[EnergyPlus_Support] Re: Connecting two Airloops to the same zone
Thanks for your answer. In fact, I manage to do what I wanted with a branch splitter located after the Air Loop Inlet Node. In fact, I hadn't seen that I could set a nodelist instead of a single node for the Demand Side Inlet Node and the Supply Side Outlet Node. sorry for the useless question.
Regards.
Robin GENOUD
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Only 1 Airloop per zone (but can serve multiple zones) since there is
> only 1 return node. Use the Airloop for the mechanical ventilation and
> then use ZoneHVAC equipment to condition each zone. Or use the
> AirloopHVAC for conditioning the zones and then use
> ZoneHVAC:OutdoorAirUnit or ZoneHVAC:EnergyRecoveryVentilator for the
> ventilation.
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/