[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] OA - Zone Level





You are back to your original design question.
 
What is the real OA need per zone?  This is taken care off by the minimum air flow rate in the AHU and the air leak of the building,  unles you are designing a hospital OR cluster will filtered air..
 
If you must have a separate feed, use an AHU and a group of uncontrolled ATU's per zone.
 
The template four pipe fan coil has its own OA intake per zone.


 Dr. Li  



To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: vinay.devanathan@xxxxxxxxx
Date: Fri, 3 Jun 2011 20:56:43 -0400
Subject: Re: [EnergyPlus_Support] OA - Zone Level

 
Dr. Li,
 
Thanks for your reply.
 
I follow your method of specifying OA controls. But it arises one more question to me, how would a multi-zone system's OA controller distribute OA supply to each zone as per its individual needs? I am not able to find an answer for that.
 
Vinay


On Fri, Jun 3, 2011 at 8:27 PM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 

The simple answer is yes, and you need not use EMS to control the OA inlet node actuator.
 
The following is from page 1670 of the I/O Ref Manual.
 

Controller:OutdoorAir,

OA Controller 1, !- Name

Relief Air Outlet Node, !- Relief Air Outlet Node Name

Outdoor Air Mixer Inlet Node, !- Return Air Node Name

Mixed Air Node, !- Mixed Air Node Name

Outdoor Air Inlet Node, !- Actuator Node Name

0.25, !- Minimum Outdoor Air Flow Rate {m3/s}

1.6, !- Maximum Outdoor Air Flow Rate {m3/s}

ElectronicEnthalpy, !- Economizer Control Type

ModulateFlow, !- Economizer Control Action Type

23., !- Economizer Maximum Limit Dry-Bulb Temperature {C}

, !- Economizer Maximum Limit Enthalpy {J/kg}

13.5, !- Economizer Maximum Limit Dewpoint Temperature {C}

ElectronicEnthalpyCurveA,!- Electronic Enthalpy Limit Curve Name

14., !- Economizer Minimum Limit Dry-Bulb Temperature {C}

NoLockout, !- Lockout Type

FixedMinimum, !- Minimum Limit Type

OAFractionSched, !- Minimum Outdoor Air Schedule Name

, !- Minimum Fraction of Outdoor Air Schedule Name

, !- Maximum Fraction of Outdoor Air Schedule Name

, !- Mechanical Ventilation Controller Name

TimeOfDayEconomizerSch, !- Time of Day Economizer Control Schedule Name

Yes, !- High Humidity Control

EAST ZONE, !- Humidistat Control Zone Name

0.9, !- High Humidity Outdoor Air Flow Ratio
Yes; !- Control High Indoor Humidity Based on Outdoor Humidity Ratio

Curve:Cubic,

          ElectronicEnthalpyCurveA,!- Name

0.01342704, !- Coefficient1 Constant

-0.00047892, !- Coefficient2 x

0.000053352, !- Coefficient3 x**2

-0.0000018103, !- Coefficient4 x**3

16.6, !- Minimum Value of x

29.13; !- Maximum Value of x

=================
You need not use all the fields.  There may be a simpler one without the economizer section.  It has the option to use the sum of the minimum, and people, equipment, etc  of the zone.
Controller:MechanicalVentilation
=======================
I do not quite follow your question with the Zone sizing - using the DesignSpecification:OutsideAir object. Zone sizing controls the equipment capacity.  It will include the load demands, but do not vary the flow rate according to a schedule.
 
 Dr. Li  



 

To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: vinay.devanathan@xxxxxxxxx
Date: Fri, 3 Jun 2011 18:28:21 -0400
Subject: [EnergyPlus_Support] OA - Zone Level


 
Hello,
 
I would like to know if it is possible to specify Outdoor Air demand at Zone Level with the use of a Schedule. For example, a schedule or a pattern describing the demand for different OA Supply CFM at different times in the Zone Level? The only way to specify OA cfm to zones is using the Sizing:Zone object (excluding VAV system - which can use the DesignSpecification:OutsideAir object). Am I correct? Is there any other way to override this and introduce OA supply to the zones? Can this be done using EMS?
 
Thank you.
 
Vinay









__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___