Hi, There were a couple of input errors in your file. Attached in the corrected file. Also transitioned the input file to V6. You need to fix the following error to get it working. ** Severe ** Attempt to assign branch to two different loops, Branch=ZONE 1 COOLING BRANCH ** ~~~ ** Branch already assigned to loop=CHILLED WATER LOOP ** ~~~ ** New attempt to assign to loop=HOT WATER LOOP ** Fatal ** GetPlantSideInput: Previous Severe errors cause termination. Suggest you look into the following files to accomplish your goal. RadLoTempCFloHeatCool.idf RadLoTempCFloHeatCoolCondFD.idf RadLoTempCFloTermReheat.idf Hope this helps. Thanks, Chandan On 6/13/2011 11:01 AM, Michela Buzzetti wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.