[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Design Day V.S. Schedule
Hello, I have a question about sizing:design day.The project I'm working on is a primary school, the occupancy, lighting, and other schedule is different in summer time. There is no people at school during June and July.
But my design day from weather data is July 21st. If I run and do the load calculation, it will be calculated on the design day, which means no occupancy and less lighting.
Is there any way that I can size my unit on design day with full internal load in summer time and less internal load for winter design day?
I don't want to change my occupancy and other schedules to increase the energy consumption.
Thanks for your help!
Qianmin
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___