Jean, I can’t recall what has been said in the past….. Keep in mind: · The Pressure Rise field in all E+ fan objects is the product of fan and motor efficiency (EFFfan x EFF motor) · You can derive the pressure rise needed for a Baseline calculation; no iteration needed. See if you can follow the attached spreadsheet for the derivation (Sorry; US units!) The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jean marais I know this topic has been disscussed to death, but I'm still a bit in the dark. I used energy plus results for constant fan volume maximum flow rates (assuming a pressure rise of 2000 Pa, 0.8 motor eff. and 0.7 fan eff.) as the input for my ASHRAE fan power calculation (G3.1.2.9) which spits out a rated input power after a fan efficiency and motor efficiency (0.7 and 0.8) have been applied. I then back calculate the ASHRAE fan pressure rise using the formula (trying from memory...correct me if I'm wrong Mr Dirks) dP=motor_Eff x fan_Eff x Wf(W)/Q to derive the |