Hey, Richard
Thanks a lot. I am not quite understand your idea. Since
The Idea Load Air System component does not control zone
humidity levels (just control zone air temperature). The
zone humidity level varies with the outdoor conditions via
infiltration. For "Idea Load Air System",the constant air
temperature and humidity of the air supplied for cooling
the zone are 13 degree Celsius and 9 g/kg. According the
ASHRAE sizing method (used by E+), total Cooling is the
rate at which total energy (sensible and latent) is
removed from the mixed outside and return air stream in
order to bring the mixed air stream to the specified
temperature and humidity ratio of the supply air stream.
For this case, the only source of latent heat gain is by
infiltration, and the infiltration latent heat gain should
be equal to total latent cooling load. But it isn't......
Xiaoshan
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad <RRaustad@...> wrote:
>
> Are you reporting the zone relative humidity? If the
zone moisture level
> is dropping, this would explain the difference. You
need to keep the
> zone conditions constant for this to work.
>
> On 6/17/2011 8:56 AM, yangxiaoshan@... wrote:
> >
> > Hi,
> > Thanks for your reply. I had set the
infiltration rate to 0 or other
> > values. If ACH is 0, there is no latent cooling
load and total cooling
> > load equals to total sensible cooling load. That
makes sense. But once
> > the ACH is not 0, the infiltration heat gain is
always less than
> > latent cooling load. I do not know what else
items could be also
> > included in the latent cooling load component.
> >
> > Best,
> > Xiaoshan
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>,
YuanLu Li <yli006@>
> > wrote:
> > >
> > >
> > > Try changing the infiltration air change
per hour to zero and to 2
> > to compare.
> > >
> > > There may be other compoent included in the
total cooling load.
> > >
> > > Dr. Li
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>
> > > From: yangxiaoshan@
> > > Date: Fri, 17 Jun 2011 06:37:59 +0800
> > > Subject: [EnergyPlus_Support] A question
about Latent Cooling Load in E+
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > Dear Colleagues,
> > >
> > >
> > > I got a question about latent cooling load
in EnergyPlus. The
> > simulation settings are: a single zone with
constant cooling setpoint
> > (26â"f through the day), no internal heat gain,
1 air changes per hour
> > and "Idea Load Air System" automatically used
for HVAC configuration.
> > Theoratically, due to there is no internal heat
gain in this case, the
> > follow correlation should be valid: "Total
cooling load - Total
> > sensible cooling load = Latent cooling load =
Infiltration latent heat
> > gain". But the simulation results shown that the
infiltration latent
> > heat gain is always less than the latent cooling
load (Total cooling
> > load - Total sensible cooling load), 2% for this
case (8-9% less was
> > found in other simulation case). I cannot
understand why the
> > infiltration heat gain is not equal to the
calculated latent cooling
> > load. Really headache! Look forward to
discussing with you, thanks
> > very much.
> > >
> > > Best regards,
> > > Xiaoshan
> > >
> >
> >
>
> --