Hi, Alvero
Because you are using templates, some sizing parameters are set by the program.
When the outdoor temperature and the Zone controlled temperature are very close (21°C), the cooling system is over sized. Therefore, you get the warning that the DX coil is less then 2°C, which is close to compressor freezing condition.
You can raise the zone thermostat temperature or the coil temperature limit in the Sizing:zone object to a higher value to avoid this warning.
When you are not using template or autosizing, these limit values can be set by you in the IDF.
Dr. Li
To:
EnergyPlus_Support@xxxxxxxxxxxxxxxFrom:
alvarofialho@xxxxxxxxx
Date: Thu, 5 May 2011 14:20:42 +0200
Subject: [EnergyPlus_Support] Warning meassage in Exercise 2C of "Getting Started..."
Hello all,
I was playing a bit with the sample Exercises provided in the "Getting
started with EnergyPlus" document. And Exercise 2C (the most "complete"
one) outputs a warning message (and some consequent error messages) that
I don't know what to do. As a "learning exercise", could you please help
me into solving this? It is important to let you know that I'm a
computer scientist, with no experience at all (for the moment) with the
design of HVAC systems :-) Thanks!
Here goes the warning message:
** Warning ** Coil:Cooling:DX:SingleSpeed "NORTH ZONE UNITARY
COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This
indicates the possibility of coil frost/freeze. Outlet temperature = 1.29 C.
** ~~~ ** ...Occurrence info = Chicago Ohare Intl Ap IL USA
TMY3 WMO#=725300, 04/25 14:00 - 14:15
** ~~~ ** ... Possible reasons for low outlet air dry-bulb
temperatures are: This DX coil
** ~~~ ** 1) may have a low inlet air dry-bulb temperature.
Inlet air temperature = 21.146 C.
** ~~~ ** 2) may have a low air flow rate per watt of cooling
capacity. Check inputs.
** ~~~ ** 3) is used as part of a HX assisted cooling coil
which uses a high sensible effectiveness. Check inputs.
And the consequent error message:
************* ===== Recurring Error Summary =====
************* The following recurring error messages occurred.
*************
************* ** Warning ** Coil:Cooling:DX:SingleSpeed "NORTH ZONE
UNITARY COOLING COIL" - Full load outlet temperature indicates a
possibility of frost/freeze error continues. Outlet air temperature
statistics follow:
************* ** ~~~ ** This error occurred 46 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=1.986818 Min=0.362192