That is the purpose of the daytypes - SummerDesignDay and WinterDesignDay.
You set up the schedules so they are appropriate on those days and leave the normal weekday schedules as they are.
At 02:01 PM 7/12/2011, Qianmin Zhang wrote:
Hello, I have a question about sizing:design day.
The project I'm working on is a primary school, the occupancy, lighting, and other schedule is different in summer time. There is no people at school during June and July.
But my design day from weather data is July 21st. If I run and do the load calculation, it will be calculated on the design day, which means no occupancy and less lighting.
Is there any way that I can size my unit on design day with full internal load in summer time and less internal load for winter design day?
I don't want to change my occupancy and other schedules to increase the energy consumption.
Thanks for your help!
Qianmin