You need to know at least 2 things. 1. The moisture generation rate of the misting process (G) and 2. The effectiveness of the evacuation (E). Assuming the fan does actually exhaust everything it intakes, you have a G*E moisture generating device which can be modeled with a latent only steam generator. Much more complicated is the heat production. The fan generates heat, the pump generates heat, the work process generates heat, and the machines don’t run 24/7. Also don’t forget that the exhaust must have some makeup from somewhere. Ned Lyon, P.E. (MA) SIMPSON GUMPERTZ & HEGER From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of smurfy33.skku I am working on modeling "mist collector" in EnergyPlus and now run into a problem that needs your help. Note that I am a beginner of EnergyPlus and lack of knowedge in EnergyPlus. Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.