Hi, QiangMin
================== SizingPeriod:DesignDay, SummerDesignDay and WinterDesignDay are the name of the schedules which you would like to use with the Sizing object. (day types 9 and 10)
Because the weekdays, etc. are related to the real situations, EPlus provided four extra conditions for you to do the simulation. In your schdules, if you wanted to use a week day to do the simulation, simply replace SummerDesignDay with, say, Monday.
The Day of Month and Month specify the solar angle or earth tilt angle. The Daylight saving time adjust the local time, as the solar noon and local time noon is changed by one hour. You may change these to other days and define special schedules and call them CustomDay1 and CustomDay2 (daytypes 11 and 12).
You can use as many DesignDay object as you want. However, you may need to use unique names. The data fields can be identical.
When you use the annual simulation or short runPeriod simulation, the actual weather file conditions are used.
When you use the Designday sizing simulation, the 24 hour period is repeated until the midnight conditions are the same.
When you use the weather file simulation, the conditions of the previous day is carried forward to the next day at midnight.
Sizing is controlled by what you think the system should be and is fixed. You have used sizing multiplier of 1.2, which means you want the system to be larger. You can also make it smaller and veriy with the PLR listing for the whole year.
The schedule can be changed according to occupancy and can have many different conditions for the whole year. Therefore you have National, Xmas, Easter holidays, etc. By default,I think Saturday is in the Holidays group. You can list all the schedules to verify as in my attached IDF. I have removed all your unused material and constructions.
School holidays can be scheduled as a period with allDays with holiday values. ========================== If you use short period for simulation, the first day result may not be accurate, therefore, th
Hello, I have a question about sizing:design day.
The project I'm working on is a primary school, the occupancy, lighting, and other schedule is different in summer time. There is no people at school during June and July.
But my design day from weather data is July 21st. If I run and do the load calculation, it will be calculated on the design day, which means no occupancy and less lighting. Is there any way that I can size my unit on design day with full internal load in summer time and less internal load for winter design day?
I don't want to change my occupancy and other schedules to increase the energy consumption. Thanks for your help! Qianmin
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.