Sharing some experience:
If your building is far away from the equator, the altitude of the sun would be low. For a rectangular building with the longer sides facing north and south, separate North and South zones make sense.
For commercial buildings with a core, a Center zone has been used.
A vertical shaft can serve to house the ducts for supply air to the 3 floors and also act as the path for the return air. The AHU is at the top of the building.
ooi
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Kristina Donova <kristinadonova@...> wrote:
>
> Hello EnergyPlus World,
>
> I am new to energy modeling and EnergyPlus and I need some help on building zoning!
> I am trying to model a three-storey building which has a radiator system for heating and some of the premises will also have outdoor air units installed for fresh air supply. As given on the design drawings there's an outdoor air unit designed to serve multiple premises situated on all three floors of the building.I know that outdoor air units can serve only one zone, so the first thing that comes to my mind is to simply add all the premises that are served by the same outdoor air unit to one zone. But can I have a zone that includes premises on different floors? Wouldn't it reflect on the floor area at least? Or can I model this system as three separate ones for each floor? I've found some older posts on a similar topic, advising to model one system and then use ZoneCrossMixing, but this would work only between two zones. In my case there would be three.
>
> Please, help me find a solution!
>
> Thank you very much!
> Kristina
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/