The simple answer is yes, and you need not use EMS to control the OA inlet node actuator.
The following is from page 1670 of the I/O Ref Manual.
Controller:OutdoorAir,
OA Controller 1, !- Name
Relief Air Outlet Node, !- Relief Air Outlet Node Name
Outdoor Air Mixer Inlet Node, !- Return Air Node Name
Mixed Air Node, !- Mixed Air Node Name
Outdoor Air Inlet Node, !- Actuator Node Name
0.25, !- Minimum Outdoor Air Flow Rate {m3/s}
1.6, !- Maximum Outdoor Air Flow Rate {m3/s}
ElectronicEnthalpy, !- Economizer Control Type
ModulateFlow, !- Economizer Control Action Type
23., !- Economizer Maximum Limit Dry-Bulb Temperature {C}
, !- Economizer Maximum Limit Enthalpy {J/kg}
13.5, !- Economizer Maximum Limit Dewpoint Temperature {C}
ElectronicEnthalpyCurveA,!- Electronic Enthalpy Limit Curve Name
14., !- Economizer Minimum Limit Dry-Bulb Temperature {C}
NoLockout, !- Lockout Type
FixedMinimum, !- Minimum Limit Type
OAFractionSched, !- Minimum Outdoor Air Schedule Name
, !- Minimum Fraction of Outdoor Air Schedule Name
, !- Maximum Fraction of Outdoor Air Schedule Name
, !- Mechanical Ventilation Controller Name
TimeOfDayEconomizerSch, !- Time of Day Economizer Control Schedule Name
Yes, !- High Humidity Control
EAST ZONE, !- Humidistat Control Zone Name
0.9, !- High Humidity Outdoor Air Flow Ratio
Yes; !- Control High Indoor Humidity Based on Outdoor Humidity RatioCurve:Cubic,
ElectronicEnthalpyCurveA,!- Name
================= 0.01342704, !- Coefficient1 Constant
-0.00047892, !- Coefficient2 x
0.000053352, !- Coefficient3 x**2
-0.0000018103, !- Coefficient4 x**3
16.6, !- Minimum Value of x
29.13; !- Maximum Value of x
You need not use all the fields. There may be a simpler one without the economizer section. It has the option to use the sum of the minimum, and people, equipment, etc of the zone.
Controller:MechanicalVentilation
=======================
I do not quite follow your question with the Zone sizing - using the DesignSpecification:OutsideAir object. Zone sizing controls the equipment capacity. It will include the load demands, but do not vary the flow rate according to a schedule.
Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: vinay.devanathan@xxxxxxxxx
Date: Fri, 3 Jun 2011 18:28:21 -0400
Subject: [EnergyPlus_Support] OA - Zone Level
Hello,I would like to know if it is possible to specify Outdoor Air demand at Zone Level with the use of a Schedule. For example, a schedule or a pattern describing the demand for different OA Supply CFM at different times in the Zone Level? The only way to specify OA cfm to zones is using the Sizing:Zone object (excluding VAV system - which can use the DesignSpecification:OutsideAir object). Am I correct? Is there any other way to override this and introduce OA supply to the zones? Can this be done using EMS?Thank you.Vinay
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___