I think this is an incorrect error message and should say
that you are missing the schedule.
Make sure you have included a schedule in the
Setpoint Schedule Name
field
At 06:41 AM 5/31/2011, dgerome06 wrote:
Hi everybody,
I try connect a plant loop with a condenser loop thanks to Heat
Exchanger:Hydronic in Condenser Equipment. In the plant i have set a
ThermalStorage:ChilledWater:Mixed and in the condenser loop i have set a
fluidcooler.
BUt i have the following message:
** Severe **
GetFreeCoolingHeatExchanger:HeatExchanger:Hydronic="EVAPORATEUR",
Controlled Component Name="CONDENSEUR" not found.
CONDENSEUR is the name of the fluidcooler, it is existing, so i dont
understand how to solve this problem.
Does someone could help me?
Thanks
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to
energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a
high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the Documentation link and press the "search"
button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/