Richard,

Thanks for your reply.

I have a Unitary System with multiple zones served by it. I am using this airloop mainly for ventilation purposes and have a separate system for space conditioning. In order to not utilize heating/cooling coils energy while providing ventilation air, I set the controlling zone to a zone that does not require conditioning at all. I assume that this is the reason the error is caused. Could you please say what you think is the best possible way to achieve what I want to do?

Thanks again.

On Fri, Jun 3, 2011 at 7:20 AM, Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
 

The Fraction of Supply Air Flow That Goes Through the Controlling Zone is automatically calculated by the program. It means that the thermostat zone, the zone that is defined in the input, provides all the air (fraction of air to the control zone divided by the total air flow rate through the heat pump). If you have more than 1 zone (or air terminal) on this air loop, then this air loop is not set up correctly. If you do only have 1 zone for this air loop, then this warning is a mistake and should probably not be written to the error file. If you do only have 1 zone, send your input file to energyplus-support@xxxxxxxx.



On 6/2/2011 10:32 PM, Vinay Devanathan wrote:
 
Hello,
 
Why would I get an error saying -
 
"The Fraction of Supply Air Flow That Goes Through the Controlling Zone is set to 1"
 
when there is no input like this in the definition of an Unitary Heat Pump : Air To Air object.
 
Any assistance would be greatly appreciated.

Thank you.
 
Vinay


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___