These warnings just mean that the performance curves for the DX cooling coil do not have a wide enough range to allow calculation of the standard ratings. Look at the Minimum/Maximum temperatures for X (indoor wet-bulb temperature) and Y (outdoor dry-bulb temperature) in the curve objects. Refer to the Engineering Reference document for further information. You could edit the batch file to add PAUSE statements to see which batch file lines are causing these DOS messages "The system cannot find the files specified." I believe the batch file is named RunEPlus.bat. When the batch file pauses you could look at the DOS screen to see if a message has been written yet. On 5/25/2011 10:40 AM, ooikoonbeng2004 wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |