|
Hi, Alvero Because you are using templates, some sizing parameters are set by the program. When the outdoor temperature and the Zone controlled temperature are very close (21°C), the cooling system is over sized. Therefore, you get the warning that the DX coil is less then 2°C, which is close to compressor freezing condition. You can raise the zone thermostat temperature or the coil temperature limit in the Sizing:zone object to a higher value to avoid this warning. When you are not using template or autosizing, these limit values can be set by you in the IDF. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: alvarofialho@xxxxxxxxx Date: Thu, 5 May 2011 14:20:42 +0200 Subject: [EnergyPlus_Support] Warning meassage in Exercise 2C of "Getting Started..."
Hello all,
I was playing a bit with the sample Exercises provided in the "Getting started with EnergyPlus" document. And Exercise 2C (the most "complete" one) outputs a warning message (and some consequent error messages) that I don't know what to do. As a "learning exercise", could you please help me into solving this? It is important to let you know that I'm a computer scientist, with no experience at all (for the moment) with the design of HVAC systems :-) Thanks! Here goes the warning message: ** Warning ** Coil:Cooling:DX:SingleSpeed "NORTH ZONE UNITARY COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = 1.29 C. ** ~~~ ** ...Occurrence info = Chicago Ohare Intl Ap IL USA TMY3 WMO#=725300, 04/25 14:00 - 14:15 ** ~~~ ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil ** ~~~ ** 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 21.146 C. ** ~~~ ** 2) may have a low air flow rate per watt of cooling capacity. Check inputs. ** ~~~ ** 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs. And the consequent error message: ************* ===== Recurring Error Summary ===== ************* The following recurring error messages occurred. ************* ************* ** Warning ** Coil:Cooling:DX:SingleSpeed "NORTH ZONE UNITARY COOLING COIL" - Full load outlet temperature indicates a possibility of frost/freeze error continues. Outlet air temperature statistics follow: ************* ** ~~~ ** This error occurred 46 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=1.986818 Min=0.362192 Thanks lot! Álvaro. ps: I'm sending the IDF attached, although you might all have it in the Examples/BasicsFiles folder of your E+ installation. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |