I think that you can achieve this with a AvailabilityManager:Nightcycle object
Set the thermostat setpoint to 23 deg C, have the HVAC System Operation Schedule set to always off
Use 2 deg C as your thermostat tolerance and set the control type to CycleOnAny
This should make you cooling system stay off until zone temp = 25 deg C and then system comes on to cool until 23 deg COn Thu, Jun 23, 2011 at 1:06 PM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
I thought type 1 or 2 thermostat control would give you the set back as you discribed.Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: jeannieboef@xxxxxxxxx
Date: Thu, 23 Jun 2011 04:16:09 +0000
Subject: [EnergyPlus_Support] Re: Thermostat Float/Throttling Range
Generally, you are correct (not possible) although I have been able to mimic this type of control using EMS. I used negative process loads to cool a space which I turned on at the upper bound temp and off at the lower bound temp after checking that there is no heating on at the same time. Basically EMS allows little IF statements which are called during the normal simulation. It's a very nice part of e+.
You can manipulate a few object types including schedules, outputs, etc. Check out the EMS documentation.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "moe_wilensky" <moe_wilensky@...> wrote:
>
> From my initial look around this forum it would seem that on is unable to define a Thermostat Float/Throttling Range in Energy plus. Is this still the case?
>
> For example , I want the cooling to kick on at 25, run until the temp is 23 and then turn off until the temp drifts back up to 25. is it possible to define the 2 degrees float on top of my 23 degree set point?
>
> Thank you in advance for your time.
>
> -Will
>
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___