|
Thanks Richard for the correction. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: RRaustad@xxxxxxxxxxxx Date: Wed, 11 May 2011 12:35:40 -0400 Subject: Re: [EnergyPlus_Support] Duplicate name error message
Actually it's 'edit', 'find', "Sizing:Zone". The name of the sizing
object is after the comma or on the second line.
Sizing:Zone, Zone One, !- Zone Name On 5/11/2011 12:31 PM, YuanLu Li wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |