Re: [EnergyPlus_Support] fatal error





yes you are right.
Thanks
It worked now.
I always felt warnings are just warnings....
but they are not

On Tue, May 10, 2011 at 12:07 PM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
 

   ** Warning ** ZoneHVAC:PackagedTerminalHeatPump - air flow rate = 0.5999120 in fan object ZONE1PTHPFAN is less than the maximum PTHP supply air flow rate.
   **   ~~~   **  The fan flow rate must be greater than the PTHP maximum supply air flow rate.
   **   ~~~   **  Occurs in ZoneHVAC:PackagedTerminalHeatPump = ZONE1PTHP

most likely identified as a warning but is a severe.  causing termination.



At 01:01 PM 5/10/2011, deepika khowal wrote:


Attached is the input file.
Pls let me know what is it that I am missing.
Thanks

On Tue, May 10, 2011 at 11:42 AM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
 

1) have you downloaded the V6.0.0.037 interim update and run this.

2) it is impossible to dx without an input file.  Pls send input file to the helpdesk.


At 12:37 PM 5/10/2011, deepika khowal wrote:
can anyone tell me what this error is...
I checked my .idf so many times and I cant find this.
Thanks
Regards
Deepika

Fatal  ** GetPTUnit: Errors found in getting input.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=0
   ..... Last severe error=
   ************* Fatal error -- final processing.  More error messages may appear.
   ************* Testing Individual Branch Integrity
   ************* All Branches passed integrity testing
   ************* Testing Individual Supply Air Path Integrity
   ************* All Supply Air Paths passed integrity testing
   ************* Testing Individual Return Air Path Integrity





Content-Type: application/octet-stream; name="Version6.1_PTHP.idf"
Content-Disposition: attachment; filename="Version6.1_PTHP.idf"
X-Attachment-Id: f_gnj7g9by0




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___