RE: [EnergyPlus_Support] Gas Consumption at Zero for March thru November
- To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
- Subject: RE: [EnergyPlus_Support] Gas Consumption at Zero for March thru November
- From: "James V Dirkes II, PE" <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>
- Date: Tue, 10 May 2011 11:00:36 -0400
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 10 May 2011 09:00:42 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1305039641; bh=pIkcjWwKqH98oF5TMLG2iTjyUYmXBaR7Lo3RBcJFQjw=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:X-EN-OrigOutIP:X-EN-IMPSID:X-Received:To:References:In-Reply-To:Message-ID:X-Mailer:Thread-Index:Content-Language:X-EN-UserInfo:X-EN-AuthUser:X-EN-OrigIP:X-EN-OrigHost:X-Originating-IP:X-eGroups-Msg-Info:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type; b=E6PY8On3FQ9iLx8+c0RQLXcrZWqSP8G/u0NEPiUDFxYt7VKNB5dxjgaR//bImopTEhV/KbaFr/16Vu4SDcqXrbH2kqhI4R1Xc+7LUIWhAcQuEHOtM+lbErNcJcOYbQdn
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=T3q+IRMmDs+GTLM+hLXj3ZgFm/F/FQRVnWSHO+Lox2wlOmRP14jJV1nUrVS+Jhw356cRjlHczsXKA/iCwyVWGo0jpzldDXbP35nPjlKVnm4RbP8UZCBtt3qCKEtDd0PO;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <BANLkTinUxnc7ejLA=s0Uk_YwirPs19wA4g@mail.gmail.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- References: <BANLkTinUxnc7ejLA=s0Uk_YwirPs19wA4g@mail.gmail.com>
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Thread-index: AcwPGwpn3kEKahYWQHGUNF2qPZF05AABipCg
Patrick,
DC does not have a severe winter and internal loads (lights, plug loads, etc.) may provide enough heat to maintain the space heating setpoint during occupied hours. However:
· A typical air handler heating coil will consume some heating energy to maintain the desired leaving temp setpoint. This depends heavily on your control scheme and amount of outdoor air.
· There will normally be heating energy needed during unoccupied hours, since all the lights and plug loads are turned off
Try reporting more variables to identify why no heating energy is used during a cold day at night (unoccupied period) when intuition suggests that it should use heating energy. Make Sherlock Holmes proud of you!
p.s., I normally report all of the node temps for each component of an air handler to see what?s going on at each timestep. That reveals whether your controls are doing what you intend. Another helpful variable is ?Output:Variable, ZoneName, Zone/Sys Sensible Load Predicted, Timestep;? This gives a general idea of the zone?s heating / cooling needs.
Once you identify some aspect of operation that is NOT what it should be, you can add more report variables to ?drill down? further.
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=20169/stime=1305039641>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmOHA4YWRnBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMDUwMzk2NDE->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkMDk1YzdwBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzA1MDM5NjQx>Visit Your Group | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___