes; !- Part of Total Floor Area
>
> Zone,
> WEST PERIMETER, !- Name
> 0, !- Direction of Relative North {deg}
> 0, !- X Origin {m}
> 0, !- Y Origin {m}
> 0, !- Z Origin {m}
> 1, !- Type
> 1, !- Multiplier
> 2.438400269, !- Ceiling Height {m}
> 103.311355591, !- Volume {m3}
> , !- Zone Inside Convection Algorithm
> , !- Zone Outside Convection Algorithm
> Yes; !- Part of Total Floor Area
>
> Zone,
> CORE, !- Name
> 0, !- Direction of Relative North {deg}
> 0, !- X Origin {m}
> 0, !- Y Origin {m}
> 0, !- Z Origin {m}
> 1, !- Type
> 1, !- Multiplier
> 2.438400269, !- Ceiling Height {m}
> 447.682556152, !- Volume {m3}
> , !- Zone Inside Convection Algorithm
> , !- Zone Outside Convection Algorithm
> Yes; !- Part of Total Floor Area
>
> GlobalGeometryRules,
> UpperLeftCorner, !- Starting Vertex Position
> Counterclockwise, !- Vertex Entry Direction
> Relative; !- Coordinate System
>
> BuildingSurface:Detailed,
> WALL-1PF, !- Name
> Wall, !- Surface Type
> WALL-1, !- Construction Name
> PLENUM, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.50000, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.0,0.0,3.0, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,0.0,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,0.0,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,0.0,3.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> WALL-1PR, !- Name
> Wall, !- Surface Type
> WALL-1, !- Construction Name
> PLENUM, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.50000, !- View Factor to Ground
> 4, !- Number of Vertices
> 30.5,0.0,3.0, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,0.0,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,15.2,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,15.2,3.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> WALL-1PB, !- Name
> Wall, !- Surface Type
> WALL-1, !- Construction Name
> PLENUM, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.50000, !- View Factor to Ground
> 4, !- Number of Vertices
> 30.5,15.2,3.0, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,15.2,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,15.2,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 0.0,15.2,3.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> WALL-1PL, !- Name
> Wall, !- Surface Type
> WALL-1, !- Construction Name
> PLENUM, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.50000, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.0,15.2,3.0, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,15.2,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,0.0,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 0.0,0.0,3.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> TOP-1, !- Name
> Roof, !- Surface Type
> ROOF-1, !- Construction Name
> PLENUM, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.00000, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.0,15.2,3.0, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,0.0,3.0, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,0.0,3.0, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,15.2,3.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C1-1P, !- Name
> Floor, !- Surface Type
> CLNG-1, !- Construction Name
> PLENUM, !- Zone Name
> Surface, !- Outside Boundary Condition
> C1-1, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,0.0,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,0.0,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C2-1P, !- Name
> Floor, !- Surface Type
> CLNG-1, !- Construction Name
> PLENUM, !- Zone Name
> Surface, !- Outside Boundary Condition
> C2-1, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,15.2,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,0.0,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C3-1P, !- Name
> Floor, !- Surface Type
> CLNG-1, !- Construction Name
> PLENUM, !- Zone Name
> Surface, !- Outside Boundary Condition
> C3-1, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,11.6,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,15.2,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,15.2,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C4-1P, !- Name
> Floor, !- Surface Type
> CLNG-1, !- Construction Name
> PLENUM, !- Zone Name
> Surface, !- Outside Boundary Condition
> C4-1, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,0.0,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,15.2,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C5-1P, !- Name
> Floor, !- Surface Type
> CLNG-1, !- Construction Name
> PLENUM, !- Zone Name
> Surface, !- Outside Boundary Condition
> C5-1, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 26.8,3.7,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,3.7,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> FRONT-1, !- Name
> Wall, !- Surface Type
> WALL-1, !- Construction Name
> SOUTH PERIMETER, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.50000, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.0,0.0,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,0.0,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,0.0,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,0.0,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C1-1, !- Name
> Ceiling, !- Surface Type
> CLNG-1, !- Construction Name
> SOUTH PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> C1-1P, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,0.0,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,0.0,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> F1-1, !- Name
> Floor, !- Surface Type
> FLOOR-SLAB-1, !- Construction Name
> SOUTH PERIMETER, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,3.7,0.0, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,0.0,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,0.0,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,3.7,0.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB12, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> SOUTH PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB21, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 30.5,0.0,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,0.0,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 26.8,3.7,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB14, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> SOUTH PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB41, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,3.7,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,0.0,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 0.0,0.0,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB15, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> SOUTH PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB51, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 26.8,3.7,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,3.7,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> RIGHT-1, !- Name
> Wall, !- Surface Type
> WALL-1, !- Construction Name
> EAST PERIMETER, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.50000, !- View Factor to Ground
> 4, !- Number of Vertices
> 30.5,0.0,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,0.0,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,15.2,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,15.2,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C2-1, !- Name
> Ceiling, !- Surface Type
> CLNG-1, !- Construction Name
> EAST PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> C2-1P, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,0.0,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,15.2,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> F2-1, !- Name
> Floor, !- Surface Type
> FLOOR-SLAB-1, !- Construction Name
> EAST PERIMETER, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,15.2,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,0.0,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,3.7,0.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB21, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> EAST PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB12, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 26.8,3.7,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,0.0,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,0.0,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB23, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> EAST PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB32, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 30.5,15.2,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,15.2,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB25, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> EAST PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB52, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 26.8,3.7,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> BACK-1, !- Name
> Wall, !- Surface Type
> WALL-1, !- Construction Name
> NORTH PERIMETER, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.50000, !- View Factor to Ground
> 4, !- Number of Vertices
> 30.5,15.2,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,15.2,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,15.2,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 0.0,15.2,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C3-1, !- Name
> Ceiling, !- Surface Type
> CLNG-1, !- Construction Name
> NORTH PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> C3-1P, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 30.5,15.2,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,15.2,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,11.6,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> F3-1, !- Name
> Floor, !- Surface Type
> FLOOR-SLAB-1, !- Construction Name
> NORTH PERIMETER, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,11.6,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,15.2,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,15.2,0.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB32, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> NORTH PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB23, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,15.2,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,15.2,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB34, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> NORTH PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB43, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.0,15.2,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,15.2,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,11.6,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB35, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> NORTH PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB53, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,11.6,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> LEFT-1, !- Name
> Wall, !- Surface Type
> WALL-1, !- Construction Name
> WEST PERIMETER, !- Zone Name
> Outdoors, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> SunExposed, !- Sun Exposure
> WindExposed, !- Wind Exposure
> 0.50000, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.0,15.2,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,15.2,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,0.0,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 0.0,0.0,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C4-1, !- Name
> Ceiling, !- Surface Type
> CLNG-1, !- Construction Name
> WEST PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> C4-1P, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,15.2,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,0.0,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> F4-1, !- Name
> Floor, !- Surface Type
> FLOOR-SLAB-1, !- Construction Name
> WEST PERIMETER, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,3.7,0.0, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,0.0,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,15.2,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,11.6,0.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB41, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> WEST PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB14, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 0.0,0.0,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,0.0,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,3.7,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB43, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> WEST PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB34, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,11.6,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,15.2,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 0.0,15.2,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB45, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> WEST PERIMETER, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB54, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,3.7,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,11.6,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> C5-1, !- Name
> Ceiling, !- Surface Type
> CLNG-1, !- Construction Name
> CORE, !- Zone Name
> Surface, !- Outside Boundary Condition
> C5-1P, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,3.7,2.4, !- X,Y,Z ==> Vertex 2 {m}
> 26.8,3.7,2.4, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> F5-1, !- Name
> Floor, !- Surface Type
> FLOOR-SLAB-1, !- Construction Name
> CORE, !- Zone Name
> Ground, !- Outside Boundary Condition
> , !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 1 {m}
> 26.8,3.7,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,3.7,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,11.6,0.0; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB51, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> CORE, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB15, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,3.7,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 26.8,3.7,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB52, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> CORE, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB25, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,3.7,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 26.8,3.7,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 26.8,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB53, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> CORE, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB35, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 26.8,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 26.8,11.6,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,11.6,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,11.6,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> BuildingSurface:Detailed,
> SB54, !- Name
> Wall, !- Surface Type
> INT-WALL-1, !- Construction Name
> CORE, !- Zone Name
> Surface, !- Outside Boundary Condition
> SB45, !- Outside Boundary Condition Object
> NoSun, !- Sun Exposure
> NoWind, !- Wind Exposure
> 0.0, !- View Factor to Ground
> 4, !- Number of Vertices
> 3.7,11.6,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 3.7,11.6,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 3.7,3.7,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 3.7,3.7,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> FenestrationSurface:Detailed,
> WF-1, !- Name
> Window, !- Surface Type
> Double LoE Clear Argon, !- Construction Name
> FRONT-1, !- Building Surface Name
> , !- Outside Boundary Condition Object
> 0.50000, !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> 1, !- Multiplier
> 4, !- Number of Vertices
> 3.0,0.0,2.1, !- X,Y,Z ==> Vertex 1 {m}
> 3.0,0.0,0.9, !- X,Y,Z ==> Vertex 2 {m}
> 16.8,0.0,0.9, !- X,Y,Z ==> Vertex 3 {m}
> 16.8,0.0,2.1; !- X,Y,Z ==> Vertex 4 {m}
>
> FenestrationSurface:Detailed,
> DF-1, !- Name
> Window, !- Surface Type
> Double LoE Clear Argon, !- Construction Name
> FRONT-1, !- Building Surface Name
> , !- Outside Boundary Condition Object
> 0.50000, !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> 1, !- Multiplier
> 4, !- Number of Vertices
> 21.3,0.0,2.4, !- X,Y,Z ==> Vertex 1 {m}
> 21.3,0.0,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 23.8,0.0,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 23.8,0.0,2.4; !- X,Y,Z ==> Vertex 4 {m}
>
> FenestrationSurface:Detailed,
> WR-1, !- Name
> Window, !- Surface Type
> Double LoE Clear Argon, !- Construction Name
> RIGHT-1, !- Building Surface Name
> , !- Outside Boundary Condition Object
> 0.50000, !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> 1, !- Multiplier
> 4, !- Number of Vertices
> 30.5,3.8,2.1, !- X,Y,Z ==> Vertex 1 {m}
> 30.5,3.8,0.9, !- X,Y,Z ==> Vertex 2 {m}
> 30.5,11.4,0.9, !- X,Y,Z ==> Vertex 3 {m}
> 30.5,11.4,2.1; !- X,Y,Z ==> Vertex 4 {m}
>
> FenestrationSurface:Detailed,
> WB-1, !- Name
> Window, !- Surface Type
> Double LoE Clear Argon, !- Construction Name
> BACK-1, !- Building Surface Name
> , !- Outside Boundary Condition Object
> 0.50000, !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> 1, !- Multiplier
> 4, !- Number of Vertices
> 27.4,15.2,2.1, !- X,Y,Z ==> Vertex 1 {m}
> 27.4,15.2,0.9, !- X,Y,Z ==> Vertex 2 {m}
> 13.7,15.2,0.9, !- X,Y,Z ==> Vertex 3 {m}
> 13.7,15.2,2.1; !- X,Y,Z ==> Vertex 4 {m}
>
> FenestrationSurface:Detailed,
> DB-1, !- Name
> Window, !- Surface Type
> Double LoE Clear Argon, !- Construction Name
> BACK-1, !- Building Surface Name
> , !- Outside Boundary Condition Object
> 0.50000, !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> 1, !- Multiplier
> 4, !- Number of Vertices
> 9.1,15.2,2.1, !- X,Y,Z ==> Vertex 1 {m}
> 9.1,15.2,0.0, !- X,Y,Z ==> Vertex 2 {m}
> 7.0,15.2,0.0, !- X,Y,Z ==> Vertex 3 {m}
> 7.0,15.2,2.1; !- X,Y,Z ==> Vertex 4 {m}
>
> FenestrationSurface:Detailed,
> WL-1, !- Name
> Window, !- Surface Type
> Double LoE Clear Argon, !- Construction Name
> LEFT-1, !- Building Surface Name
> , !- Outside Boundary Condition Object
> 0.50000, !- View Factor to Ground
> , !- Shading Control Name
> , !- Frame and Divider Name
> 1, !- Multiplier
> 4, !- Number of Vertices
> 0.0,11.4,2.1, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,11.4,0.9, !- X,Y,Z ==> Vertex 2 {m}
> 0.0,3.8,0.9, !- X,Y,Z ==> Vertex 3 {m}
> 0.0,3.8,2.1; !- X,Y,Z ==> Vertex 4 {m}
>
> Shading:Zone:Detailed,
> Main South Overhang, !- Name
> FRONT-1, !- Base Surface Name
> ShadeTransSch, !- Transmittance Schedule Name
> 4, !- Number of Vertices
> 0.0,-1.3,2.2, !- X,Y,Z ==> Vertex 1 {m}
> 0.0,0.0,2.2, !- X,Y,Z ==> Vertex 2 {m}
> 19.8,0.0,2.2, !- X,Y,Z ==> Vertex 3 {m}
> 19.8,-1.3,2.2; !- X,Y,Z ==> Vertex 4 {m}
>
> Shading:Zone:Detailed,
> South Door Overhang, !- Name
> FRONT-1, !- Base Surface Name
> ShadeTransSch, !- Transmittance Schedule Name
> 4, !- Number of Vertices
> 21.0,-2.0,2.6, !- X,Y,Z ==> Vertex 1 {m}
> 21.0,0.0,2.6, !- X,Y,Z ==> Vertex 2 {m}
> 24.1,0.0,2.6, !- X,Y,Z ==> Vertex 3 {m}
> 24.1,-2.0,2.6; !- X,Y,Z ==> Vertex 4 {m}
>
> ScheduleTypeLimits,
> Any Number; !- Name
>
> ScheduleTypeLimits,
> Fraction, !- Name
> 0.0, !- Lower Limit Value
> 1.0, !- Upper Limit Value
> Continuous; !- Numeric Type
>
> ScheduleTypeLimits,
> Temperature, !- Name
> -60, !- Lower Limit Value
> 200, !- Upper Limit Value
> Continuous; !- Numeric Type
>
> ScheduleTypeLimits,
> On/Off, !- Name
> 0, !- Lower Limit Value
> 1, !- Upper Limit Value
> Discrete; !- Numeric Type
>
> Schedule:Compact,
> Constant, !- Name
> on/off, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00,1.0; !- Field 3
>
> Schedule:Compact,
> Office HVAC, !- Name
> on/off, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 06:00,0.0, !- Field 3
> Until: 22:00,1.0, !- Field 5
> Until: 24:00,0.0, !- Field 7
> For: Saturday WinterDesignDay, !- Field 9
> Until: 06:00,0.0, !- Field 10
> Until: 18:00,1.0, !- Field 12
> Until: 24:00,0.0, !- Field 14
> For: Sunday Holidays AllOtherDays, !- Field 16
> Until: 24:00,0.0; !- Field 17
>
> Schedule:Compact,
> Office Heating Setpoints,!- Name
> Temperature, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays, !- Field 2
> Until: 06:00,12.8, !- Field 3
> Until: 22:00,21.1, !- Field 5
> Until: 24:00,12.8, !- Field 7
> For: Saturday, !- Field 9
> Until: 06:00,12.8, !- Field 10
> Until: 18:00,21.1, !- Field 12
> Until: 24:00,12.8, !- Field 14
> For: SummerDesignDay, !- Field 16
> Until: 24:00,12.8, !- Field 17
> For: WinterDesignDay, !- Field 19
> Until: 24:00,21.1, !- Field 20
> For: Sunday Holidays AllOtherDays, !- Field 22
> Until: 24:00,12.8; !- Field 23
>
> Schedule:Compact,
> Office Cooling Setpoints,!- Name
> Temperature, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays, !- Field 2
> Until: 06:00,40.0, !- Field 3
> Until: 22:00,23.9, !- Field 5
> Until: 24:00,40.0, !- Field 7
> For: Saturday, !- Field 9
> Until: 06:00,40.0, !- Field 10
> Until: 18:00,23.9, !- Field 12
> Until: 24:00,40.0, !- Field 14
> For: SummerDesignDay, !- Field 16
> Until: 24:00,23.9, !- Field 17
> For: WinterDesignDay, !- Field 19
> Until: 24:00,40.0, !- Field 20
> For: Sunday Holidays AllOtherDays, !- Field 22
> Until: 24:00,40.0; !- Field 23
>
> Schedule:Compact,
> Office Minimum OA, !- Name
> on/off, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 07:00,0.0, !- Field 3
> Until: 22:00,1.0, !- Field 5
> Until: 24:00,0.0, !- Field 7
> For: Saturday WinterDesignDay, !- Field 9
> Until: 07:00,0.0, !- Field 10
> Until: 18:00,1.0, !- Field 12
> Until: 24:00,0.0, !- Field 14
> For: Sunday Holidays AllOtherDays, !- Field 16
> Until: 24:00,0.0; !- Field 17
>
> Schedule:Compact,
> Office Lighting 2, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 05:00,0.05, !- Field 3
> Until: 07:00,0.1, !- Field 5
> Until: 08:00,0.3, !- Field 7
> Until: 17:00,0.9, !- Field 9
> Until: 18:00,0.5, !- Field 11
> Until: 20:00,0.3, !- Field 13
> Until: 22:00,0.2, !- Field 15
> Until: 23:00,0.1, !- Field 17
> Until: 24:00,0.05, !- Field 19
> For: Saturday, !- Field 21
> Until: 06:00,0.05, !- Field 22
> Until: 08:00,0.1, !- Field 24
> Until: 12:00,0.3, !- Field 26
> Until: 17:00,0.15, !- Field 28
> Until: 24:00,0.05, !- Field 30
> For: WinterDesignDay, !- Field 32
> Until: 24:00,0.0, !- Field 33
> For: Sunday Holidays AllOtherDays, !- Field 35
> Until: 24:00,0.05; !- Field 36
>
> Schedule:Compact,
> Office Occupancy 2, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: Weekdays SummerDesignDay, !- Field 2
> Until: 07:00,0.0, !- Field 3
> Until: 08:00,0.2, !- Field 5
> Until: 12:00,0.95, !- Field 7
> Until: 13:00,0.5, !- Field 9
> Until: 17:00,0.95, !- Field 11
> Until: 18:00,0.3, !- Field 13
> Until: 22:00,0.1, !- Field 15
> Until: 24:00,0.0, !- Field 17
> For: Saturday, !- Field 19
> Until: 07:00,0.0, !- Field 20
> Until: 08:00,0.1, !- Field 22
> Until: 12:00,0.3, !- Field 24
> Until: 17:00,0.1, !- Field 26
> Until: 18:00,0.05, !- Field 28
> Until: 24:00,0.0, !- Field 30
> For: Sunday Holidays WinterDesignDay AllOtherDays, !- Field 32
> Until: 24:00,0.0; !- Field 33
>
> Schedule:Compact,
> ActSchd, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00,117.239997864; !- Field 3
>
> !- Complex Field #4
>
> Schedule:Compact,
> ShadeTransSch, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00,0.0; !- Field 3
>
> Schedule:Compact,
> Seasonal Reset Supply Air Temp Sch, !- Name
> Temperature, !- Schedule Type Limits Name
> Through: 3/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00,16.0, !- Field 3
> Through: 9/30, !- Field 5
> For: AllDays, !- Field 6
> Until: 24:00,13.0, !- Field 7
> Through: 12/31, !- Field 9
> For: AllDays, !- Field 10
> Until: 24:00,16.0; !- Field 11
>
> People,
> SOUTH PERIMETER People 1,!- Name
> SOUTH PERIMETER, !- Zone or ZoneList Name
> Office Occupancy 2, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 11, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> , !- Sensible Heat Fraction
> ActSchd; !- Activity Level Schedule Name
>
> People,
> EAST PERIMETER People 1, !- Name
> EAST PERIMETER, !- Zone or ZoneList Name
> Office Occupancy 2, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 5, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> , !- Sensible Heat Fraction
> ActSchd; !- Activity Level Schedule Name
>
> People,
> NORTH PERIMETER People 1,!- Name
> NORTH PERIMETER, !- Zone or ZoneList Name
> Office Occupancy 2, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 11, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> , !- Sensible Heat Fraction
> ActSchd; !- Activity Level Schedule Name
>
> People,
> WEST PERIMETER People 1, !- Name
> WEST PERIMETER, !- Zone or ZoneList Name
> Office Occupancy 2, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 5, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> , !- Sensible Heat Fraction
> ActSchd; !- Activity Level Schedule Name
>
> People,
> CORE People 1, !- Name
> CORE, !- Zone or ZoneList Name
> Office Occupancy 2, !- Number of People Schedule Name
> People, !- Number of People Calculation Method
> 20, !- Number of People
> , !- People per Zone Floor Area {person/m2}
> , !- Zone Floor Area per Person {m2/person}
> 0.3, !- Fraction Radiant
> , !- Sensible Heat Fraction
> ActSchd; !- Activity Level Schedule Name
>
> Lights,
> SOUTH PERIMETER Lights 1,!- Name
> SOUTH PERIMETER, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> LightingLevel, !- Design Level Calculation Method
> 1584, !- Lighting Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0.2, !- Return Air Fraction
> 0.59, !- Fraction Radiant
> 0.2, !- Fraction Visible
> 0, !- Fraction Replaceable
> GeneralLights; !- End-Use Subcategory
>
> Lights,
> EAST PERIMETER Lights 1, !- Name
> EAST PERIMETER, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> LightingLevel, !- Design Level Calculation Method
> 684, !- Lighting Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0.2, !- Return Air Fraction
> 0.59, !- Fraction Radiant
> 0.2, !- Fraction Visible
> 0, !- Fraction Replaceable
> GeneralLights; !- End-Use Subcategory
>
> Lights,
> NORTH PERIMETER Lights 1,!- Name
> NORTH PERIMETER, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> LightingLevel, !- Design Level Calculation Method
> 1584, !- Lighting Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0.2, !- Return Air Fraction
> 0.59, !- Fraction Radiant
> 0.2, !- Fraction Visible
> 0, !- Fraction Replaceable
> GeneralLights; !- End-Use Subcategory
>
> Lights,
> WEST PERIMETER Lights 1, !- Name
> WEST PERIMETER, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> LightingLevel, !- Design Level Calculation Method
> 684, !- Lighting Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0.2, !- Return Air Fraction
> 0.59, !- Fraction Radiant
> 0.2, !- Fraction Visible
> 0, !- Fraction Replaceable
> GeneralLights; !- End-Use Subcategory
>
> Lights,
> CORE Lights 1, !- Name
> CORE, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> LightingLevel, !- Design Level Calculation Method
> 2964, !- Lighting Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0.2, !- Return Air Fraction
> 0.59, !- Fraction Radiant
> 0.2, !- Fraction Visible
> 0, !- Fraction Replaceable
> GeneralLights; !- End-Use Subcategory
>
> ElectricEquipment,
> SOUTH PERIMETER ElecEq 1,!- Name
> SOUTH PERIMETER, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 1056, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0, !- Fraction Latent
> 0.3, !- Fraction Radiant
> 0, !- Fraction Lost
> General; !- End-Use Subcategory
>
> ElectricEquipment,
> EAST PERIMETER ElecEq 1, !- Name
> EAST PERIMETER, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 456, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0, !- Fraction Latent
> 0.3, !- Fraction Radiant
> 0, !- Fraction Lost
> General; !- End-Use Subcategory
>
> ElectricEquipment,
> NORTH PERIMETER ElecEq 1,!- Name
> NORTH PERIMETER, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 1056, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0, !- Fraction Latent
> 0.3, !- Fraction Radiant
> 0, !- Fraction Lost
> General; !- End-Use Subcategory
>
> ElectricEquipment,
> WEST PERIMETER ElecEq 1, !- Name
> WEST PERIMETER, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 456, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0, !- Fraction Latent
> 0.3, !- Fraction Radiant
> 0, !- Fraction Lost
> General; !- End-Use Subcategory
>
> ElectricEquipment,
> CORE ElecEq 1, !- Name
> CORE, !- Zone or ZoneList Name
> Office Lighting 2, !- Schedule Name
> EquipmentLevel, !- Design Level Calculation Method
> 1976, !- Design Level {W}
> , !- Watts per Zone Floor Area {W/m2}
> , !- Watts per Person {W/person}
> 0, !- Fraction Latent
> 0.3, !- Fraction Radiant
> 0, !- Fraction Lost
> General; !- End-Use Subcategory
>
> ZoneInfiltration:DesignFlowRate,
> SOUTH PERIMETER Infil 1, !- Name
> SOUTH PERIMETER, !- Zone or ZoneList Name
> Constant, !- Schedule Name
> Flow/Zone, !- Design Flow Rate Calculation Method
> 0.035, !- Design Flow Rate {m3/s}
> , !- Flow per Zone Floor Area {m3/s-m2}
> , !- Flow per Exterior Surface Area {m3/s-m2}
> , !- Air Changes per Hour
> 0, !- Constant Term Coefficient
> 0, !- Temperature Term Coefficient
> 0.2237, !- Velocity Term Coefficient
> 0; !- Velocity Squared Term Coefficient
>
> ZoneInfiltration:DesignFlowRate,
> EAST PERIMETER Infil 1, !- Name
> EAST PERIMETER, !- Zone or ZoneList Name
> Constant, !- Schedule Name
> Flow/Zone, !- Design Flow Rate Calculation Method
> 0.015, !- Design Flow Rate {m3/s}
> , !- Flow per Zone Floor Area {m3/s-m2}
> , !- Flow per Exterior Surface Area {m3/s-m2}
> , !- Air Changes per Hour
> 0, !- Constant Term Coefficient
> 0, !- Temperature Term Coefficient
> 0.2237, !- Velocity Term Coefficient
> 0; !- Velocity Squared Term Coefficient
>
> ZoneInfiltration:DesignFlowRate,
> NORTH PERIMETER Infil 1, !- Name
> NORTH PERIMETER, !- Zone or ZoneList Name
> Constant, !- Schedule Name
> Flow/Zone, !- Design Flow Rate Calculation Method
> 0.035, !- Design Flow Rate {m3/s}
> , !- Flow per Zone Floor Area {m3/s-m2}
> , !- Flow per Exterior Surface Area {m3/s-m2}
> , !- Air Changes per Hour
> 0, !- Constant Term Coefficient
> 0, !- Temperature Term Coefficient
> 0.2237, !- Velocity Term Coefficient
> 0; !- Velocity Squared Term Coefficient
>
> ZoneInfiltration:DesignFlowRate,
> WEST PERIMETER Infil 1, !- Name
> WEST PERIMETER, !- Zone or ZoneList Name
> Constant, !- Schedule Name
> Flow/Zone, !- Design Flow Rate Calculation Method
> 0.015, !- Design Flow Rate {m3/s}
> , !- Flow per Zone Floor Area {m3/s-m2}
> , !- Flow per Exterior Surface Area {m3/s-m2}
> , !- Air Changes per Hour
> 0, !- Constant Term Coefficient
> 0, !- Temperature Term Coefficient
> 0.2237, !- Velocity Term Coefficient
> 0; !- Velocity Squared Term Coefficient
>
> ZoneInfiltration:DesignFlowRate,
> CORE Infil 1, !- Name
> CORE, !- Zone or ZoneList Name
> Constant, !- Schedule Name
> Flow/Zone, !- Design Flow Rate Calculation Method
> 0.062, !- Design Flow Rate {m3/s}
> , !- Flow per Zone Floor Area {m3/s-m2}
> , !- Flow per Exterior Surface Area {m3/s-m2}
> , !- Air Changes per Hour
> 0, !- Constant Term Coefficient
> 0, !- Temperature Term Coefficient
> 0.2237, !- Velocity Term Coefficient
> 0; !- Velocity Squared Term Coefficient
>
> Output:Variable,*,Outdoor Dry Bulb,Monthly;
>
> Output:Variable,*,Zone/Sys Air Temperature,Monthly;
>
> Output:Variable,*,Zone/Sys Sensible Cooling Rate,Monthly;
>
> Output:Variable,*,Zone/Sys Sensible Heating Rate,Monthly;
>
> Output:Variable,*,Zone People Number Of Occupants,Monthly;
>
> Output:Variable,*,Zone Lights Total Heat Gain,Monthly;
>
> Output:Variable,*,Zone Electric Equipment Total Heat Gain,Monthly;
>
> Output:Variable,*,Zone Infiltration Air Change Rate,Monthly;
>
> Output:Variable,*,Zone Infiltration Sensible Heat Loss,Monthly;
>
> Output:Variable,*,Zone Infiltration Sensible Heat Gain,Monthly;
>
> Output:Meter:MeterFileOnly,Electricity:Facility,Monthly;
>
> Output:Meter:MeterFileOnly,Electricity:Building,Monthly;
>
> Output:Meter:MeterFileOnly,Electricity:HVAC,Monthly;
>
> Output:Meter:MeterFileOnly,Electricity:Plant,Monthly;
>
> Output:Meter:MeterFileOnly,Electricity:Facility,RunPeriod;
>
> Output:Meter:MeterFileOnly,Electricity:Building,RunPeriod;
>
> Output:Meter:MeterFileOnly,Electricity:HVAC,RunPeriod;
>
> Output:Meter:MeterFileOnly,Electricity:Plant,RunPeriod;
>
> Output:Meter:MeterFileOnly,Gas:Facility,Monthly;
>
> Output:Meter:MeterFileOnly,Gas:HVAC,Monthly;
>
> Output:Meter:MeterFileOnly,Gas:Plant,Monthly;
>
> Output:Meter:MeterFileOnly,Gas:Facility,RunPeriod;
>
> Output:Meter:MeterFileOnly,Gas:HVAC,RunPeriod;
>
> Output:Meter:MeterFileOnly,Gas:Plant,RunPeriod;
>
> Output:VariableDictionary,Regular;
>
> Output:Surfaces:Drawing,dxf;
>
> OutputControl:Table:Style,
> HTML; !- Column Separator
>
> Output:Table:SummaryReports,
> ABUPS, !- Report 1 Name
> EquipmentSummary; !- Report 2 Name
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/