I am guessing here but I suspect that you are using HVACTemplate
objects? If so, look for the expidf file after a simulation and then
look for the Coil:Cooling:DX object. If no HVACTemplate objects are
used then the dx cooling coil will be in your input file.
Here is an example:
Coil:Cooling:DX:SingleSpeed,
Furnace ACDXCoil 1, !- Name
FanAndCoilAvailSched, !- Availability Schedule Name
25000, !- Rated Total Cooling Capacity {W}
0.75, !- Rated Sensible Heat Ratio
3.0, !- Rated COP
1.3, !- Rated Air Flow Rate {m3/s}
, !- Rated Evaporator Fan Power Per
Volume Flow Rate {W/(m3/s)}
DX Cooling Coil Air Inlet Node, !- Air Inlet Node Name
Heating Coil Air Inlet Node, !- Air Outlet Node Name
WindACCoolCapFT, !- Total Cooling Capacity Function of
Temperature Curve Name
WindACCoolCapFFF, !- Total Cooling Capacity Function of
Flow Fraction Curve Name
WindACEIRFT, !- Energy Input Ratio Function of
Temperature Curve Name
WindACEIRFFF, !- Energy Input Ratio Function of Flow
Fraction Curve Name
WindACPLFFPLR; !- Part Load Fraction Correlation Curve
Name
The performance curves are the last 5 input fields shown above.
These curves tell the program how the coil performs at various
conditions. These performance curves can either be curve objects
(Curve:*) or you could use the table objects (Table:*). You are
probably using the curve objects.
Curve:Biquadratic,
WindACCoolCapFT, !- Name
0.942587793, !- Coefficient1 Constant
0.009543347, !- Coefficient2 x
0.000683770, !- Coefficient3 x**2
-0.011042676, !- Coefficient4 y
0.000005249, !- Coefficient5 y**2
-0.000009720, !- Coefficient6 x*y
12.77778, !- Minimum Value of x
23.88889, !- Maximum Value of x
18.0, !- Minimum Value of y
46.11111, !- Maximum Value of y
, !- Minimum Curve Output
, !- Maximum Curve Output
Temperature, !- Input Unit Type for X
Temperature, !- Input Unit Type for Y
Dimensionless; !- Output Unit Type
Curve:Biquadratic,
WindACEIRFT, !- Name
0.342414409, !- Coefficient1 Constant
0.034885008, !- Coefficient2 x
-0.000623700, !- Coefficient3 x**2
0.004977216, !- Coefficient4 y
0.000437951, !- Coefficient5 y**2
-0.000728028, !- Coefficient6 x*y
12.77778, !- Minimum Value of x
23.88889, !- Maximum Value of x
18.0, !- Minimum Value of y
46.11111, !- Maximum Value of y
, !- Minimum Curve Output
, !- Maximum Curve Output
Temperature, !- Input Unit Type for X
Temperature, !- Input Unit Type for Y
Dimensionless; !- Output Unit Type
See the Minimum/Maximum Value of x and y in this performance curve?
Lower or raise the values in your file for CAP-FT and EIR-FT and the
warning should go away. In these specific curves, x = inlet air
wet-bulb temperature and y = outdoor air temperature. These curves
came from the example file FurnaceWithDXSystem.idf. I assume the
warnings do not show up in that file and you can use the values
shown in this example (e.g., 12.77778, 23.88889, 18.0, and 46.11111)
On 5/27/2011 9:30 PM, ooikoonbeng2004 wrote:
i am not sure if the subject shouold be changed to
Coil:Cooling:DX.
Thank you Richard, i would like to learn how to make
adjustments, which may just be academic, to the
Coil:Cooling:DX performance so that, ultimately this
warning does not appear.
A search in the Engineering Reference gives a single
instance of 'indoor wet-bulb' as follows
As with other table or curve objects, the lookup table can
be used anywhere a valid curve object name is allowed.
Care must be taken to ensure the table data format is
consistent with the associate model that is using the
performance curve (e.g. DX cooling coil capacity as a
function of temperature where independent variable X1 =
indoor wet-bulb temperature and independent variable X2 =
outdoor dry-bulb temperature).
i do not know where the Performance Curves or Lookup
Tables are.
All the best,
ooi
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad <RRaustad@...> wrote:
>
> These warnings just mean that the performance curves
for the DX cooling
> coil do not have a wide enough range to allow
calculation of the
> standard ratings. Look at the Minimum/Maximum
temperatures for X (indoor
> wet-bulb temperature) and Y (outdoor dry-bulb
temperature) in the curve
> objects. Refer to the Engineering Reference document
for further
> information.
>
> You could edit the batch file to add PAUSE statements
to see which batch
> file lines are causing these DOS messages "The system
cannot find the
> files specified."
> I believe the batch file is named RunEPlus.bat. When
the batch file
> pauses you could look at the DOS screen to see if a
message has been
> written yet.
>
> On 5/25/2011 10:40 AM, ooikoonbeng2004 wrote:
> >
> > There is 1 Warning when the file
ExerciseOutput1.idf is run. The
> > warning is Warning ** One of the Standard
Ratings for
> > Coil:Cooling:DX:SingleSpeed = AHU 1 COOLING COIL
could not be
> > calculated, so set to zero in output.
> > ** ~~~ ** Review the Standard Ratings
calculations in the Engineering
> > Reference for this coil type. Also, use
Output:Diagnostics,
> > DisplayExtraWarnings for further guidance.
> > ** ~~~ ** CheckCurveLimitsForStandardRatings:
The max and/or min
> > limits specified in the corresponding curve
objects did not
> > ** ~~~ ** allow the curves to be evaluated at
the conditions required
> > to calculate one or more of the Standard Rating
values.
> > ** ~~~ ** Coil:Cooling:DX:SingleSpeed=AHU 1
COOLING COIL: Integrated
> > Energy Efficiency Ratio (IEER) can not be
calculated.
> > ** ~~~ ** Check limits in Total Cooling Capacity
Function of
> > Temperature Curve , Curve Type = BIQUADRATIC,
Curve Name = AHU 1 DX
> > COIL CAP-FT
> > ** ~~~ ** Check limits in EIR Function of
Temperature Curve, Curve
> > Type = BIQUADRATIC, Curve Name = AHU 1 DX COIL
EIR-FT
> >
> > i am not sure if the above waring has got
something to do with the
> > errors shown in the DOS window
> >
> > May we all be well and happy
> > ooi
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>,
"ooikoonbeng2004"
> > <ooi_kb3@> wrote:
> > >
> > > i followed your instructions in your "Tips
& Tricks". When the .bat
> > file is used at the command (DOS) window, the
following is shown
> > >
> > > 1 file(s) copied.
> > > 1 file(s) copied.
> > >
> > > ===== Extracting Results
> > >
> > > The system cannot find the files specified.
> > > The system cannot find the files specified.
> > > The system cannot find the files specified.
> > > The system cannot find the files specified.
> > > The system cannot find the files specified.
> > >
> > > The above was done in
> >
C:\EnergyPlusv6-0-0-037\ExampleFiles\AdvancedOutput where
the idf, rvi
> > and bat files are located.
> > >
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>, Linda
Lawrie <linda@>
> > wrote:
> > > >
> > > > use rvi and mvi files.
> > > >
> > > > Described several places in
documentation including a "tips & tricks".
> > > >
> > > > At 06:09 AM 5/21/2011, Vaibhav Jain
wrote:
> > > >
> > > > >How columns of output CSV files
can be arranged in user desired
> > > > >order. It is easy to do so.
> > > >
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40
Years
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|