[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: PTHP Baseline outperforming VAV
Hi Markus,
For a large performance differace, look to the facade. Example: Proposed building has three pane glass, but the total window to wall ratio is 80%. baseline has single pane, but 40%. Baseline outperforms proposed because you simply can't compare 100 mm thick glass and 300 mm brick interms of conduction and Solar gain into the space.
PS example is not accurate and a little over played, but you get my meaning. Otherwise, I find it unlikely that the window units outperform a central unit, unless their are scheduling differences, or you zone dampers are not working.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Marcus" <clasz14@...> wrote:
>
> Hi all, please excuse cross-posting to Bldg-sim;
>
> Having some difficulty in an App. G model for a 6-floor 14,000 m2 GFA Hotel in zone 1B (Abu Dhabi). Assuming standard design for each, should a proposed VAV system out-perform window AC units (the baseline)?
>
> Proposed:
> VAV with 2 Air-cooled centrifugal chillers, chiller COP = 3.1 (2.8 if condenser fan energy included)
> Envelope - Better windows decrease heating demand by 8% rest of envelope is minimum required for compliance
>
> Baseline:
> System Packaged terminal heat pump, COP = 3.52
>
> Using Energyplus v6.0 the results are;
>
> Site Energy in End Uses BL Proposed COP5
> MWh MWh MWh
> Space Cooling 747.5 1052.0 715.6
> Heat Rejection 0.0 0.0 0.0
> Space Heating 1.3 0.1 0.1
> Pumps 0.0 60.0 60.0
> Fans - Interior 42.2 137.7 137.7
> Fans - Car park 0.0 0.0 0.0
> Interior Lighting 530.5 530.5 530.5
> Exterior Lighting 0.0 0.0 0.0
> Service Water Heating 0.0 0.0 0.0
> Receptacle/Process Equipment 146.3 146.3 146.3
> Data Centre Equipment 0.0 0.0 0.0
> Elevators and Escalators 0.0 0.0 0.0
> Total Site Energy 1467.9 1926.6 1590.2
>
> I have the energy for the baseline, the proposed with COP = 3.1, and then trying COP = 5. It seems that even if we drastically increase the COP of the chiller plant in the proposed VAV system, we still can't get any energy savings. Is this realistic, an artifact of the simulation, or just an error on my part?
>
> Any guidance would be appreciated,
>
> Marcus
> --
> Marcus Jones, LEED AP, M.Sc.
> Freelance energy consultant
> Vienna, Austria
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/