RE: [EnergyPlus_Support] Warning meassage in Exercise 2C of "Getting Started..."





Hi, Alvero

Because you are using templates, some sizing parameters are set by the program.

When the outdoor temperature and the Zone controlled  temperature are very close  (21°C), the cooling system is over sized.  Therefore, you get the warning that the DX coil is less then 2°C, which is close to  compressor freezing condition.

You can raise the zone thermostat temperature or the coil temperature limit in the Sizing:zone object to a higher value to avoid this warning.

When you are not using template or autosizing, these limit values can be set by you in the IDF.

 Dr. Li  

To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: alvarofialho@xxxxxxxxx
Date: Thu, 5 May 2011 14:20:42 +0200
Subject: [EnergyPlus_Support] Warning meassage in Exercise 2C of "Getting Started..."

 
Hello all,

I was playing a bit with the sample Exercises provided in the "Getting
started with EnergyPlus" document. And Exercise 2C (the most "complete"
one) outputs a warning message (and some consequent error messages) that
I don't know what to do. As a "learning exercise", could you please help
me into solving this? It is important to let you know that I'm a
computer scientist, with no experience at all (for the moment) with the
design of HVAC systems :-) Thanks!

Here goes the warning message:

** Warning ** Coil:Cooling:DX:SingleSpeed "NORTH ZONE UNITARY
COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This
indicates the possibility of coil frost/freeze. Outlet temperature = 1.29 C.
** ~~~ ** ...Occurrence info = Chicago Ohare Intl Ap IL USA
TMY3 WMO#=725300, 04/25 14:00 - 14:15
** ~~~ ** ... Possible reasons for low outlet air dry-bulb
temperatures are: This DX coil
** ~~~ ** 1) may have a low inlet air dry-bulb temperature.
Inlet air temperature = 21.146 C.
** ~~~ ** 2) may have a low air flow rate per watt of cooling
capacity. Check inputs.
** ~~~ ** 3) is used as part of a HX assisted cooling coil
which uses a high sensible effectiveness. Check inputs.

And the consequent error message:

************* ===== Recurring Error Summary =====
************* The following recurring error messages occurred.
*************
************* ** Warning ** Coil:Cooling:DX:SingleSpeed "NORTH ZONE
UNITARY COOLING COIL" - Full load outlet temperature indicates a
possibility of frost/freeze error continues. Outlet air temperature
statistics follow:
************* ** ~~~ ** This error occurred 46 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=1.986818 Min=0.362192

Thanks lot!
Álvaro.

ps: I'm sending the IDF attached, although you might all have it in the
Examples/BasicsFiles folder of your E+ installation.



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___