Hi Giulio. In my opinion, will be hard to model such a frame. Windows in Eplus are limited to 3 or 4 vertices. Modelling one hexagonal surface considering it's a window is impossible. You can try to model each hexagonal as two windows, but that way you would end up having an extra frame right across the hexagonal area, and two window objects for each hexagonal window (and if your total window will have that many hexagonal surfaces as there is in your link, you're in for a lot of windows). If for your study you really need those frames in that geometry, honestly don't see any other way to do it. Pedro On 18-05-2011 12:49, artitecture82 wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.